[Nut-upsuser] tripplite SMART3000RM2U ups.status never change

Niels Baggesen nba at users.sourceforge.net
Wed Mar 1 19:21:01 UTC 2006


On Wed, Mar 01, 2006 at 08:26:02AM -0600, Brady Chang wrote:
> SNMPv2-SMI::mib-2.33.1.4.1.0 = INTEGER: 3

This one is the crucial one ...
If we translate it using the MIB it is

$ snmptranslate -Td -m+UPS-MIB SNMPv2-SMI::mib-2.33.1.4.1.0
UPS-MIB::upsOutputSource.0
upsOutputSource OBJECT-TYPE
  -- FROM       UPS-MIB
  SYNTAX        INTEGER {other(1), none(2), normal(3), bypass(4),
			  battery(5), booster(6), reducer(7)}
  MAX-ACCESS    read-only
  STATUS        current
  DESCRIPTION   "The present source of output power.  The enumeration
		none(2) indicates that there is no source of output
		power (and therefore no output power), for example,
		the system has opened the output breaker."
::= { iso(1) org(3) dod(6) internet(1) mgmt(2) mib-2(1) upsMIB(33)
      upsObjects(1) upsOutput(4) upsOutputSource(1) 0 }

or

UPS-MIB::upsOutputSource.0 = INTEGER: normal(3)

So the UPS does not say that it is on battery, which means that there is
no way for NUT to say it

/Niels

-- 
Niels Baggesen - @home - Århus - Denmark - nba at users.sourceforge.net
The purpose of computing is insight, not numbers   ---   R W Hamming