[Nut-upsuser] HP/Compaq T700H UPS cable pinout

Kjell Claesson kjell.claesson at epost.tidanet.se
Wed Jan 14 23:57:01 UTC 2009


Den Wednesday 14 January 2009 23.34.27 skrev Mathew McBride:
Hi again Mathew,
> On 14/1/09 9:27 AM, Arjen de Korte wrote:
> > This probably needs to be multiplied by 100. Note that this value is
> > reported in percentage, not a factor. Either this, or the load can't
> > be right.
>
> It appears the UPS only provides a correct load percentage when the
> inverter is on (i.e battery or switching to trim mode)
>
> A correct load line is: "ups.load:  17.3"
>
From my PW5115. (should be the same as your T700H)
# upsc pw5115
ambient.temperature: 37
battery.charge: 90
battery.runtime: 810
battery.voltage: 13.47
driver.name: bcmxcp
driver.parameter.baud_rate: 9600
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.parameter.shutdown_delay: 10
driver.version: 2.3.0-1722M
driver.version.internal: 0.19
input.frequency: 50.34
input.voltage: 226
output.current: 0.68
output.current.nominal: 2.27
output.frequency: 50.00
output.phases: 1
output.voltage: 226
output.voltage.nominal: 230
ups.firmware: Inve:01.04
ups.load:  39.8
ups.model: PW5115 500i         500VA
ups.power: 199
ups.power.nominal: 500
ups.serial: XXXXXXXXXX
ups.status: OL

Regards
Kjell