I just used upsdrvctl shutdown. I don't care if it reboots or not. I'm
just concerned about power failure. Is there another way to check to see
if this will shutdown when the battery runs low? Is there anything else I
need to do?
Thanks
On Sun, 23 Nov 2008 21:19:26 -0000, Arjen de Korte
<nut+users at de-korte.org> wrote:
> Citeren Barb Smith <mystified at satx.rr.com>:
>
>> I ran a test and got the following:
>
> What test? Please be specific here.
>
>> Network UPS Tools - UPS driver controller 2.2.2
>> Network UPS Tools: 0.29 USB communication driver - core 0.33 (2.2.2)
>>
>> Using subdriver: TrippLite HID 0.2 (experimental)
>> Initiating UPS shutdown
>> Shutdown failed!
>> Driver failed to start (exit status=1)
>>
>> But the driver is started
>
> You UPS doesn't support enough HID PDC variables to be able to specify
> a shutdown with delay and a delayed restart. This makes that the
> 'shutdown.return' function can't be used (this is tried first).
> Unfortunately, it also doesn't seem to support 'shutdown.reboot'
> (which is tried if the first method fails). The only way to shutdown
> your UPS, is to send it a 'load.off.delay' command (and hope for the
> best that it will switch back on when the power returns). That command
> most likely will be supported (see the list of commands by running
> 'upscmd -l omni1000' when both driver and server are running), but
> isn't in the set of shutdown commands in nut-2.2.2. This has been in
> the development version for a while now, so it will be included in the
> next stable release when that comes out.
>
> Best regards, Arjen
--