[Nut-upsdev] (no subject)

cinowell cinowell at gmail.com
Fri Mar 13 22:30:16 UTC 2015


Hello,

I had running OpenMediaVault server with NUT 2.4.3 megatec_usb driver.
After the OMV upgrade, NUT also upgraded to 2.6.4. I realised that
megatec_usb removed in this version. So I have configured to use blazer_usb
driver. However NUT behaves incorrectly after switching blazer_usb. System
is being halted upon booted up.
Is it possible to use megatec_usb driver in the new version?


# NUT 2.4.3 with megatec_usb driver
battery.charge: 98.3
battery.voltage: 27.00
battery.voltage.nominal: 23.5
device.mfr: TUNCMATIK
device.model: DG1200VA VER1.01C
device.serial: unknown
device.type: ups
driver.name: megatec_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.internal: 1.6
input.frequency: 50.0
input.frequency.nominal: 50.0
input.voltage: 220.0
input.voltage.fault: 165.0
input.voltage.maximum: 226.0
input.voltage.minimum: 217.0
input.voltage.nominal: 220.0
output.voltage: 220.0
ups.beeper.status: disabled
ups.delay.shutdown: 0
ups.delay.start: 2
ups.load: 0.0
ups.mfr: TUNCMATIK
ups.model: DG1200VA VER1.01C
ups.serial: unknown
ups.status: OL OFF
ups.type: standby

# NUT 2.6.4 with blazer_usb driver
battery.charge: 100
battery.voltage: 27.00
battery.voltage.high: 25.46
battery.voltage.low: 20.37
battery.voltage.nominal: 23.5
device.mfr: TUNCMATIK
device.model: DG1200VA
device.type: ups
driver.name: blazer_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.4
driver.version.internal: 0.08
input.current.nominal: 8.0
input.frequency: 50.0
input.frequency.nominal: 50
input.voltage: 212.0
input.voltage.fault: 165.0
input.voltage.nominal: 220
output.voltage: 212.0
ups.alarm: Shutdown imminent!
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 180
ups.firmware: VER1.01C
ups.load: 0
ups.mfr: TUNCMATIK
ups.model: DG1200VA
ups.productid: 0000
ups.status: ALARM OL FSD
ups.temperature: 0.0
ups.type: offline / line interactive
ups.vendorid: 0001

#NUT logs

   1. Feb 22 19:48:43 microserver upsd[2586]: listening on 127.0.0.1 port
   3493
   2. Feb 22 19:48:43 microserver upsd[2586]: Connected to UPS [ups]:
   blazer_usb-ups
   3. Feb 22 19:48:43 microserver upsd[2596]: Startup successful
   4. Feb 22 19:48:43 microserver upsd[2596]: User monmaster at 127.0.0.1
   logged into UPS [ups]
   5. Feb 22 19:48:43 microserver upsmon[2608]: Startup successful
   6. Feb 22 19:48:48 microserver upsmon[2610]: UPS ups at localhost: forced
   shutdown in progress
   7. Feb 22 19:48:48 microserver upsd[2596]: Client monmaster at 127.0.0.1
   set FSD on UPS [ups]
   8. Feb 22 19:48:48 microserver upsmon[2610]: Executing automatic
   power-fail shutdown
   9. Feb 22 19:48:48 microserver upsmon[2610]: Auto logout and shutdown
   proceeding
   10. Feb 22 19:48:48 microserver upssched[2760]: Executing command: notify
   11. Feb 22 19:48:48 microserver upssched[2758]: Executing command:
   forced-shutdown
   12. Feb 22 19:48:48 microserver upsmon[2610]: Signal 10: User requested
   FSD
   13. Feb 22 19:48:49 microserver upssched-cmd: UPS ups at localhost: -
   Forced shutdown in progress
   14. Feb 22 19:48:49 microserver upssched-cmd: Automatic logout and
   shutdown proceeding

# dmesg

usbfs: USBDEVFS_CONTROL failed cmd blazer_usb rqt 128 rq 6 len 255 ret -110

Regards.
Mustafa T.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsdev/attachments/20150314/4d4faca5/attachment.html>


More information about the Nut-upsdev mailing list