[Nut-upsdev] [HCL] CyberPower Systems PR6000LCDRTXL5U supported by usbhid-ups
Dax Kelson
dkelson at gurulabs.com
Thu Apr 26 22:05:16 UTC 2012
CyberPower Systems PR6000LCDRTXL5U
http://www.cyberpowersystems.com/products/ups-systems/smart-app-ups/pp-series/PR6000LCDRTXL5U.html
I had to create the following udev rule (on RHEL6):
ATTR{idVendor}=="0764", ATTR{idProduct}=="0601", MODE="664", GROUP="dialout"
Shutdown testing successful. UPS comes back online after turning off.
# upsc
battery.charge: 100
battery.charge.low: 35
battery.charge.warning: 20
battery.mfr.date: CyberPower Systems
battery.runtime: 1800
battery.runtime.low: 0
battery.type: PbAcid
battery.voltage: 53.8
battery.voltage.nominal: 48
device.mfr: CyberPower Systems
device.model: PR6000LCDRTXL5U
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.35
input.transfer.high: 254
input.transfer.low: 147
input.voltage: 240.0
input.voltage.nominal: 112
output.voltage: 207.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 46
ups.mfr: CyberPower Systems
ups.model: PR6000LCDRTXL5U
ups.productid: 0601
ups.realpower.nominal: 4500
ups.status: OL
ups.timer.shutdown: 0
ups.timer.start: 0
ups.vendorid: 0764
# upsrw
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Value: 35
[battery.runtime.low]
Remaining battery runtime when UPS switches to LB (seconds)
Type: STRING
Value: 0
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Value: 254
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Value: 147
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 20
[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Value: 30
# upscmd -l
Instant commands supported on UPS [cyberpower]:
beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
load.on - Turn on the load immediately
load.on.delay - Turn on the load with a delay (seconds)
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
More information about the Nut-upsdev
mailing list