Ah yes - the firmware line is there. Here's the full listing:
# upsc eaton at localhost
Init SSL without certificate database
battery.capacity: 9.00
battery.charge: 100
battery.charge.low: 20
battery.charge.restart: 0
battery.energysave: no
battery.protection: yes
battery.runtime: 1069
battery.type: PbAc
device.mfr: EATON
device.model: Eaton 5P 2200
device.serial: G103G45001
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.7.2
driver.version.data: MGE HID 1.33
driver.version.internal: 0.38
input.current: 0.00
input.frequency: 59.9
input.frequency.extended: no
input.frequency.nominal: 60
input.sensitivity: normal
input.transfer.boost.low: 102
input.transfer.high: 151
input.transfer.low: 89
input.transfer.trim.high: 132
input.voltage: 119.2
input.voltage.extended: no
input.voltage.nominal: 120
outlet.1.autoswitch.charge.low: 0
outlet.1.delay.shutdown: 65535
outlet.1.delay.start: 3
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 1
outlet.1.status: on
outlet.1.switchable: yes
outlet.2.autoswitch.charge.low: 0
outlet.2.delay.shutdown: 65535
outlet.2.delay.start: 6
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 2
outlet.2.status: on
outlet.2.switchable: yes
outlet.desc: Main Outlet
outlet.id: 0
outlet.switchable: no
output.current: 4.30
output.frequency: 59.9
output.frequency.nominal: 60
output.powerfactor: 0.92
output.voltage: 119.2
output.voltage.nominal: 120
ups.alarm: Fatal EEPROM fault!
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.efficiency: 88
ups.firmware: 04
ups.load: 24
ups.load.high: 105
ups.mfr: EATON
ups.model: Eaton 5P 2200
ups.power: 513
ups.power.nominal: 2200
ups.productid: ffff
ups.realpower: 475
ups.realpower.nominal: 1980
ups.serial: G103G45001
ups.shutdown: enabled
ups.start.auto: yes
ups.start.battery: yes
ups.start.reboot: yes
ups.status: ALARM OL CHRG
ups.test.interval: 604800
ups.test.result: Done and passed
ups.timer.shutdown: 0
ups.timer.start: 0
ups.type: offline / line interactive
ups.vendorid: 0463
Nothing special done with the unit - it's a new unit, replaced an
older APC model.
Thank you,
Chris
More information about the Nut-upsuser
mailing list