[Nut-upsuser] Emerson Liebert GXT4
Charles Lepple
clepple at gmail.com
Tue Jun 6 12:46:48 UTC 2017
On Jun 5, 2017, at 1:05 AM, zefanjas <nut at zefanjas.de> wrote:
>> I think the Logical Min/Max are responsible for the battery voltages, since there are larger values in the log:
>>
>> 0.240091 Report[buf]: (5 bytes) => 05 51 00 48 00
>> 0.240097 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x05, Offset: 0, Size: 16, Value: 1
>> 0.240127 Report[buf]: (5 bytes) => 05 51 00 48 00
>> 0.240138 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x05, Offset: 16, Size: 16, Value: 0
>>
>> Does a battery voltage of 72 Volts (0x48) sound right?
>
> Almost. I've justed checked the UPS. When it's 100% charged the battery
> voltage is 82 Volts.
Right, I meant the nominal voltage is 72V. The actual voltage in that log is 0x51, or 81V.
I merged the PID=0000 change, so the productid parameter should not be necessary for this UPS in the next NUT release.
More information about the Nut-upsuser