[shutdown sequence]
I have tested and verified the shutdown sequence works.
[manufacturor]
https://www.cyberpowersystems.com/product/ups/ec350g/
mbeisser at nas:~$ upsc ups
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 1575
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 9.3
battery.voltage.nominal: 12
device.mfr: CPS
device.model: EC350G
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.7.2
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 140
input.transfer.low: 96
input.voltage: 118.0
input.voltage.nominal: 120
output.voltage: 118.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 20
ups.mfr: CPS
ups.model: EC350G
ups.productid: 0501
ups.realpower.nominal: 255
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: 0
ups.vendorid: 0764
mbeisser at nas:~$ upsrw ups
[battery.charge.low]
Remaining battery level when UPS switches to LB (percent)
Type: STRING
Maximum length: 10
Value: 10
[battery.runtime.low]
Remaining battery runtime when UPS switches to LB (seconds)
Type: STRING
Maximum length: 10
Value: 300
[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 140
[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Maximum length: 10
Value: 96
[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Maximum length: 10
Value: 20
[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Maximum length: 10
Value: 30
--