[Nut-upsuser] Tripp Lite SMART1000RM2U

Charles Lepple clepple at gmail.com
Mon Dec 10 01:30:03 UTC 2012


On Dec 7, 2012, at 3:01 AM, Dawning Sky wrote:

> 1. battery.charge doesn't report correct charge level when the UPS is
> On Batter.  It just reports 0.  Even though it will report 100 when on
> line power.

I wonder if this is connected with the following:

> ups.debug.S: 31 34 30 00 64 30 0d '140.d0.'

As I remember it, '4' is the status character representing "self-test status is unknown". You might need to do a deep discharge test first before the state-of-charge constants are programmed into the UPS.

If you can start a deep discharge test from the front panel, I'd try that first. Otherwise, there is a "test.battery.start" command in NUT which might be what you're looking for. However, bear in mind that this driver was written without the benefit of protocol documentation.

-- 
Charles Lepple
clepple at gmail






More information about the Nut-upsuser mailing list