[Nut-upsdev] [networkupstools/nut] Riello IDG400 wrong values & not powering off (#530)
Charles Lepple
clepple at gmail.com
Mon Feb 26 13:56:21 UTC 2018
On Feb 26, 2018, at 4:58 AM, Elio Parisi <e.parisi at riello-ups.com> wrote:
>
> Hi Charles,
> this type of UPS doesn't support realtime autonomy calculation, instead a fixed countdown must be used.
>
> How we can fix non supported values?
If a value is not supported, the driver should not publish it with the dstate API. Dhould the driver be modified to not return battery.charge if the UPS returns 0xFF? Are there other variables that are affected?
(I don't think the IDG400 is covered in the protocol documentation that the NUT project received a while back.)
>
> For the point number 2, as we know NUT perfomrs the shutdown after battery low signal with a delay of 5 seconds as specified in the FINALDELAY.
> Is this correct?
Right, NUT tells the computer to shut down, but it also typically sends a shutdown signal to the UPS. Does the IDG400 also respond to the same shutdown command as others?