I had a similar problem with Ubuntu 6.10. There was a problem during
system shutdown and the whole script was not executed. I went back to
Ubuntu 6.6 and the problem went away. Check your syslog for a problem
with one of the nut programs shutting down. It was happening on any
shutdown not just the fsd.
Stuart Rackham wrote:
> Charles Lepple wrote:
>
>> On 7/25/07, Stuart Rackham <srackham at methods.co.nz> wrote:
>>
>>> Hi
>>>
>>> I'm having a problem with the bcmxcp_usb driver FSD command: everything
>>> seems to work apart from:
>>>
>>> upsmon -c fsd
>>>
>>> Environment: Ubuntu 7.04, nut 2.0.5-1, nut-usb 2.0.5-1, Powerware 3105
>>> UPS.
>>>
>>> upsd appears to send the FSD command to the UPS, upsmon then runs my
>>> NOTIFYCMD (which halts my PC) but the UPS just doesn't turn off.
>>> Here are the /var/log/daemon.log entries:
>>>
>> I have seen a similar problem with usbhid-ups on an MGE Pulsar
>> Evolution with Ubuntu 7.04. The machine shuts down on the LB signal,
>> but the UPS stays on.
>>
>> My suspicion is that there is something in the Ubuntu shutdown
>> procedure that is killing the driver (or upsd) before it can send the
>> shutdown command to the UPS.
>>
>> I haven't had a chance to verify this, though.
>>
>>
>
> Thanks for the fast response Charles.
>
> I changed the SHUTDOWNCMD to "/sbin/shutdown -H +1" which gives the
> driver 1 minute to send the command but it made no difference.
>
>
> Cheers, Stuart
>