[Nut-upsuser] APC Smart-UPS 1000

Kevin bakdong at gmail.com
Sun Jan 23 15:55:09 UTC 2011


on 23/01/2011 16:16 Arjen de Korte wrote:
> Citeren Kevin <bakdong at gmail.com>:
> 
> I see my error now. The above line should be moved up to before the 
> first occurence of { "ups.delay.shutdown", ... }. The first available 
> HID path that is found, will set the NUT mapping and there is one before 
> this line now, so the above will never be used in its present location.

Ok, try again....

   { "ups.delay.start", ST_FLAG_RW | ST_FLAG_STRING, 10, 
"UPS.PowerSummary.DelayBeforeStartup", NULL, DEFAULT_ONDELAY, 
HU_FLAG_ABSENT, NULL},
   { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, 
"UPS.Output.APCShutdownAfterDelay", NULL, "%.0f", HU_FLAG_QUICK_POLL, 
NULL },
   { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, 
"UPS.PowerSummary.DelayBeforeShutdown", NULL, DEFAULT_OFFDELAY, 
HU_FLAG_ABSENT, NULL},
   { "ups.timer.start", 0, 0, "UPS.PowerSummary.DelayBeforeStartup", 
NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},
   { "ups.timer.shutdown", 0, 0, "UPS.PowerSummary.DelayBeforeShutdown", 
NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},
   { "ups.timer.reboot", 0, 0, "UPS.PowerSummary.DelayBeforeReboot", 
NULL, "%.0f", HU_FLAG_QUICK_POLL, NULL},
   /* used by APC SmartUPS RM */
   { "ups.delay.start", ST_FLAG_RW | ST_FLAG_STRING, 10, 
"UPS.Output.DelayBeforeStartup", NULL, DEFAULT_ONDELAY, HU_FLAG_ABSENT, 
NULL},
   { "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10, 
"UPS.Output.DelayBeforeShutdown", NULL, DEFAULT_OFFDELAY, 
HU_FLAG_ABSENT, NULL},
   { "ups.timer.start", 0, 0, "UPS.Output.DelayBeforeStartup", NULL, 
"%.0f", HU_FLAG_QUICK_POLL, NULL},
   { "ups.timer.shutdown", 0, 0, "UPS.Output.DelayBeforeShutdown", NULL, 
"%.0f", HU_FLAG_QUICK_POLL, NULL},
   { "ups.timer.reboot", 0, 0, "UPS.Output.DelayBeforeReboot", NULL, 
"%.0f", HU_FLAG_QUICK_POLL, NULL},


Different....

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 33.3
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patch3
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 230.4
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 90
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d


./clients/upsrw -s ups.delay.shutdown=30 -u apcmon -p pass123 apc1500
OK

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 33.3
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patch3
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 231.8
output.voltage: 231.8
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d


Sorry....

# ./clients/upscmd -u apcmon -p pass123 apc1500 shutdown.return
OK

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 33.3
battery.type: PbAc
battery.voltage: 27.0
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patch3
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 231.8
output.voltage: 229.6
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: 88
ups.timer.start: 248
ups.vendorid: 051d


delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:-1 START:-1
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:-1 START:-1
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:88 START:248
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:88 START:248
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:86 START:246
delay.start:250 delay.shutdown:30 REBOOT:-1 SHUT:86 START:246

Regards,
Kevin.