[Nut-upsdev] shut down smart ups with snmp protocol
Arjen de Korte
nut+devel at de-korte.org
Tue Jun 9 14:35:51 UTC 2009
Citeren "mbedyn Gazeta.pl" <mbedyn op gazeta.pl>:
>> See 'man 8 snmp-ups'.
>
> I have read docs... and it stays that
>
> This driver has been tagged experimental, even if it has been reported
> to be stable. Thus it is not suitable for production systems and it is
> not built by default. This is mainly due to the fact that there is
> still no proper upsdrv_shutdown() function implemented !
Well, that pretty much says it all, doesn't it?
Since you're writing to the development mailing list, we assume that
you know that not having a upsdrv_shutdown() function in a driver
pretty much means that you can't shut the UPS down via upsdrvctl and
that you need to use an alternative way to send it a shutdown command.
> Maybe there is somebody who has done this before with this driver...
It can't be done. Upgrade to the latest version (nut-2.4.1) and you'll
find that the man page for snmp-ups mentions why this will never be
possible and what you might do about it.
Note that we don't backport changes to earlier versions, so if you
have questions for development, make sure you're running at least the
latest stable version (or better yet, the SVN trunk version). Older
version might be supported through the nut-users mailing list.
Best regards, Arjen
--