[Nut-upsuser] APC Back-UPS ES 550 reports zero(0) load
Arjen de Korte
nut+users at de-korte.org
Fri Oct 12 15:02:29 UTC 2007
> Any help or guidance would be appreciated. If I need to patch the
> source to add support for the ES 550, I can do that, with a little
> guidance.
There is nothing we can do about this. According to the output you
attached (which is great, thanks), the UPS is reporting this.
Path: UPS.PowerConverter.PercentLoad, Type: Feature, ReportID: 0x50,
Offset: 0, Size: 8, Value: 0.000000
We can't tell if the load is really zero or not, so if the UPS provides us
with bogus data, this will be displayed as is.
Best regards, Arjen
--