[Nut-upsuser] bcmxcp_usb can not communicate with Eaton Powerware 5110
Arnaud Quette
aquette.dev at gmail.com
Sat Aug 11 17:49:40 UTC 2012
2012/8/11 Massimo Gais <simosagi9 at gmail.com>
> On Fri, Aug 10, 2012 at 11:58 PM, Arnaud Quette <aquette.dev at gmail.com>
> wrote:
> >
> > the driver runs fine. you should get a good upsc output now.
> > the "Comm lost" msg are part of code adjustments needed, but the code
> > already handle this fine, and recovers (check "entering get_answer(33)"
> for
> > example).
> >
> > could you please confirm this by sending the upsc output, and starting
> > upsmon to monitor on the RPi?
> >
>
> Hello Arnaud,
>
Hi Masssimo,
> the driver seems indeed to be working fine, except the 'Lost comm'
> message at beginning. I started the upsc and I can get the expected
> output:
>
> ambient.temperature.high: 1
> battery.charge.low: 11
> battery.voltage: 13.7
> device.mfr: Eaton
> device.model: POWERWARE UPS 700i
> device.serial:
> device.type: ups
> driver.name: bcmxcp_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.shutdown_delay: 60
> driver.version: 2.6.5
> driver.version.internal: 0.26
> input.frequency: 49.9
> input.frequency.high: 55
> input.frequency.low: 45
> input.frequency.nominal: 50
> input.transfer.boost.high: 207
> input.transfer.high: 275
> input.transfer.low: 178
> input.transfer.trim.low: 250
> input.voltage: 238
> input.voltage.nominal: 230
> output.current: 0.6
> output.current.nominal: 1.8
> output.frequency: 49.9
> output.phases: 1
> output.voltage: 238
> output.voltage.nominal: 230
> ups.beeper.status: enabled
> ups.firmware: Cont:00.50 Inve:01.50
> ups.load: 33.3
> ups.mfr: Eaton
> ups.model: POWERWARE UPS 700i
> ups.power.nominal: 700
> ups.serial:
> ups.status: OL
> ups.test.result: Done and passed
>
> Before I'm ready to keep upsmon running and execute some tests with
> the UPS I have to do some cleanup but the basics seems to be in place.
>
great!
I'll probably bother you with some more testing, once the final code enter
the subversion repos.
cheers,
Arno
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20120811/310b3fca/attachment.html>
More information about the Nut-upsuser
mailing list