Citeren Garðar Arnarsson <gardar op giraffi.net>:

>> Only if the UPS finds that the battery needs to be replaced it will report
>> the 'RB' status (replace battery). If it doesn't, all is well. The Q1
>> protocol that is used by your UPS doesn't support more verbose messages
>> (and neither does it report runtime or charge capacity) so there is nothing
>> more to report.
> When using the software supplied from the manufacturer I do see runtime and
> charge capacity messages.

Again, the Q1 protocol that is used by your UPS doesn't support more  
info than we already provide. There are ways to guesstimate the  
runtime and charge remaining, see 'man 8 blazer' for cues on how to  
set this up.

Best regards, Arjen
-- 