[Nut-upsuser] APC Back-UPS CS 650 offdelay and startdelay

Karol Olszewski karol.olszewski at ipflow.pl
Fri Aug 24 22:13:35 BST 2018


W dniu 24.08.2018 o 13:10, Charles Lepple pisze:
> Sorry, I didn't mean to imply that the master branch was necessarily going to be different, just wanted to make sure you had everything set up to recompile. The real test is to see if things change after commenting out that line (such as by changing it to start with "//"):
>
> // { "shutdown.return", 0, 0, "UPS.Output.APCDelayBeforeReboot", NULL, "1", HU_TYPE_CMD, NULL },
>
> For reference, here's the thread related to adding that mapping: https://alioth-lists.debian.net/pipermail/nut-upsuser/2011-January/006550.html
>
Hi
I'm bit closer :)
Acctually change "UPS.Output.APCDelayBeforeReboot" to

  { "shutdown.return", 0, 0, "UPS.Output.APCShutdownAfterDelay", NULL,
"90", HU_TYPE_CMD, NULL },

Now, UPS turn off load after 90 sec, but not power ON when power is back


-- 
Karol Olszewski ipflow.pl