[Nut-upsuser] Strange battery power shortage on an Unitek iZi UPS 525

Carlos Rodrigues carlos.efr at mail.telepac.pt
Sat Dec 22 18:19:59 UTC 2007


On Dec 22, 2007 2:34 PM, Ciprian Marius Vizitiu <cvizitiu at gbif.org> wrote:
> 3. Somehow the newer version of nut fails to correctly read/interpret the
> values from the UPS and decides to shut down earlier.

Unless you specify a "lowbatt" value in you ups.conf, the shutdown
will happen when the UPS raises the "low battery" flag. How this flag
is handled by megatec/powermust hasn't changed between 2.0.3 and
2.2.0.

> 4. ... any other ideas?

Either you "new" system draws enough extra power, or your UPS wasn't
fully charged when you did that second test, or your battery is going
bad, or a combination thereof.

It doesn't look like something related to NUT.

-- 
Carlos Rodrigues