[Nut-upsuser] Belkin F6C100-UNV and "-x wait"

Arjen de Korte nut+users at de-korte.org
Sat Jan 19 08:29:21 UTC 2008


[...]

> Is there an equivalent to "-x wait" when using the same UPS with the
> 'usbhid-ups' driver?

I don't think this will be needed with the usbhid-ups. Why don't you just
try this out? Pull the mains plug from the UPS (it will now run on
batteries) and type

    # upsmon -c fsd

This will force an OB+LB situation (so that you don't have to wait until
the batteries are low). If both the UPS and the system are powered off,
you don't need this option.

Best regards, Arjen
-- 
Eindhoven - The Netherlands