[Nut-upsuser] Multiple Tripplite OMNI900LCD

Todd Woods twoods at commo.com
Fri Aug 31 16:21:03 UTC 2007


------------------------------------
One UPS plugged into first USB port
-------------------------------------
# /usr/local/ups/bin/usbhid-ups -a ups2 -DD
debug level is '2'
Checking device (0000/0000) (002/001)
- VendorID: 0000
- ProductID: 0000
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 002
Trying to match device
Device does not match - skipping
Checking device (09AE/2007) (002/002)
- VendorID: 09ae
- ProductID: 2007
- Manufacturer: Tripp Lite
- Product: TRIPP LITE UPS
- Serial Number: FW-2263 E
- Bus: 002
Trying to match device
Device matches
Warning: two different HID descriptors retrieved (Reportlen = 447 vs. 601)
HID descriptor retrieved (Reportlen = 601)
Report descriptor retrieved (Reportlen = 601)
Found HID device
Report Descriptor size = 601
Detected a UPS: Tripp Lite /TRIPP LITE UPS
Using subdriver: TrippLite HID 0.1 (experimental)
Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, 
Size: 8, Value: 1.000000
Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 
0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 
0, Size: 8, Value: 3.000000
Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, 
Offset: 0, Size: 8, Value: 120.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, 
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, 
Offset: 0, Size: 8, Value: 24.000000
Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 
0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 
0, Size: 16, Value: 1395.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, 
Offset: 0, Size: 16, Value: 1395.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, 
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, 
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, 
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, 
ReportID: 0x32, Offset: 0, Size: 1, Value: 0.000000
Can't find object UPS.PowerSummary.PresentStatus.TLACPresent
Path: UPS.PowerSummary.PresentStatus.TLACPresent, Type: Input, ReportID: 
0x32, Offset: 1, Size: 1
Can't find object UPS.PowerSummary.PresentStatus.TLCharging
Path: UPS.PowerSummary.PresentStatus.TLCharging, Type: Input, ReportID: 
0x32, Offset: 2, Size: 1
Can't find object UPS.PowerSummary.PresentStatus.TLDischarging
Path: UPS.PowerSummary.PresentStatus.TLDischarging, Type: Input, ReportID: 
0x32, Offset: 3, Size: 1
Can't find object UPS.PowerSummary.PresentStatus.TLNeedReplacement
Path: UPS.PowerSummary.PresentStatus.TLNeedReplacement, Type: Input, 
ReportID: 0x32, Offset: 4, Size: 1
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, 
ReportID: 0x32, Offset: 0, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 
0x32, Offset: 1, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 
0x32, Offset: 2, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 
0x32, Offset: 3, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, 
ReportID: 0x32, Offset: 4, Size: 1, Value: 0.000000
Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 
0x04, Offset: 0, Size: 16, Value: 12.000000
Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, 
ReportID: 0x23, Offset: 0, Size: 1, Value: 1.000000
Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, 
ReportID: 0x23, Offset: 1, Size: 1, Value: 0.000000
Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: 
Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, 
Size: 8, Value: 0.000000
Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, 
Size: 8, Value: 120.000000
Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, 
Size: 8, Value: 60.000000
Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 
0, Size: 16, Value: 1000.000000
Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 
0x15, Offset: 0, Size: 16, Value: 65535.000000
Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, ReportID: 0x51, 
Offset: 0, Size: 8, Value: 0.000000
Path: UPS.OutletSystem.Outlet.ffff0092, Type: Feature, ReportID: 0x52, 
Offset: 0, Size: 8, Value: 0.000000
Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature, ReportID: 0xb6, 
Offset: 0, Size: 8, Value: 1.000000
Path: UPS.ffff0010.[1].ffff007d, Type: Feature, ReportID: 0x6c, Offset: 0, 
Size: 16, Value: 8199.000000
Path: UPS.ffff0015.[1].ffff00c0, Type: Feature, ReportID: 0x96, Offset: 0, 
Size: 8, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00d2, Type: Feature, ReportID: 0xb4, Offset: 0, 
Size: 32, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c1, Type: Feature, ReportID: 0x97, Offset: 0, 
Size: 16, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c2, Type: Feature, ReportID: 0x98, Offset: 0, 
Size: 8, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c3, Type: Feature, ReportID: 0x99, Offset: 0, 
Size: 16, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c5, Type: Feature, ReportID: 0x9b, Offset: 0, 
Size: 16, Value: 3.000000
Path: UPS.ffff0015.[1].ffff00d6, Type: Feature, ReportID: 0xc2, Offset: 0, 
Size: 32, Value: 14.000000
Can't retrieve Report 154 (110): Connection timed out
Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID: 0x9a, Offset: 0, 
Size: 32
Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, 
Size: 16, Value: 1177.000000
Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, 
Offset: 0, Size: 16, Value: 135.000000
Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, 
Offset: 0, Size: 16, Value: 117.700005
Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, 
Offset: 0, Size: 16, Value: 60.000000
Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, 
ReportID: 0x22, Offset: 0, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, 
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, 
Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 
0x22, Offset: 4, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature, ReportID: 0x22, 
Offset: 5, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, 
ReportID: 0x22, Offset: 6, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, 
ReportID: 0x22, Offset: 7, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, 
ReportID: 0x22, Offset: 14, Size: 1, Value: 0.000000
Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 
0x17, Offset: 0, Size: 16, Value: 65535.000000
Can't find object UPS.PowerSummary.RemainingCapacityLimit
Can't find object UPS.PowerSummary.WarningCapacityLimit
Can't find object UPS.BatterySystem.Temperature
Can't find object UPS.OutletSystem.Outlet.DelayBeforeStartup
Can't find object UPS.OutletSystem.Outlet.ActivePower
Can't find object UPS.PowerConverter.Output.ActivePower
Can't find object UPS.OutletSystem.Outlet.PercentLoad
Can't find object UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit
Can't find object UPS.PowerSummary.PresentStatus.FullyCharged
Can't find object UPS.PowerSummary.PresentStatus.TLACPresent
Can't find object UPS.PowerSummary.PresentStatus.TLDischarging
Can't find object UPS.PowerSummary.PresentStatus.TLCharging
Can't find object UPS.PowerSummary.PresentStatus.TLNeedReplacement
Can't find object UPS.PowerConverter.Output.HighVoltageTransfer
Can't find object UPS.PowerConverter.Output.LowVoltageTransfer
Can't find object UPS.PowerConverter.Output.Current
Can't find object UPS.PowerConverter.Output.Frequency
Can't find object UPS.OutletSystem.Outlet.DelayBeforeStartup
upsdrv_updateinfo...
dstate_init: sock /var/state/ups/usbhid-ups-ups2 open on fd 5
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
Signal 2: exiting
Closing device

---------------------------------------------
Different UPS plugged into second USB port
----------------------------------------------
#/usr/local/ups/bin/usbhid-ups -a ups2 -DD
Network UPS Tools: 0.28 USB communication driver 0.28 - core 0.30 (2.2.0-)

debug level is '2'
Checking device (0000/0000) (002/001)
- VendorID: 0000
- ProductID: 0000
- Manufacturer: unknown
- Product: unknown
- Serial Number: unknown
- Bus: 002
Trying to match device
Device does not match - skipping
Checking device (09AE/2007) (002/005)
- VendorID: 09ae
- ProductID: 2007
- Manufacturer: Tripp Lite
- Product: TRIPP LITE UPS
- Serial Number: FW-2263 E
- Bus: 002
Trying to match device
Device matches
failed to claim USB device, trying 2 more time(s)...
detaching kernel driver from USB device...
trying again to claim USB device...
Warning: two different HID descriptors retrieved (Reportlen = 447 vs. 601)
HID descriptor retrieved (Reportlen = 601)
Report descriptor retrieved (Reportlen = 601)
Found HID device
Report Descriptor size = 601
Detected a UPS: Tripp Lite /TRIPP LITE UPS
Using subdriver: TrippLite HID 0.1 (experimental)
Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, 
Size: 8, Value: 1.000000
Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 
0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 
0, Size: 8, Value: 3.000000
Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, 
Offset: 0, Size: 8, Value: 120.000000
Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, 
Offset: 0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, 
Offset: 0, Size: 8, Value: 24.000000
Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 
0, Size: 8, Value: 2.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 
0, Size: 16, Value: 800.000000
Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, 
Offset: 0, Size: 16, Value: 800.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, 
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, 
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, 
Offset: 0, Size: 8, Value: 100.000000
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, 
ReportID: 0x32, Offset: 0, Size: 1, Value: 0.000000
Can't find object UPS.PowerSummary.PresentStatus.TLACPresent
Path: UPS.PowerSummary.PresentStatus.TLACPresent, Type: Input, ReportID: 
0x32, Offset: 1, Size: 1
Can't find object UPS.PowerSummary.PresentStatus.TLCharging
Path: UPS.PowerSummary.PresentStatus.TLCharging, Type: Input, ReportID: 
0x32, Offset: 2, Size: 1
Can't find object UPS.PowerSummary.PresentStatus.TLDischarging
Path: UPS.PowerSummary.PresentStatus.TLDischarging, Type: Input, ReportID: 
0x32, Offset: 3, Size: 1
Can't find object UPS.PowerSummary.PresentStatus.TLNeedReplacement
Path: UPS.PowerSummary.PresentStatus.TLNeedReplacement, Type: Input, 
ReportID: 0x32, Offset: 4, Size: 1
Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, 
ReportID: 0x32, Offset: 0, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 
0x32, Offset: 1, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 
0x32, Offset: 2, Size: 1, Value: 1.000000
Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 
0x32, Offset: 3, Size: 1, Value: 0.000000
Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, 
ReportID: 0x32, Offset: 4, Size: 1, Value: 0.000000
Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 
0x04, Offset: 0, Size: 16, Value: 12.000000
Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, 
ReportID: 0x23, Offset: 0, Size: 1, Value: 1.000000
Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, 
ReportID: 0x23, Offset: 1, Size: 1, Value: 0.000000
Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: 
Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0.000000
Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, 
Size: 8, Value: 1.000000
Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, 
Size: 8, Value: 120.000000
Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, 
Size: 8, Value: 60.000000
Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 
0, Size: 16, Value: 900.000000
Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 
0x15, Offset: 0, Size: 16, Value: 65535.000000
Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, ReportID: 0x51, 
Offset: 0, Size: 8, Value: 0.000000
Path: UPS.OutletSystem.Outlet.ffff0092, Type: Feature, ReportID: 0x52, 
Offset: 0, Size: 8, Value: 0.000000
Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature, ReportID: 0xb6, 
Offset: 0, Size: 8, Value: 1.000000
Path: UPS.ffff0010.[1].ffff007d, Type: Feature, ReportID: 0x6c, Offset: 0, 
Size: 16, Value: 8199.000000
Path: UPS.ffff0015.[1].ffff00c0, Type: Feature, ReportID: 0x96, Offset: 0, 
Size: 8, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00d2, Type: Feature, ReportID: 0xb4, Offset: 0, 
Size: 32, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c1, Type: Feature, ReportID: 0x97, Offset: 0, 
Size: 16, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c2, Type: Feature, ReportID: 0x98, Offset: 0, 
Size: 8, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c3, Type: Feature, ReportID: 0x99, Offset: 0, 
Size: 16, Value: 255.000000
Path: UPS.ffff0015.[1].ffff00c5, Type: Feature, ReportID: 0x9b, Offset: 0, 
Size: 16, Value: 3.000000
Path: UPS.ffff0015.[1].ffff00d6, Type: Feature, ReportID: 0xc2, Offset: 0, 
Size: 32, Value: 14.000000
Can't retrieve Report 154 (110): Connection timed out
Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID: 0x9a, Offset: 0, 
Size: 32
Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, 
Size: 16, Value: 1214.000000
Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, 
Offset: 0, Size: 16, Value: 135.000000
Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, 
Offset: 0, Size: 16, Value: 121.400002
Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, 
Offset: 0, Size: 16, Value: 59.900002
Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, 
ReportID: 0x22, Offset: 0, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, 
Offset: 1, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, 
Offset: 2, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 
0x22, Offset: 4, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature, ReportID: 0x22, 
Offset: 5, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, 
ReportID: 0x22, Offset: 6, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, 
ReportID: 0x22, Offset: 7, Size: 1, Value: 0.000000
Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, 
ReportID: 0x22, Offset: 14, Size: 1, Value: 0.000000
Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 
0x17, Offset: 0, Size: 16, Value: 65535.000000
Can't find object UPS.PowerSummary.RemainingCapacityLimit
Can't find object UPS.PowerSummary.WarningCapacityLimit
Can't find object UPS.BatterySystem.Temperature
Can't find object UPS.OutletSystem.Outlet.DelayBeforeStartup
Can't find object UPS.OutletSystem.Outlet.ActivePower
Can't find object UPS.PowerConverter.Output.ActivePower
Can't find object UPS.OutletSystem.Outlet.PercentLoad
Can't find object UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit
Can't find object UPS.PowerSummary.PresentStatus.FullyCharged
Can't find object UPS.PowerSummary.PresentStatus.TLACPresent
Can't find object UPS.PowerSummary.PresentStatus.TLDischarging
Can't find object UPS.PowerSummary.PresentStatus.TLCharging
Can't find object UPS.PowerSummary.PresentStatus.TLNeedReplacement
Can't find object UPS.PowerConverter.Output.HighVoltageTransfer
Can't find object UPS.PowerConverter.Output.LowVoltageTransfer
Can't find object UPS.PowerConverter.Output.Current
Can't find object UPS.PowerConverter.Output.Frequency
Can't find object UPS.OutletSystem.Outlet.DelayBeforeStartup
upsdrv_updateinfo...
dstate_init: sock /var/state/ups/usbhid-ups-ups2 open on fd 5
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
upsdrv_updateinfo...
Waiting for notifications...
Signal 2: exiting
Closing device

------------------------------------------------------------
    Thanks.



----- Original Message ----- 
From: "Arjen de Korte" <nut+users at de-korte.org>
To: "Todd Woods" <twoods at commo.com>
Cc: <nut-upsuser at lists.alioth.debian.org>
Sent: Friday, August 31, 2007 9:51 AM
Subject: Re: [Nut-upsuser] Multiple Tripplite OMNI900LCD


>> We have multiple TrippLite Omni900LCD UPS.  There are a couple pieces
>> of equipment connected to each UPS.  I would like to connect the UPSs to
>> one computer through USB which would shutdown the appropriate equipment
>> based on events monitored by upsmon using upssched.  I've configured NUT
>> using usbhid-ups driver and compiled/installed NUT.  I've done some
>> testing and it seems to work.  Unfortunately all the USB ports are on the
>> same bus for the computers that I could use for this and the TrippLites
>> seem to use the same serial number.  Any way to uniquely identify the
>> UPSs to NUT? Or maybe to set a value in the UPS that could be used to
>> identify the UPS?
>
> Could you run the driver in debug mode (start it up from the commandline
> with the -DD option added) like
>
> usbhid-ups -a <upsname> -DD
>
> with each time just one UPS attached? This command will dump all the
> variables that the UPS has and we *might* be able to tell them apart. The
> first few seconds of output should be enough.
>
> Best regards, Arjen
> -- 