Kjell,
Thank you -- we'd be happy to check out the subversion repository code and
try it. Just tell us when you are ready for us to do this, and which tag
or branch to check out.
(Note: my inclination is to build and replace just the driver and the cgi
script. But we can do differently if you tell us to.)
I'm very grateful for your support, and for the NUT package. It's very
important to us, since it shuts down ~ 700 machines and file systems and
helps us to protect about 250 TB of data. And in Milwaukee, Wisconsin, we
have at least a few power loss events every year, normally in winter.
Cheers,
Bruce
On Thu, 3 Aug 2006, Kjell Claesson wrote:
> tor 2006-08-03 klockan 15:00 -0500 skrev Paul Armor:
>> Hi Kjell,
>>
>
> Hi Paul,
>> We're using the bcmxcp driver.
>>
>> Thanks!
>> Paul
>>
>
> I have checked up the packages. The nut-2.0.3 does not support this in
> the cgi that make up the page.
> And it did not get into the last release nut-2.0.4.
>
> But it is in the subversion trunk. I can change the bcmxcp driver
> to support this values. This have been on the 'todo' list for
> me for some time. But my time on this have been limited.
>
> The changes that have to be done is the image var table in upsimage.c
> in the cgi client and also extending the bcmxcp_meter_map in the driver.
>
> The first is done, so i can extend the driver. The problem is that you
> need to use the svn code. And that may be a problem if it is a
> production setup.
>
> But i get to it asap, then you can decide if you want to try it out.
>
> Regards
> Kjell
>
>
>>
>>
>> On Thu, 3 Aug 2006, Kjell Claesson wrote:
>>
>>> Hi Bruce,
>>> tor 2006-08-03 klockan 11:59 -0500 skrev Bruce Allen:
>>>> Adam: Thanks for putting up this page. But something is wrong. In
>>>> particular, our Powerware 9135 is a three phase UPS system with THREE 480
>>>> volt outputs. So the displayed voltage is not correct -- in fact there
>>>> should really be THREE voltages displayed, all around 480v.
>>>>
>>>> Nut developers: I am copying the NUT mailing list to see if anyone can
>>>> suggest how to fix this. NUT developers, see the following page to see
>>>> the problem: http://nemo.phys.uwm.edu/cgi-bin/upsstats.cgi . Instead of
>>>> displaying a single voltage of 276 VAC we should see three voltages of
>>>> around 480 VAC.
>>>>
>>>> Cheers,
>>>> Bruce
>>>
>>> Yes this can be fixed.
>>>
>>> Are you using the bcmxcp driver or is it monitored by snmp?
>>>
>>> Regards
>>> Kjell
>>>
>>>
>>> _______________________________________________
>>> Nemo-devel mailing list
>>> Nemo-devel at gravity.phys.uwm.edu
>>> http://gravity.phys.uwm.edu/mailman/listinfo/nemo-devel
>>>
>>
>
> _______________________________________________
> Nemo-devel mailing list
> Nemo-devel at gravity.phys.uwm.edu
> http://gravity.phys.uwm.edu/mailman/listinfo/nemo-devel
>
More information about the Nut-upsdev
mailing list