[Nut-upsuser] MGE Pulsar M 3000 communication problems

Ingo Schaefer ingo at ingo-schaefer.de
Mon Oct 9 05:57:14 UTC 2006


Hello Arnaud,
Am Freitag, den 06.10.2006, 09:21 +0200 schrieb Arnaud Quette:
> can you now make an integration test (mge-shut, not in debug mode +
> upsd + upsmon) and report back.
> Note that you will need to adjust MAXAGE and DEADTIME to 20/25 seconds.

I adjusted both a bit, MAXAGE to 45 (because 25 was not enough) and
DEADTIME now to 25 (maybe I should also reduce the polling interval?)

Bit I am afraid it was not successful.

Oct  9 07:12:08 suncore mge-shut[26651]: [ID 702911 daemon.info] Startup
successful
Oct  9 07:12:08 suncore upsd[26652]: [ID 702911 daemon.info] Connected
to UPS [mge3000-1]: mge-shut-ttyb
Oct  9 07:12:13 suncore upsd[26653]: [ID 702911 daemon.info] Startup
successful
[several manual queries via upsc]
Oct  9 07:13:16 suncore upsmon[26741]: [ID 702911 daemon.info] Startup
successful
Oct  9 07:13:16 suncore upsd[26653]: [ID 702911 daemon.info] Connection
from 127.0.0.1
Oct  9 07:13:16 suncore upsd[26653]: [ID 702911 daemon.info] Client
monitor at 127.0.0.1 logged into UPS [mge3000-1]
Oct  9 07:18:49 suncore upsd[26653]: [ID 702911 daemon.notice] Data for
UPS [mge3000-1] is stale - check driver
Oct  9 07:18:51 suncore upsmon[26743]: [ID 702911 daemon.error] Poll UPS
[mge3000-1 at localhost] failed - Data stale
Oct  9 07:18:51 suncore upsmon[26743]: [ID 702911 daemon.notice]
Communications with UPS mge3000-1 at localhost lost
Oct  9 07:18:56 suncore upsmon[26743]: [ID 702911 daemon.error] Poll UPS
[mge3000-1 at localhost] failed - Data stale
Oct  9 07:19:01 suncore upsmon[26743]: [ID 702911 daemon.error] Poll UPS
[mge3000-1 at localhost] failed - Data stale
Oct  9 07:19:06 suncore upsmon[26743]: [ID 702911 daemon.error] Poll UPS
[mge3000-1 at localhost] failed - Data stale
Oct  9 07:19:07 suncore upsd[26653]: [ID 702911 daemon.notice] UPS
[mge3000-1] data is no longer stale
Oct  9 07:19:11 suncore upsmon[26743]: [ID 702911 daemon.notice]
Communications with UPS mge3000-1 at localhost established

> Also note that the mge-shut rewritte for 2.2 (merge with newhidups,
> which shares the same HID core) will greatly improve such kind of
> problems, since the hardware is polled too much, even for constant
> data. And I've already addressed this in newhidups. So we're more
> about finding a temporary solution to your problem, while waiting for
> the real good solution.

as we now have version 2.0.4 - how long will it take to get 2.2 out? And
plans yet?

> > Thats the way I know OSS projects. Especially if supported by hardware
> > vendors or distributors. Great!
> 
> right, but what MGE does is still more an exception than the standard!

I don't want to start a meta discussion about this. We did research
about OSS and found that a lot of projects get support from hardware
vendors or distributors. Lot more than expected. So MGE is in good
company.

On the other side is a lot of hardware vendors hiding their stuff and
not let the linux developers write drivers.

Regards,
Ingo
-- 
"Milchreis schmeckt hervorragend, wenn man ihn kurz vor dem Verzehr
durch ein saftiges Steak ersetzt."
                                         gefunden bei frag-mutti.de
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: application/pgp-signature
Size: 189 bytes
Desc: Dies ist ein digital signierter Nachrichtenteil
Url : http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20061009/87b42df4/attachment.pgp


More information about the Nut-upsuser mailing list