[Nut-upsuser] [HCL] Powerware PW5125 with driver bcmxcp

Mike the.lists at mgm51.com
Tue Feb 21 15:14:02 UTC 2017


On 2/21/2017 8:34 AM, Charles Lepple wrote:
> On Feb 20, 2017, at 11:19 AM, Mike <the.lists at mgm51.com> wrote:
>>
>> This UPS is already listed in the compatibility list.   But I wanted to
>> add the instant commands supported by upscmd:
>>
> ...
>> and note that a delayed shutoff command is not available.
>>
>> (NUT 2.7.4 on OpenBSD 6.0)
>>
>> imo, it would be useful if this info were submitted along with the other
>> info when an HCL entry is submitted.
> 
> Agreed, and we do ask for upsc, upsrw and upscmd output here:
> 
> http://networkupstools.org/stable-hcl.html#footnotes
> 
> Let us know if there is another place we should update.
> 
> To get an idea of the age of the unit, is this a pre-merger Powerware, or is it also labeled Eaton?
> 
> Given the age of the other PW5125 entries, can you please send upsc (and upsrw) output as well? Feel free to mask portions of the serial number, but at least for other vendors, the first few characters can be useful for identifying differences in the underlying implementation. Hopefully the ups.firmware value is sufficient.
> 
> Thanks!
> 

I'm attaching a text file with the requested info.

The company logo on the front panel says, "Powerware."  The company name
in the upsc output is Eaton.  The serial number decal on the back of the
unit also says "Powerware."  My hazy memory thinks that I bought the
unit in 2006.



> Let us know if there is another place we should update.

That place is fine.  I wrote that in my post more to encourage others to
submit the info for the UPS they use.  :)


btw, back in December, I was having this conversation...

http://lists.alioth.debian.org/pipermail/nut-upsuser/2016-December/010461.html

which went quiet while I was waiting for a reply.   I'm back in a spot
where I can play with that UPS again, if there is something you'd like
me to do with it.


Let me know if there is anything else you need...
-------------- next part --------------

via NUT 2.7.4, FreeBSD 11.0

# upsc

ambient.temperature: 42
ambient.temperature.high: 70
battery.charge: 95
battery.charge.restart: 76
battery.charger.status: resting
battery.energysave.delay: 0
battery.energysave.load: 0
battery.packs: 1
battery.runtime: 2760
battery.runtime.low: 2
battery.voltage: 52.26
device.mfr: Eaton
device.model: PW5125     1500i
device.part: 05146632-5501   
device.serial: UX475A0xxxxx      
device.type: ups
driver.name: bcmxcp
driver.parameter.baud_rate: 9600
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/cuaU0
driver.parameter.shutdown_delay: 120
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.internal: 0.31
input.frequency: 60.08
input.frequency.high: 65
input.frequency.low: 55
input.frequency.nominal: 60
input.transfer.boost.high: 108
input.transfer.high: 144
input.transfer.low: 84
input.transfer.trim.low: 127
input.voltage: 119
input.voltage.nominal: 120
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 3
outlet.1.id: 1
outlet.1.status: on/closed
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 5
outlet.2.id: 2
outlet.2.status: on/closed
output.current:  0.0
output.current.nominal: 13.6
output.frequency: 60.08
output.frequency.nominal: 60
output.phases: 1
output.voltage: 119
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.description: Line-Interactive UPS, Single Phase
ups.firmware: Cont:01.01 Inve:01.01
ups.load:  13.7
ups.mfr: Eaton
ups.model: PW5125     1500i
ups.power: 205
ups.power.nominal: 1500
ups.realpower: 132
ups.serial: UX475A0xxxx    
ups.status: OL
ups.test.result: No test initiated





# upsrw

[battery.energysave.delay]
Delay before switch off UPS if on battery and load level low (min)
Type: STRING
Maximum length: 3
Value: 0

[battery.energysave.load]
Switch off UPS if on battery and load level lower (percent)
Type: STRING
Maximum length: 3
Value: 0

[battery.packs]
Number of battery packs
Type: STRING
Maximum length: 1
Value: 1

[outlet.1.delay.shutdown]
Interval to wait before shutting down this outlet (seconds)
Type: STRING
Maximum length: 5
Value: -1

[outlet.1.delay.start]
Interval to wait before restarting this outlet (seconds)
Type: STRING
Maximum length: 5
Value: 3

[outlet.2.delay.shutdown]
Interval to wait before shutting down this outlet (seconds)
Type: STRING
Maximum length: 5
Value: -1

[outlet.2.delay.start]
Interval to wait before restarting this outlet (seconds)
Type: STRING
Maximum length: 5
Value: 5

[output.voltage.nominal]
Nominal output voltage (V)
Type: STRING
Maximum length: 3
Value: 120





# upscmd

Instant commands supported on UPS [PW5125]:

beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
load.on - Turn on the load immediately
outlet.1.load.off - Turn off the load on outlet 1 immediately
outlet.1.load.on - Turn on the load on outlet 1 immediately
outlet.1.shutdown.return - Turn off the outlet 1 and return when power is back
outlet.2.load.off - Turn off the load on outlet 2 immediately
outlet.2.load.on - Turn on the load on outlet 2 immediately
outlet.2.shutdown.return - Turn off the outlet 2 and return when power is back
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
test.battery.start - Start a battery test