[Nut-upsuser] CyberPower DX600E won't switch up after power

Arnaud Quette aquette.dev at gmail.com
Wed Dec 5 20:38:45 UTC 2012


2012/12/1 Franck <franck at secretfatty.net>

> Date: Mon, 26 Nov 2012 19:34:28 +0100
>> From: Arnaud Quette <aquette.dev at gmail.com>
>> To: Franck <franck at secretfatty.net>
>> Cc: nut-upsuser at lists.alioth.**debian.org<nut-upsuser at lists.alioth.debian.org>
>> Subject: Re: [Nut-upsuser] CyberPower DX600E won't switch up after power
>>
>>
>>
>> right. we need to monitor the UPS while it's shutting down...
>>
>>
> Well I'd like to try that; but I'm 2000km from my UPS and It seems to be
> problematic for me to have the test done.
>
> But anyway I just got this reply to my quite random inquiry to CyberPower
> (wrong country) support:
>
> "I can only make vague guesses because I have never seen the product you
> have, and I am not familiar with the software you used to generate that
> data.  The following values stand out to me.
>
> battery.voltage: 4.7
>
> battery.voltage.nominal: 12
>
> ups.load: 31
>
> If I am interpreting them correctly your battery should be at 12 volts,
> but it is only at 4.7 volts?
>
> And the UPS load is 31%?
>
>
>
> If the battery is at 4.7 volts it will not pass the power on self-test. It
> needs to be somewhere above 10 volts (Perhaps 10.5 or 11)before it will
> pass the self-test and let the ups turn on.
>
>
>
> Other possibilities.
>
> If you have the computers set to auto start when power is restored, they
> will turn on simultaneously, if there has been a power loss that
> significantly drained the batteries, they will have very little energy when
> the power is restored.  The power on self test checks the CyberPower’s
> ability to run on battery by stopping access to wall power and forcing the
> UPS on to battery power.  If the batteries are very low and the auto
> startup of the computers hits while they are being tested then the load of
> the computers on the weak battery could cause the voltage to drop and the
> self-test would fail.
>
>
>
> One or both of your computers has an Active PFC power supply and your UPS
> is not a sine wave ups. If you are not familiar with this problem, just
> search the internet on the terms “active pfc” and “sine”
>
>
>
> The battery in the UPS could be defective.
>
>
>
> Again.  I do not know the product you are asking about so I can’t provide
> an accurate diagnosis.  I can only suggest possibilities.
>
> "
>
> So if the guy os right and this might be a battery problem.


hem, ups.load is the load on the UPS output.
what you were looking for is probably battery.charge.

battery.voltage seems indeed wrong, but to me, that's another issue.
yours is with the restart function, that is tied to the USB/HID data I
mentioned before.
monitoring these counting down should help understanding how these actually
behave.

it's true that being 2000kms away doesn't make things easy.
but there each problem has at least 1 solution:
instead of doing a full reboot cycle, we can just monitor for 10 seconds,
and cancel the procedure

- stop NUT after the reboot,
- restart the driver in debug more (/lib/nut/usbhid-ups -DDDDD myups)
and upsd (simply type "upsd" as root) in another term
- then execute "upscmd -u ... -p ... myups shutdown.return"
CAUTION: wait no more than 10-15 seconds!!! Otherwise, your server will
crash!!!
possibly monitor your unit with upsc
- then execute "upscmd -u ... -p ... myups shutdown.cancel" (mention -u and
-p to avoid loosing a few seconds!)
-then Ctrl+C in the driver term.
and send back the driver output, in compressed form.
you can then restart everything as usual...

cheers,
Arnaud
-- 
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr