On Jul 9, 2013, at 9:04 AM, Gregor Burck wrote:
> we bought two Smart-UPS X 1500 FW:UPS 09.1 / ID=20
[...]
> I see there should be problems to get it work with a free daemon like nut, but are there some hints using it?
> In my ups.conf I tried:
> 
> [apc001]
>        driver = apcsmart
>        port = auto
>        desc = "Smart APC"
Only the USB drivers should work with port = auto. The "apcsmart" driver connects over the serial port, so under Linux, you would need to pass something like "port = /dev/ttyS0".
To connect over USB, change to "driver = usbhid-ups".
> 
> And I get broadcast messages when I connect/disconnect the device like:
> Broadcast Message from root at glus  
>        (somewhere) at 14:24 ...                                               
> 
> Communications restored with UPS glustersv001 
Not sure I understand what you did here. Are you disconnecting the USB or AC connection? Also, apcsmart shouldn't have connected at all with "port = auto".
-- 