[Nut-upsuser] Help with Elite 800VA usb UPS
Andrea de Lutti
adelutti at gmail.com
Tue Jun 27 13:23:43 UTC 2017
Sorry, I didn't received it...
I don't have any REPLBATT message, but when in battery test I have OL CAL
status: it would be good to have the result.
Anyway I still not receive any email on any test (power cord disconnected
and/or reconnected for example)
Does the runtime calibration test alter the values of ups.conf? Or do I
have to change it manually? Which would be the right procedure for changing
the battery for calibrating NUT (over the manufacturer's suggestions)?
Thank you lots,
Andrea
2017-06-27 14:50 GMT+02:00 Charles Lepple <clepple at gmail.com>:
> On Jun 26, 2017, at 7:03 AM, Andrea de Lutti <adelutti at gmail.com> wrote:
> >
> > Are there no warnings for battery test?
>
> not sure if you saw my reply on 2016-06-17:
>
> Do you mean a notification that a test is in progress, or something for
> the results?
>
> There is the REPLBATT message in upsmon when the battery test fails, but I
> don't think the generic Qx protocol supports the RB status flag.
>
> You could possibly trigger on the OB status and look for the CAL flag in
> ups.status as well, but I haven't tried to automate that.
>
> ^^^ If you run "upsc $UPSNAME ups.status", do you see CAL in the status
> string during a battery test? If not, your UPS is not reporting this the
> way that the driver expects.