[Nut-upsuser] Nut problems with Centos and Belkin UPS
Arjen de Korte
nut+users at de-korte.org
Sun Nov 25 09:40:59 UTC 2007
> On the bottom of the Belkin UPS unit - is the model number: F6C120auUNV
> The "au" is for Australia I think.
It probably is. We've seen other combinations here, like 'eu', 'uk' and so
on.
> "man belkinunv" states that F6C120-UNV is supported - and I assumed that
> the "au" would not prevent this.
> I plugged in the USB to gather the information you requested. My
> intention was to use the serial connection and probably still is, though
> if there is a solution via USB - I would certainly consider it.
There is and in many cases, it will be better than the serial connection.
Many UPS'es use a fairly verbose protocol, where a faster (USB) interface
helps to prevent timeouts.
> I tried "lsusb -W" (as suggested) but this seems an invalid option so I
> assume you mean "lsusb -v"
No, I wrote 'lsusb -vv' (double 'v'). Apparently, this looks very similar
in the font you're using... :-)
> Below is the relevant part of the output from "lsusb -v".
[...]
> Bus 004 Device 002: ID 050d:0912 Belkin Components
Good. This device is fully supported through the 'usbhid-ups' driver.
Although the stable nut-2.2.0 version works with this UPS, you may want to
try out the (improved) version from the trunk. If you don't know what the
latter is, just wait for the upcoming stable release, which should be
available shortly (Arnaud?)
Best regards, Arjen
More information about the Nut-upsuser