[Nut-upsuser] Tripp-Lite BCPERS450 shutdown/restart problems
Ken Olum
kdo at cosmos.phy.tufts.edu
Mon Dec 18 16:37:36 UTC 2017
I have a Tripp-Lite BCPERS450, connected to a system running Ubuntu
16.04.3 LTS and NUT 2.7.2-4ubuntu1.2. I had to make my own
/lib/systemd/system-shutdown/nutshutdown, but now everything is working
except for powering on and off the UPS. Regardless of the settings of
offdelay and ondelay in upsconf, and regardless of whether the AC power
is on, when I say "upsdrvctl shutdown" the UPS turns off the power to
the system instantly and turns it back on in ten seconds.
Any ideas how to get more reasonable behavior, in particular not
turning the system back on until the AC power is restored?
Here is the status reported by upsc:
battery.charge: 100
battery.runtime: 4050
battery.type: PbAC
battery.voltage: 13.4
battery.voltage.nominal: 12.0
device.mfr: Tripp Lite
device.model: Tripp Lite UPS
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 20
driver.parameter.ondelay: -1
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.7.2
driver.version.data: TrippLite HID 0.81
driver.version.internal: 0.38
input.frequency: 60.0
input.voltage: 118.2
input.voltage.nominal: 120
output.frequency.nominal: 60
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.mfr: Tripp Lite
ups.model: Tripp Lite UPS
ups.power.nominal: 450
ups.productid: 2010
ups.status: OL
ups.timer.reboot: 65535
ups.timer.shutdown: 65535
ups.vendorid: 09ae
ups.watchdog.status: 0
I said /lib/nut/usbhid-ups -DD -a bcpers450
and got:
Network UPS Tools - Generic HID driver 0.38 (2.7.2)
USB communication driver 0.32
0.000000 debug level is '2'
0.000808 upsdrv_initups...
0.017090 Checking device (1D6B/0003) (002/001)
0.033199 - VendorID: 1d6b
0.033215 - ProductID: 0003
0.033217 - Manufacturer: unknown
0.033220 - Product: unknown
0.033222 - Serial Number: unknown
0.033224 - Bus: 002
0.033227 Trying to match device
0.033232 Device does not match - skipping
0.033289 Checking device (09AE/2010) (001/014)
0.036998 - VendorID: 09ae
0.037011 - ProductID: 2010
0.037014 - Manufacturer: Tripp Lite
0.037018 - Product: Tripp Lite UPS
0.037021 - Serial Number: unknown
0.037024 - Bus: 001
0.037027 Trying to match device
0.037042 Device matches
0.037886 HID descriptor too short (expected 8, got 0)
0.037901 HID descriptor length 613
0.057332 Report Descriptor size = 613
0.057663 Using subdriver: TrippLite HID 0.81
0.058304 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 2
0.059008 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 3
0.059619 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8, Value: 1
0.060167 Path: UPS.PowerSummary.ffff00d9, Type: Feature, ReportID: 0xc0, Offset: 0, Size: 8, Value: 5
0.060709 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
0.061316 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
0.061905 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
0.062534 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 2
0.063079 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8, Value: 1
0.063619 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050
0.063658 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050
0.064254 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
0.064292 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
0.064954 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8, Value: 100
0.065578 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
0.066133 Path: UPS.PowerSummary.PresentStatus.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 1182
0.066673 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
0.066711 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
0.066736 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
to 0.066756 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
0.066777 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
0.066798 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 5, Size: 1, Value: 0
0.066819 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
0.066839 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
0.066863 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
0.066886 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
0.066908 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
0.066931 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
0.066953 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
0.066977 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0
0.067000 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
0.067022 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
0.067583 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12
0.068064 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 0, Size: 1, Value: 1
0.068087 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 1, Size: 1, Value: 0
0.068108 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
0.068625 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0
0.069120 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
0.069695 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
0.070252 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 450
0.070916 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
0.071567 Path: UPS.OutletSystem.Outlet.ffff00bc, Type: Feature, ReportID: 0xe0, Offset: 0, Size: 16, Value: 0
0.072081 Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 0
0.072701 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
0.073273 Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature, ReportID: 0xb6, Offset: 0, Size: 8, Value: 1
0.073997 Path: UPS.TLCustom.[1].CommunicationProtocolVersion, Type: Feature, ReportID: 0x6c, Offset: 0, Size: 16, Value: 8208
0.074644 Path: UPS.ffff0015.[1].ffff00c0, Type: Feature, ReportID: 0x96, Offset: 0, Size: 8, Value: 255
0.075266 refresh_report_buffer: expected 5 bytes, but got 2 instead
0.075310 Path: UPS.ffff0015.[1].ffff00d2, Type: Feature, ReportID: 0xb4, Offset: 0, Size: 32, Value: 255
0.075908 refresh_report_buffer: expected 5 bytes, but got 2 instead
0.075952 Path: UPS.ffff0015.[1].ffff00d3, Type: Feature, ReportID: 0xb5, Offset: 0, Size: 32, Value: 255
0.076633 Path: UPS.ffff0015.[1].ffff00c1, Type: Feature, ReportID: 0x97, Offset: 0, Size: 16, Value: 255
0.077150 Path: UPS.ffff0015.[1].ffff00c2, Type: Feature, ReportID: 0x98, Offset: 0, Size: 8, Value: 255
0.077710 Path: UPS.ffff0015.[1].ffff00c3, Type: Feature, ReportID: 0x99, Offset: 0, Size: 16, Value: 255
0.078289 Path: UPS.ffff0015.[1].ffff00c5, Type: Feature, ReportID: 0x9b, Offset: 0, Size: 16, Value: 3
0.079011 Path: UPS.ffff0015.[1].ffff00d6, Type: Feature, ReportID: 0xc2, Offset: 0, Size: 32, Value: 14
0.079620 libusb_get_report: error sending control message: Operation not permitted
0.079665 Can't retrieve Report c1: Operation not permitted
0.079687 Path: UPS.ffff0015.[1].ffff00d8, Type: Feature, ReportID: 0xc1, Offset: 0, Size: 32
0.080267 Path: UPS.ffff0015.[1].ffff00d7, Type: Feature, ReportID: 0xc3, Offset: 0, Size: 32, Value: 1
0.080847 libusb_get_report: error sending control message: Operation not permitted
0.080879 Can't retrieve Report 9a: Operation not permitted
0.080937 Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID: 0x9a, Offset: 0, Size: 32
0.081647 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 134
0.082228 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 118.2
0.083058 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 60
0.083646 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
0.083681 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0
0.083704 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0
0.083723 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0
0.083741 Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature, ReportID: 0x22, Offset: 5, Size: 1, Value: 0
0.083758 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
0.083777 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
0.083799 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
0.084531 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
0.084569 Report descriptor retrieved (Reportlen = 613)
0.084578 Found HID device
0.084591 Detected a UPS: Tripp Lite /Tripp Lite UPS
0.084664 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
0.084726 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050
0.084748 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12
0.084772 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 134
0.084795 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4
0.086130 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
0.086156 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
0.086175 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0
0.086201 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
0.086224 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 450
0.086272 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
0.086305 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
0.086325 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
0.086346 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0
0.086365 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
0.086385 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
0.086402 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
0.086420 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
0.086439 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
0.086486 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
0.086508 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0
0.086527 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0
0.086546 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0
0.086565 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
0.086583 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
0.086603 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
0.086622 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
0.086651 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 118.2
0.086672 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 60
0.086722 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
0.086756 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
0.086781 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0
0.086797 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0
0.086813 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0
0.086834 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
0.086862 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
0.086881 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
0.086897 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
0.086912 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
0.086928 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
0.086944 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
0.086960 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
0.086975 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
0.086990 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
0.087010 find_nut_info: unknown info type: load.on.delay
0.087022 find_nut_info: unknown info type: load.on.delay
0.087041 upsdrv_initinfo...
0.087055 upsdrv_updateinfo...
0.338069 libusb_get_interrupt: Connection timed out
0.338103 Got 0 HID objects...
0.338178 Quick update...
0.338215 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
0.338242 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
0.338262 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
0.338277 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0
0.338303 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
0.338337 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
0.338352 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
0.338373 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
0.338503 dstate_init: sock /var/run/nut/usbhid-ups-bcpers450 open on fd 5
0.338534 upsdrv_updateinfo...
0.343549 Got 1 HID objects...
0.343585 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050
0.343603 Quick update...
0.343628 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
0.343632 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
0.343636 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
0.343639 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0
0.343642 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
0.343645 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
0.343647 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
0.343650 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
2.340759 upsdrv_updateinfo...
2.359621 Got 8 HID objects...
2.359637 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 0, Size: 1, Value: 0
2.359646 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
2.359653 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
2.359659 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
2.359665 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 4, Size: 1, Value: 0
2.359672 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 5, Size: 1, Value: 0
2.359677 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
2.359683 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
2.359690 Quick update...
2.360150 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
2.360609 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
2.360614 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1
2.360617 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0
2.360620 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1
2.360623 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1
2.360625 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0
2.360628 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
Thanks very much.
Ken
More information about the Nut-upsuser