[Nut-upsuser] false low battery alarm
Vieri
rentorbuy at yahoo.com
Thu Feb 28 09:10:50 UTC 2013
Hi,
I have two types of UPS devices and one of them (APC) gave me a false "low battery" alert. I can't reproduce the problem... Also, there was nothing apparently wrong with the UPS at the time of the false alert. All I could do was grab the driver values within a minute after the "low battery" notification.
These are the values:
battery.runtime.low : 120
battery.voltage : 55.65
battery.voltage.nominal : 048
device.mfr : APC
device.model : SMART-UPS 5000 RM DL4
device.serial : CS0603110575
device.type : ups
driver.name : apcsmart
driver.parameter.pollinterval : 2
driver.parameter.port : /dev/UPS-1
driver.version : 2.6.3
driver.version.internal : 3.0
input.frequency : 50.00
input.quality : FF
input.sensitivity : H
input.transfer.high : 253
input.transfer.low : 196
input.transfer.reason : simulated power failure or UPS test
input.voltage : 224.9
input.voltage.maximum : 224.9
input.voltage.minimum : 223.6
output.voltage : 224.9
output.voltage.nominal : 230
ups.delay.shutdown : 020
ups.delay.start : 000
ups.firmware : 112.1DL4.I
ups.id : UPS_IDEN
ups.load : 069.6
ups.mfr : APC
ups.mfr.date : 01/10/06
ups.model : SMART-UPS 5000 RM DL4
ups.serial : CS0603110575
ups.status : OL
ups.temperature : 027.4
ups.test.interval : 1209600
ups.test.result : NO
The NUT version installed is 2.6.3 and I'm using a serial-to-USB hub (1 usb port and 4 serial ports). The brand is ATEN,
My upssched.conf contains:
AT LOWBATT INF-APC at 127.0.0.1 EXECUTE lowbatt-now-apc
and my upssched custom script notified me of the LOWBATT event.
My ups.conf contains:
[INF-APC]
driver = apcsmart
port = /dev/UPS-1
desc = "UPS Monitor - ATEN port 2 - APC UPS"
If I were to update to nut 2.6.5 (I can't do it for now) would I solve this issue (ie. is it a known issue?)?
Thanks,
Vieri