[Nut-upsuser] MGE Pulsar Extreme - restart problem

Axel Bergerhoff axelbergerhoff at compuserve.com
Thu Jul 13 15:08:23 UTC 2006


> Hi Axel,
>
> 2006/7/13, Axel Bergerhoff <axelbergerhoff at compuserve.com>:
> > Hello,
> >
> > looking for replacements for some older Powerware equipment I found the
> > MGE
> > Pulsar Extreme 1000C and I'm currently testing one with nut-2.0.3 on a
> > self-brewn i386-linux.
> >
> > Upto now everything seems to work fine - except I can't get the power
> > outlets
> > switching on again after mains returns. As this works with Personal
> > Solution-Pac 2 on W2k I thought that there might be a way to achieve it
> > with
> > nut, too. However, after trying "everything", I don't know any further.
> >
> > My ups.conf:
> >   driverpath = /bin
> >   [Pulsar1000]
> >   driver = mge-shut
> >   port = /dev/ttyS1
> >   offdelay = 120
> >   # mge-shut:  ondelay in s * 10
> >   ondelay = 15
> >   desc = tfp-3
> >
> > Manually set
> >   cold start            disabled
> >   automatic restart     enabled
> >   energy savings        disabled
> >
> >
> > Any ideas?
>
> I don't see anything according to your settings.
> can you send an upsc output so that I can do some check.
> FYI, I'm completly rewritting mge-shut for nut 2.2. Some
> things are still lacking, but this approach will solve all the
> current mge-shut problems and lacks.
>
> You should also have a look at this thread:
> http://lists.alioth.debian.org/pipermail/nut-upsuser/2006-July/001267.html
> http://lists.alioth.debian.org/pipermail/nut-upsuser/2006-July/001271.html
>
> This will be available soon in newmge-shut (the current development
> version).
>
> Arnaud

Thanks for your being that fast!

I'll look to the threads tomorrow, ouptuts from upsc and upsrw are here:

tfp-3:~ # upsrw Pulsar1000 at localhost
[battery.charge.low]
Remaining battery level when UPS switches to LB
Type: STRING
Value: 20

[outlet.0.desc]
Unavailable
Type: STRING
Value: Main Outlet

[outlet.1.autoswitch.charge.low]
Unavailable
Type: STRING
Value: 0

[outlet.1.delay.shutdown]
Unavailable
Type: STRING
Value: -1

[outlet.1.delay.start]
Unavailable
Type: STRING
Value: -1

[outlet.1.desc]
Unavailable
Type: STRING
Value: PowerShare Outlet 1

[outlet.1.switch]
Unavailable
Type: STRING
Value: 1

[outlet.2.autoswitch.charge.low]
Unavailable
Type: STRING
Value: 0

[outlet.2.delay.shutdown]
Unavailable
Type: STRING
Value: -1

[outlet.2.delay.start]
Unavailable
Type: STRING
Value: -1

[outlet.2.desc]
Unavailable
Type: STRING
Value: PowerShare Outlet 2

[outlet.2.switch]
Unavailable
Type: STRING
Value: 1

[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: -1

[ups.delay.start]
Interval to wait before (re)starting the load (seconds)
Type: STRING
Value: -1

--------------------------------------------------------

tfp-3:~ # upsc Pulsar1000 at localhost
battery.charge: 82
battery.charge.low: 20
battery.runtime: 03979
driver.name: mge-shut
driver.parameter.offdelay: 120
driver.parameter.ondelay: 15
driver.parameter.port: /dev/ttyS1
driver.version: 2.0.3
driver.version.internal: 0.65
input.frequency: 49
input.voltage: 229
outlet.0.desc: Main Outlet
outlet.0.id: 0
outlet.0.switchable: 1
outlet.1.autoswitch.charge.low: 0
outlet.1.delay.shutdown: -1
outlet.1.delay.start: -1
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 1
outlet.1.switch: 1
outlet.1.switchable: 1
outlet.2.autoswitch.charge.low: 0
outlet.2.delay.shutdown: -1
outlet.2.delay.start: -1
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 2
outlet.2.switch: 1
outlet.2.switchable: 1
output.frequency: 49
output.voltage: 230
output.voltage.target.battery: 40
output.voltage.target.line: 40
ups.delay.shutdown: -1
ups.delay.start: -1
ups.load: 10
ups.mfr: MGE UPS SYSTEMS
ups.power.nominal: 1000
ups.serial: 1Y2G15069
ups.status: OL CHRG
ups.test.result: Done and passed


Axel



More information about the Nut-upsuser mailing list