[Nut-upsuser] false low battery alarm

Charles Lepple clepple at gmail.com
Thu Feb 28 12:58:47 UTC 2013


On Feb 28, 2013, at 4:10 AM, Vieri wrote:

> input.transfer.reason : simulated power failure or UPS test 

Sounds like it was the UPS self test?

> ups.mfr.date : 01/10/06

If this is the original battery, it is certainly possible that it has built up enough internal resistance that the voltage reads normal when idle, but it dips too low during a test.

> ups.test.interval : 1209600

1209600 seconds = 14 days, so if it does it again in two weeks...

-- 
Charles Lepple
clepple at gmail