On 1/29/07, Herman <herman at ofzo.nl> wrote:
> reset.watchdog - Reset watchdog timer | didn't test *no clue* what its
> for.
If that command is called, the UPS powers off in a couple of minutes
(and returns a minute after that). If it is called before the UPS
shuts down, it resets the timer back to zero.
If you put some script calling this command at 1 minute intervals (or
you make the "watchdog" daemon do it for you), then the UPS will power
off the box if it crashes, and then power it back on.
It's a poor man's watchdog, but it works. The box will never be down
for more than a minute or two.
--
Carlos Rodrigues