[Nut-upsuser] MGE Pulsar Extreme - restart problem
Axel Bergerhoff
axelbergerhoff at compuserve.com
Thu Jul 20 09:53:47 UTC 2006
> 2006/7/14, Axel Bergerhoff <axelbergerhoff at compuserve.com>:
> > ...
> > Addendum:
> > Looked to the thread mentioned above - found that I already knew it.
> > My current problem is not delaying power on of outlet.1 and
> > outlet.2(although this does not work for me either) but automatically
> > powering on the main outlet when reapplying mains after a complete
> > shutdown and an indefinite off
> > time.
>
> right, sorry. I mixed with another case.
>
> Can you make a shutdown test?
> - remove the load on the ups output (ie computers, ...),
> - stop nut
> - call mge-shut in shutdown mode with debug info:
> mge-shut -DD -k /dev/ttyS0
>
> the ups should be turned off after 20 sec, and on 10 after.
> send me back the above mge-shut output.
>
> Arnaud
UPS behaves differently (see below).
Additionally I dumped the traffic with a serial analyzer - if that helps I
could post it, too (lenghty).
My tests:
Setup:
- computer directly connected to mains
- 100W bulb used as load
- load manually switched on at UPS
- nut-2.0.3
nut started:
tfp-3:~ # rcnut start
NUT Starting UPS model drivers: Network UPS Tools - UPS driver controller
2.0.3
Network UPS Tools - MGE UPS SYSTEMS/SHUT driver 0.65 (2.0.3)
Detected (null) [1Y2G15069] on /dev/ttyS1
NUT Starting UPS daemon: Network UPS Tools upsd 2.0.3
Connected to UPS [Pulsar1000]: mge-shut-ttyS1
Synchronizing...........done
Network UPS Tools upsmon 2.0.3
UPS: Pulsar1000 at localhost (master) (power value 1)
Using power down flag file /var2/nut/killpower
tfp-3:~ #
nut stopped:
tfp-3:~ # rcnut stop
Network UPS Tools upsmon 2.0.3
NUT Stopping UPS daemon
Network UPS Tools upsd 2.0.3
NUT Stopping UPS model drivers
Network UPS Tools - UPS driver controller 2.0.3
Stopping UPS: Pulsar1000
tfp-3:~ #
test:
08:54:10
tfp-3:~ # mge-shut -DD -k /dev/ttyS1
Network UPS Tools - MGE UPS SYSTEMS/SHUT driver 0.65 (2.0.3)
debug level is '2'
entering upsdrv_initups()
entering shut_ups_start()
Communication with UPS established
entering shut_get_descriptor(n 21, 9)
shut_wait_ack(): ACK received
entering shut_get_descriptor(n 01, 18)
shut_wait_ack(): ACK received
Device Descriptor:
bLength: 0x12
bDescriptorType: 0x01
bcdUSB: 0x0110
bDeviceClass: 0x00
bDeviceSubClass: 0x00
bDeviceProtocol: 0x00
bMaxPacketSize0: 0x08
idVendor: 0x0463
idProduct: 0xffff
bcdDevice: 0x0100
iManufacturer: 0x01
iProduct: 0x02
iSerialNumber: 0x04
bNumConfigurations: 0x01
entering shut_get_descriptor(n 22, 2002)
shut_wait_ack(): ACK received
Initiating UPS shutdown
============== entering hid_set_value(ups.delay.start, 3) ==============
entering shut_get_report(id: 0a, len: 1800)
shut_wait_ack(): ACK received
entering shut_set_report(id: 0a, len: 05)
shut_wait_ack(): ACK received
shut_wait_ack(): ACK received
============== entering hid_set_value(ups.delay.shutdown, 20) ==============
entering shut_get_report(id: 09, len: 1800)
shut_wait_ack(): ACK received
entering shut_set_report(id: 09, len: 05)
shut_wait_ack(): ACK received
shut_wait_ack(): ACK received
tfp-3:~ #
08:54:50
load off
09:26:00
nothing happened
UPS-display:
load not powered, on/off to start
tried to start by button
UPS-display:
UPS off in progress
09:26:05
UPS-display:
load not powered, on/off to start
09:27:00
tried to start by button again
load is on
---------------------------------------------
Tried nut-2.0.4-pre1
start nut:
tfp-3:~ # rcnut start
NUT Starting UPS model drivers: Network UPS Tools - UPS driver controller
2.0.4-pre1
Network UPS Tools - MGE UPS SYSTEMS/SHUT driver 0.66 (2.0.4-pre1)
Detected Pulsar 1000 [1Y2G15069] on /dev/ttyS1
NUT Starting UPS daemon: Network UPS Tools upsd 2.0.4-pre1
Connected to UPS [Pulsar1000]: mge-shut-ttyS1
Synchronizing..........done
Network UPS Tools upsmon 2.0.4-pre1
UPS: Pulsar1000 at localhost (master) (power value 1)
Using power down flag file /var2/nut/killpower
tfp-3:~ #
stop nut:
tfp-3:~ # rcnut stop
Network UPS Tools upsmon 2.0.4-pre1
NUT Stopping UPS daemon
Network UPS Tools upsd 2.0.4-pre1
NUT Stopping UPS model drivers
Network UPS Tools - UPS driver controller 2.0.4-pre1
Stopping UPS: Pulsar1000
tfp-3:~ #
test:
09:42:00
tfp-3:~ # mge-shut -DD -k /dev/ttyS1
Network UPS Tools - MGE UPS SYSTEMS/SHUT driver 0.66 (2.0.4-pre1)
debug level is '2'
entering upsdrv_initups()
entering shut_ups_start()
Communication with UPS established
entering shut_get_descriptor(n 21, 9)
shut_wait_ack(): ACK received
entering shut_get_descriptor(n 01, 18)
shut_wait_ack(): ACK received
Device Descriptor:
bLength: 0x12
bDescriptorType: 0x01
bcdUSB: 0x0110
bDeviceClass: 0x00
bDeviceSubClass: 0x00
bDeviceProtocol: 0x00
bMaxPacketSize0: 0x08
idVendor: 0x0463
idProduct: 0xffff
bcdDevice: 0x0100
iManufacturer: 0x01
iProduct: 0x02
iSerialNumber: 0x04
bNumConfigurations: 0x01
entering shut_get_descriptor(n 22, 2002)
shut_wait_ack(): ACK received
09:42:20
Initiating UPS shutdown
============== entering hid_set_value(ups.delay.start, 3) ==============
entering shut_get_report(id: 0a, len: 1800)
shut_wait_ack(): ACK received
entering shut_set_report(id: 0a, len: 05)
shut_wait_ack(): ACK received
shut_wait_ack(): ACK received
============== entering hid_set_value(ups.delay.shutdown, 20) ==============
entering shut_get_report(id: 09, len: 1800)
shut_wait_ack(): ACK received
entering shut_set_report(id: 09, len: 05)
shut_wait_ack(): ACK received
shut_wait_ack(): ACK received
tfp-3:~ #
09:42:42
load off
Rest same as before
Axel
More information about the Nut-upsuser
mailing list