[Nut-upsuser] Eaton 5PX after battery replacement still says "replace battery" in NUT

James Whitwell jams at momento.com.au
Tue Jan 16 23:07:48 UTC 2018


Hi,

This might be a simple thing to fix, but I can’t figure it out.  We replaced the battery for the first time in our Eaton 5PX a couple of weeks ago, but we haven’t been able to clear the “ups.alarm: replace battery!” status.

Details of our installation are:
OS: Debian 6
NUT version: 2.7.4
Installation method: from source tarball
UPS device: Eaton 5PX2000IRT, 240V, 1800W, 2000VA, bought in October 2013

Here’s the status as reported by upsc:

battery.capacity: 9.00
battery.charge: 100
battery.charge.low: 20
battery.charge.restart: 0
battery.charger.status: floating
battery.energysave: no
battery.protection: yes
battery.runtime: 1032
battery.type: PbAc
device.mfr: EATON
device.model: Eaton 5PX 2000
device.serial: G098D27047
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.parameter.vendorid: 0463
driver.version: 2.7.4
driver.version.data: MGE HID 1.39
driver.version.internal: 0.41
input.current: 0.00
input.frequency: 49.9
input.frequency.extended: no
input.frequency.nominal: 50
input.sensitivity: normal
input.transfer.boost.low: 184
input.transfer.high: 294
input.transfer.low: 160
input.transfer.trim.high: 265
input.voltage: 235.0
input.voltage.extended: no
input.voltage.nominal: 230
outlet.1.autoswitch.charge.low: 0
outlet.1.current: 1.20
outlet.1.delay.shutdown: 65535
outlet.1.delay.start: 3
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 1
outlet.1.power: 282
outlet.1.powerfactor: 57.00
outlet.1.realpower: 162
outlet.1.status: on
outlet.1.switchable: yes
outlet.2.autoswitch.charge.low: 0
outlet.2.current: 0.40
outlet.2.delay.shutdown: 65535
outlet.2.delay.start: 6
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 2
outlet.2.power: 94
outlet.2.powerfactor: 72.00
outlet.2.realpower: 68
outlet.2.status: on
outlet.2.switchable: yes
outlet.current: 1.00
outlet.desc: Main Outlet
outlet.id: 0
outlet.power: 276
outlet.powerfactor: 99.00
outlet.realpower: 274
outlet.switchable: no
output.current: 2.60
output.frequency: 49.9
output.frequency.nominal: 50
output.powerfactor: 0.82
output.voltage: 235.0
output.voltage.nominal: 230
ups.alarm: Replace battery!
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.efficiency: 95
ups.firmware: 06
ups.load: 30
ups.load.high: 105
ups.mfr: EATON
ups.model: Eaton 5PX 2000
ups.power: 611
ups.power.nominal: 2000
ups.productid: ffff
ups.realpower: 504
ups.realpower.nominal: 1800
ups.serial: G098D27047
ups.shutdown: enabled
ups.start.auto: yes
ups.start.battery: yes
ups.start.reboot: yes
ups.status: ALARM OL CHRG RB
ups.test.interval: 604800
ups.test.result: Done and passed
ups.timer.shutdown: 0
ups.timer.start: 0
ups.type: offline / line interactive
ups.vendorid: 0463

And here’s the output from /usr/local/nut/bin/usbhid-ups -DD -a <ups-name>

I had to ^C it after a bit as it was just retrying.  Looks like a communications problem with the UPS over the USB cable?  We’ve unplugged it and replugged it half a dozen times before this.

Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
   0.000000	debug level is '2'
   0.000279	upsdrv_initups...
   0.000424	Checking device (0463/FFFF) (002/008)
   0.275036	- VendorID: 0463
   0.275054	- ProductID: ffff
   0.275056	- Manufacturer: EATON
   0.275059	- Product: Eaton 5PX
   0.275061	- Serial Number: G098D27047
   0.275063	- Bus: 002
   0.275065	- Device release number: 0100
   0.275068	Trying to match device
   0.275102	Device matches
   0.309531	HID descriptor length 2580
   4.749244	Report Descriptor size = 2580
   4.749684	Using subdriver: MGE HID 1.39
   4.749691	234 HID objects found
   4.778444	Path: UPS.BatterySystem.Battery.AudibleAlarmControl, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 2
   4.816700	Path: UPS.BatterySystem.Battery.BatteryID, Type: Feature, ReportID: 0x20, Offset: 0, Size: 8, Value: 1
   4.850696	Path: UPS.BatterySystem.Battery.Count, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 0
   4.886600	Path: UPS.BatterySystem.Battery.DeepDischargeProtection, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 1
   4.925954	Path: UPS.BatterySystem.Battery.DesignCapacity, Type: Feature, ReportID: 0x23, Offset: 0, Size: 32, Value: 32400
   4.964082	Path: UPS.BatterySystem.Battery.PresentStatus.Present, Type: Feature, ReportID: 0x27, Offset: 0, Size: 8, Value: 1
   4.964102	Path: UPS.BatterySystem.Battery.PresentStatus.Present, Type: Input, ReportID: 0x27, Offset: 0, Size: 8, Value: 1
   4.994604	Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1
   5.033884	Path: UPS.BatterySystem.Battery.TestPeriod, Type: Feature, ReportID: 0x25, Offset: 0, Size: 32, Value: 604800
   5.033899	Path: UPS.BatterySystem.BatterySystemID, Type: Feature, ReportID: 0x20, Offset: 8, Size: 8, Value: 1
   5.066597	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
   5.066620	Path: UPS.BatterySystem.Charger.ChargerID, Type: Feature, ReportID: 0x20, Offset: 16, Size: 8, Value: 1
   5.103461	Path: UPS.BatterySystem.Charger.ChargerType, Type: Feature, ReportID: 0x26, Offset: 0, Size: 8, Value: 4
   5.103480	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
   5.103489	Path: UPS.BatterySystem.Charger.PresentStatus.Floating, Type: Feature, ReportID: 0x27, Offset: 8, Size: 8, Value: 1
   5.103557	Path: UPS.BatterySystem.Charger.PresentStatus.Floating, Type: Input, ReportID: 0x27, Offset: 8, Size: 8, Value: 1
   5.103569	Path: UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x27, Offset: 16, Size: 8, Value: 0
   5.103579	Path: UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Input, ReportID: 0x27, Offset: 16, Size: 8, Value: 0
   5.103589	Path: UPS.BatterySystem.Charger.PresentStatus.Used, Type: Feature, ReportID: 0x27, Offset: 24, Size: 8, Value: 1
   5.103599	Path: UPS.BatterySystem.Charger.PresentStatus.Used, Type: Input, ReportID: 0x27, Offset: 24, Size: 8, Value: 1
   5.103609	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Feature, ReportID: 0x27, Offset: 32, Size: 8, Value: 0
   5.103619	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Input, ReportID: 0x27, Offset: 32, Size: 8, Value: 0
   5.103628	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Feature, ReportID: 0x27, Offset: 40, Size: 8, Value: 0
   5.103637	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Input, ReportID: 0x27, Offset: 40, Size: 8, Value: 0
   5.138588	Path: UPS.Flow.[1].ConfigFrequency, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 50
   5.175587	Path: UPS.Flow.[1].ConfigVoltage, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 230
   5.215207	Path: UPS.Flow.[1].FlowID, Type: Feature, ReportID: 0x0b, Offset: 0, Size: 8, Value: 1
   5.247504	Path: UPS.Flow.[4].ConfigActivePower, Type: Feature, ReportID: 0x74, Offset: 0, Size: 16, Value: 1800
   5.283621	Path: UPS.Flow.[4].ConfigApparentPower, Type: Feature, ReportID: 0x75, Offset: 0, Size: 16, Value: 2000
   5.320753	Path: UPS.Flow.[4].ConfigFrequency, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 50
   5.354218	Path: UPS.Flow.[4].ConfigPercentLoad, Type: Feature, ReportID: 0x16, Offset: 0, Size: 8, Value: 105
   5.391725	Path: UPS.Flow.[4].ConfigVoltage, Type: Feature, ReportID: 0x72, Offset: 0, Size: 16, Value: 230
   5.391743	Path: UPS.Flow.[4].FlowID, Type: Feature, ReportID: 0x0b, Offset: 8, Size: 8, Value: 4
   5.473244	Path: UPS.HistorySystem.Event.[1].Code, Type: Feature, ReportID: 0x71, Offset: 0, Size: 16, Value: 0
   5.473263	Path: UPS.HistorySystem.Event.[2].Code, Type: Feature, ReportID: 0x71, Offset: 16, Size: 16, Value: 0
   5.473271	Path: UPS.HistorySystem.Event.[3].Code, Type: Feature, ReportID: 0x71, Offset: 32, Size: 16, Value: 0
   5.473279	Path: UPS.HistorySystem.Event.[4].Code, Type: Feature, ReportID: 0x71, Offset: 48, Size: 16, Value: 0
   5.473287	Path: UPS.HistorySystem.Event.[5].Code, Type: Feature, ReportID: 0x71, Offset: 64, Size: 16, Value: 0
   5.473297	Path: UPS.HistorySystem.Event.[6].Code, Type: Feature, ReportID: 0x71, Offset: 80, Size: 16, Value: 0
   5.473311	Path: UPS.HistorySystem.Event.[7].Code, Type: Feature, ReportID: 0x71, Offset: 96, Size: 16, Value: 0
   5.473325	Path: UPS.HistorySystem.Event.[8].Code, Type: Feature, ReportID: 0x71, Offset: 112, Size: 16, Value: 0
   5.473340	Path: UPS.HistorySystem.Event.[9].Code, Type: Feature, ReportID: 0x71, Offset: 128, Size: 16, Value: 0
   5.473359	Path: UPS.HistorySystem.Event.[10].Code, Type: Feature, ReportID: 0x71, Offset: 144, Size: 16, Value: 0
   5.473368	Path: UPS.HistorySystem.Event.[11].Code, Type: Feature, ReportID: 0x71, Offset: 160, Size: 16, Value: 0
   5.473376	Path: UPS.HistorySystem.Event.[12].Code, Type: Feature, ReportID: 0x71, Offset: 176, Size: 16, Value: 0
   5.473384	Path: UPS.HistorySystem.Event.[13].Code, Type: Feature, ReportID: 0x71, Offset: 192, Size: 16, Value: 0
   5.473392	Path: UPS.HistorySystem.Event.[14].Code, Type: Feature, ReportID: 0x71, Offset: 208, Size: 16, Value: 0
   5.473399	Path: UPS.HistorySystem.Event.[15].Code, Type: Feature, ReportID: 0x71, Offset: 224, Size: 16, Value: 0
   5.498223	Path: UPS.LCMSystem.LCMAlarm.[1].Count, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 0
   5.537897	Path: UPS.LCMSystem.LCMAlarm.[1].Interval, Type: Feature, ReportID: 0x54, Offset: 0, Size: 32, Value: 2.592e+06
   5.572599	Path: UPS.LCMSystem.LCMAlarm.[1].LCMAlarmID, Type: Feature, ReportID: 0x50, Offset: 0, Size: 8, Value: 1
   5.606524	Path: UPS.LCMSystem.LCMAlarm.[1].Mode, Type: Feature, ReportID: 0x57, Offset: 0, Size: 8, Value: 0
   5.643485	Path: UPS.LCMSystem.LCMAlarm.[1].PresentStatus.TimerExpired, Type: Feature, ReportID: 0x5d, Offset: 0, Size: 8, Value: 1
   5.643505	Path: UPS.LCMSystem.LCMAlarm.[1].PresentStatus.TimerExpired, Type: Input, ReportID: 0x5d, Offset: 0, Size: 8, Value: 1
   5.681732	Path: UPS.LCMSystem.LCMAlarm.[1].Timer, Type: Feature, ReportID: 0x5a, Offset: 0, Size: 32, Value: 0
   5.714495	Path: UPS.LCMSystem.LCMAlarm.[2].Count, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   5.753866	Path: UPS.LCMSystem.LCMAlarm.[2].Interval, Type: Feature, ReportID: 0x55, Offset: 0, Size: 32, Value: 2.592e+06
   5.753885	Path: UPS.LCMSystem.LCMAlarm.[2].LCMAlarmID, Type: Feature, ReportID: 0x50, Offset: 8, Size: 8, Value: 2
   5.786526	Path: UPS.LCMSystem.LCMAlarm.[2].Mode, Type: Feature, ReportID: 0x58, Offset: 0, Size: 8, Value: 0
   5.786541	Path: UPS.LCMSystem.LCMAlarm.[2].PresentStatus.TimerExpired, Type: Feature, ReportID: 0x5d, Offset: 8, Size: 8, Value: 1
   5.786547	Path: UPS.LCMSystem.LCMAlarm.[2].PresentStatus.TimerExpired, Type: Input, ReportID: 0x5d, Offset: 8, Size: 8, Value: 1
   5.825868	Path: UPS.LCMSystem.LCMAlarm.[2].Timer, Type: Feature, ReportID: 0x5b, Offset: 0, Size: 32, Value: 0
   5.825882	Path: UPS.LCMSystem.LCMSystemID, Type: Feature, ReportID: 0x50, Offset: 16, Size: 8, Value: 1
   5.890506	Path: UPS.OutletSystem.Outlet.[1].ActivePower, Type: Feature, ReportID: 0x83, Offset: 0, Size: 16, Value: 279
   5.890528	Path: UPS.OutletSystem.Outlet.[1].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 16, Size: 16, Value: 281
   5.890541	Path: UPS.OutletSystem.Outlet.[1].Current, Type: Feature, ReportID: 0x83, Offset: 32, Size: 16, Value: 1.1
   5.919144	Path: UPS.OutletSystem.Outlet.[1].FlowID, Type: Feature, ReportID: 0x80, Offset: 0, Size: 8, Value: 4
   5.919158	Path: UPS.OutletSystem.Outlet.[1].OutletID, Type: Feature, ReportID: 0x80, Offset: 8, Size: 8, Value: 0
   5.919167	Path: UPS.OutletSystem.Outlet.[1].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 48, Size: 8, Value: 99
   5.952998	Path: UPS.OutletSystem.Outlet.[1].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 0, Size: 8, Value: 0
   6.015393	Path: UPS.OutletSystem.Outlet.[1].Statistic.[1].Energy, Type: Feature, ReportID: 0x8c, Offset: 0, Size: 32, Value: 982000
   6.015450	Path: UPS.OutletSystem.Outlet.[1].Statistic.[1].Interval, Type: Feature, ReportID: 0x8c, Offset: 32, Size: 32, Value: 3600
   6.015468	Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].Energy, Type: Feature, ReportID: 0x8c, Offset: 64, Size: 32, Value: 2.59786e+10
   6.038539	Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x64, Offset: 0, Size: 8, Value: 0
   6.038558	Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x8c, Offset: 96, Size: 32, Value: 0
   6.038567	Path: UPS.OutletSystem.Outlet.[1].Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x8c, Offset: 128, Size: 32, Value: 0
   6.038576	Path: UPS.OutletSystem.Outlet.[2].ActivePower, Type: Feature, ReportID: 0x83, Offset: 56, Size: 16, Value: 157
   6.038584	Path: UPS.OutletSystem.Outlet.[2].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 72, Size: 16, Value: 282
   6.038590	Path: UPS.OutletSystem.Outlet.[2].AutomaticRestart, Type: Feature, ReportID: 0x81, Offset: 8, Size: 8, Value: 1
   6.038597	Path: UPS.OutletSystem.Outlet.[2].Current, Type: Feature, ReportID: 0x83, Offset: 88, Size: 16, Value: 1.2
   6.077774	Path: UPS.OutletSystem.Outlet.[2].DelayBeforeShutdown, Type: Feature, ReportID: 0x8d, Offset: 0, Size: 32, Value: 0
   6.113789	Path: UPS.OutletSystem.Outlet.[2].DelayBeforeStartup, Type: Feature, ReportID: 0x90, Offset: 0, Size: 32, Value: 0
   6.113806	Path: UPS.OutletSystem.Outlet.[2].FlowID, Type: Feature, ReportID: 0x80, Offset: 16, Size: 8, Value: 4
   6.113812	Path: UPS.OutletSystem.Outlet.[2].OutletID, Type: Feature, ReportID: 0x80, Offset: 24, Size: 8, Value: 1
   6.113821	Path: UPS.OutletSystem.Outlet.[2].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 104, Size: 8, Value: 55
   6.113827	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 16, Size: 8, Value: 1
   6.147518	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 0, Size: 8, Value: 1
   6.147538	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Input, ReportID: 0x82, Offset: 0, Size: 8, Value: 1
   6.182160	Path: UPS.OutletSystem.Outlet.[2].RemainingCapacityLimit, Type: Feature, ReportID: 0x84, Offset: 0, Size: 8, Value: 0
   6.219571	Path: UPS.OutletSystem.Outlet.[2].ShutdownTimer, Type: Feature, ReportID: 0x87, Offset: 0, Size: 16, Value: 65535
   6.255267	Path: UPS.OutletSystem.Outlet.[2].StartupTimer, Type: Feature, ReportID: 0x8a, Offset: 0, Size: 16, Value: 3
   6.321171	Path: UPS.OutletSystem.Outlet.[2].Statistic.[1].Energy, Type: Feature, ReportID: 0x86, Offset: 0, Size: 32, Value: 561000
   6.321190	Path: UPS.OutletSystem.Outlet.[2].Statistic.[1].Interval, Type: Feature, ReportID: 0x86, Offset: 32, Size: 32, Value: 3600
   6.321199	Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].Energy, Type: Feature, ReportID: 0x86, Offset: 64, Size: 32, Value: 1.11775e+10
   6.344154	Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x65, Offset: 0, Size: 8, Value: 0
   6.344171	Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x86, Offset: 96, Size: 32, Value: 0
   6.344179	Path: UPS.OutletSystem.Outlet.[2].Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x86, Offset: 128, Size: 32, Value: 0
   6.344188	Path: UPS.OutletSystem.Outlet.[3].ActivePower, Type: Feature, ReportID: 0x83, Offset: 112, Size: 16, Value: 68
   6.344196	Path: UPS.OutletSystem.Outlet.[3].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 128, Size: 16, Value: 94
   6.344201	Path: UPS.OutletSystem.Outlet.[3].AutomaticRestart, Type: Feature, ReportID: 0x81, Offset: 24, Size: 8, Value: 1
   6.344209	Path: UPS.OutletSystem.Outlet.[3].Current, Type: Feature, ReportID: 0x83, Offset: 144, Size: 16, Value: 0.4
   6.383811	Path: UPS.OutletSystem.Outlet.[3].DelayBeforeShutdown, Type: Feature, ReportID: 0x8e, Offset: 0, Size: 32, Value: 0
   6.419781	Path: UPS.OutletSystem.Outlet.[3].DelayBeforeStartup, Type: Feature, ReportID: 0x91, Offset: 0, Size: 32, Value: 0
   6.419807	Path: UPS.OutletSystem.Outlet.[3].FlowID, Type: Feature, ReportID: 0x80, Offset: 32, Size: 8, Value: 4
   6.419813	Path: UPS.OutletSystem.Outlet.[3].OutletID, Type: Feature, ReportID: 0x80, Offset: 40, Size: 8, Value: 2
   6.419822	Path: UPS.OutletSystem.Outlet.[3].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 160, Size: 8, Value: 72
   6.419829	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 32, Size: 8, Value: 1
   6.419835	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 8, Size: 8, Value: 1
   6.419840	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Input, ReportID: 0x82, Offset: 8, Size: 8, Value: 1
   6.452164	Path: UPS.OutletSystem.Outlet.[3].RemainingCapacityLimit, Type: Feature, ReportID: 0x85, Offset: 0, Size: 8, Value: 0
   6.489272	Path: UPS.OutletSystem.Outlet.[3].ShutdownTimer, Type: Feature, ReportID: 0x88, Offset: 0, Size: 16, Value: 65535
   6.525515	Path: UPS.OutletSystem.Outlet.[3].StartupTimer, Type: Feature, ReportID: 0x8b, Offset: 0, Size: 16, Value: 6
   6.591172	Path: UPS.OutletSystem.Outlet.[3].Statistic.[1].Energy, Type: Feature, ReportID: 0x89, Offset: 0, Size: 32, Value: 244000
   6.591192	Path: UPS.OutletSystem.Outlet.[3].Statistic.[1].Interval, Type: Feature, ReportID: 0x89, Offset: 32, Size: 32, Value: 3600
   6.591201	Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].Energy, Type: Feature, ReportID: 0x89, Offset: 64, Size: 32, Value: 8.74446e+09
   6.614262	Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x66, Offset: 0, Size: 8, Value: 0
   6.614280	Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x89, Offset: 96, Size: 32, Value: 0
   6.614292	Path: UPS.OutletSystem.Outlet.[3].Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x89, Offset: 128, Size: 32, Value: 0
   6.614301	Path: UPS.OutletSystem.OutletSystemID, Type: Feature, ReportID: 0x80, Offset: 48, Size: 8, Value: 1
   6.650537	Path: UPS.PowerConverter.ConverterType, Type: Feature, ReportID: 0x4a, Offset: 0, Size: 8, Value: 1
   6.686274	Path: UPS.PowerConverter.Input.[1].AutomaticRestart, Type: Feature, ReportID: 0x73, Offset: 0, Size: 8, Value: 1
   6.727900	Path: UPS.PowerConverter.Input.[1].Current, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0
   6.761672	Path: UPS.PowerConverter.Input.[1].FlowID, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 1
   6.761686	Path: UPS.PowerConverter.Input.[1].Frequency, Type: Feature, ReportID: 0x31, Offset: 16, Size: 16, Value: 49.9
   6.761693	Path: UPS.PowerConverter.Input.[1].InputID, Type: Feature, ReportID: 0x30, Offset: 8, Size: 8, Value: 1
   6.799965	Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost, Type: Feature, ReportID: 0x32, Offset: 0, Size: 8, Value: 0
   6.799981	Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost, Type: Input, ReportID: 0x32, Offset: 0, Size: 8, Value: 0
   6.799987	Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck, Type: Feature, ReportID: 0x32, Offset: 8, Size: 8, Value: 0
   6.799993	Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck, Type: Input, ReportID: 0x32, Offset: 8, Size: 8, Value: 0
   6.799999	Path: UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type: Feature, ReportID: 0x32, Offset: 16, Size: 8, Value: 0
   6.800005	Path: UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type: Input, ReportID: 0x32, Offset: 16, Size: 8, Value: 0
   6.800011	Path: UPS.PowerConverter.Input.[1].PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 24, Size: 8, Value: 0
   6.800017	Path: UPS.PowerConverter.Input.[1].PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 24, Size: 8, Value: 0
   6.800023	Path: UPS.PowerConverter.Input.[1].PresentStatus.Used, Type: Feature, ReportID: 0x32, Offset: 32, Size: 8, Value: 1
   6.800029	Path: UPS.PowerConverter.Input.[1].PresentStatus.Used, Type: Input, ReportID: 0x32, Offset: 32, Size: 8, Value: 1
   6.800035	Path: UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x32, Offset: 40, Size: 8, Value: 0
   6.800041	Path: UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type: Input, ReportID: 0x32, Offset: 40, Size: 8, Value: 0
   6.800048	Path: UPS.PowerConverter.Input.[1].Voltage, Type: Feature, ReportID: 0x31, Offset: 32, Size: 16, Value: 235
   6.830932	Path: UPS.PowerConverter.Input.[3].ControlStandby, Type: Feature, ReportID: 0x3e, Offset: 0, Size: 8, Value: 0
   6.866207	Path: UPS.PowerConverter.Input.[3].EnergySaving, Type: Feature, ReportID: 0x39, Offset: 0, Size: 8, Value: 0
   6.866223	Path: UPS.PowerConverter.Input.[3].FlowID, Type: Feature, ReportID: 0x30, Offset: 16, Size: 8, Value: 3
   6.866229	Path: UPS.PowerConverter.Input.[3].InputID, Type: Feature, ReportID: 0x30, Offset: 24, Size: 8, Value: 3
   6.902061	Path: UPS.PowerConverter.Input.[3].PresentStatus.Used, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 8, Value: 0
   6.902077	Path: UPS.PowerConverter.Input.[3].PresentStatus.Used, Type: Input, ReportID: 0x3b, Offset: 0, Size: 8, Value: 0
   6.938061	Path: UPS.PowerConverter.Input.[3].StartOnBattery, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 1
   6.974283	Path: UPS.PowerConverter.Inverter.PresentStatus.Used, Type: Feature, ReportID: 0x41, Offset: 0, Size: 8, Value: 0
   6.974296	Path: UPS.PowerConverter.Inverter.PresentStatus.Used, Type: Input, ReportID: 0x41, Offset: 0, Size: 8, Value: 0
   7.027572	Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: 522
   7.027590	Path: UPS.PowerConverter.Output.ApparentPower, Type: Feature, ReportID: 0x42, Offset: 16, Size: 16, Value: 611
   7.027597	Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x42, Offset: 32, Size: 16, Value: 2.6
   7.027603	Path: UPS.PowerConverter.Output.Efficiency, Type: Feature, ReportID: 0x42, Offset: 48, Size: 8, Value: 95
   7.064046	Path: UPS.PowerConverter.Output.ExtendedFrequencyMode, Type: Feature, ReportID: 0x4b, Offset: 0, Size: 8, Value: 0
   7.100065	Path: UPS.PowerConverter.Output.ExtendedVoltageMode, Type: Feature, ReportID: 0x4c, Offset: 0, Size: 8, Value: 0
   7.138686	Path: UPS.PowerConverter.Output.FlowID, Type: Feature, ReportID: 0x40, Offset: 0, Size: 8, Value: 4
   7.172050	Path: UPS.PowerConverter.Output.ForcedReboot, Type: Feature, ReportID: 0x43, Offset: 0, Size: 8, Value: 1
   7.172071	Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x42, Offset: 56, Size: 16, Value: 49.9
   7.209322	Path: UPS.PowerConverter.Output.HighVoltageBuckTransfer, Type: Feature, ReportID: 0x4d, Offset: 0, Size: 16, Value: 265
   7.245308	Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x48, Offset: 0, Size: 16, Value: 294
   7.281371	Path: UPS.PowerConverter.Output.LowVoltageBoostTransfer, Type: Feature, ReportID: 0x4e, Offset: 0, Size: 16, Value: 184
   7.317332	Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 160
   7.317349	Path: UPS.PowerConverter.Output.OutputID, Type: Feature, ReportID: 0x40, Offset: 8, Size: 8, Value: 1
   7.317356	Path: UPS.PowerConverter.Output.PowerFactor, Type: Feature, ReportID: 0x42, Offset: 72, Size: 8, Value: 85
   7.352209	Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Feature, ReportID: 0x49, Offset: 0, Size: 8, Value: 0
   7.352227	Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Input, ReportID: 0x49, Offset: 0, Size: 8, Value: 0
   7.388051	Path: UPS.PowerConverter.Output.SensitivityMode, Type: Feature, ReportID: 0x4f, Offset: 0, Size: 8, Value: 0
   7.454940	Path: UPS.PowerConverter.Output.Statistic.[1].Energy, Type: Feature, ReportID: 0x44, Offset: 0, Size: 32, Value: 1.789e+06
   7.454964	Path: UPS.PowerConverter.Output.Statistic.[1].Interval, Type: Feature, ReportID: 0x44, Offset: 32, Size: 32, Value: 3600
   7.454979	Path: UPS.PowerConverter.Output.Statistic.[4].Energy, Type: Feature, ReportID: 0x44, Offset: 64, Size: 32, Value: 4.59005e+10
   7.477934	Path: UPS.PowerConverter.Output.Statistic.[4].ModuleReset, Type: Feature, ReportID: 0x67, Offset: 0, Size: 8, Value: 0
   7.477953	Path: UPS.PowerConverter.Output.Statistic.[4].Reset.Energy, Type: Feature, ReportID: 0x44, Offset: 96, Size: 32, Value: 0
   7.477962	Path: UPS.PowerConverter.Output.Statistic.[4].Reset.Timer, Type: Feature, ReportID: 0x44, Offset: 128, Size: 32, Value: 0
   7.477969	Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x42, Offset: 80, Size: 16, Value: 235
   7.477975	Path: UPS.PowerConverter.PowerConverterID, Type: Feature, ReportID: 0x40, Offset: 16, Size: 8, Value: 1
   7.514187	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
   7.553561	Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 1
   7.553579	Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x0c, Offset: 8, Size: 8, Value: 2
   7.588562	Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x0d, Offset: 8, Size: 16, Value: 48
   7.626811	Path: UPS.PowerSummary.Country, Type: Feature, ReportID: 0x0b, Offset: 16, Size: 8, Value: 0
   7.661596	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
   7.697588	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
   7.697604	Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x0c, Offset: 16, Size: 8, Value: 100
   7.697609	Path: UPS.PowerSummary.FlowID, Type: Feature, ReportID: 0x0b, Offset: 24, Size: 8, Value: 4
   7.697615	Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x0c, Offset: 24, Size: 8, Value: 100
   7.736943	Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 4
   7.736962	Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x10, Offset: 8, Size: 8, Value: 1
   7.736973	Path: UPS.PowerSummary.iModel, Type: Feature, ReportID: 0x10, Offset: 16, Size: 8, Value: 10
   7.736983	Path: UPS.PowerSummary.iPartNumber, Type: Feature, ReportID: 0x10, Offset: 24, Size: 8, Value: 15
   7.736992	Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x10, Offset: 32, Size: 8, Value: 2
   7.737001	Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x10, Offset: 40, Size: 8, Value: 3
   7.737010	Path: UPS.PowerSummary.iVersion, Type: Feature, ReportID: 0x10, Offset: 48, Size: 8, Value: 5
   7.768583	Path: UPS.PowerSummary.PercentLoad, Type: Feature, ReportID: 0x07, Offset: 0, Size: 8, Value: 30
   7.768606	Path: UPS.PowerSummary.PowerSummaryID, Type: Feature, ReportID: 0x0b, Offset: 32, Size: 8, Value: 1
   7.806602	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
   7.806618	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
   7.806624	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
   7.806629	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
   7.806635	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
   7.806642	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
   7.838070	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 0
   7.838086	Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type: Input, ReportID: 0x0f, Offset: 0, Size: 8, Value: 0
   7.878821	Path: UPS.PowerSummary.PresentStatus.ConfigurationFailure, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
   7.878839	Path: UPS.PowerSummary.PresentStatus.ConfigurationFailure, Type: Input, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
   7.878848	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
   7.878857	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
   7.878865	Path: UPS.PowerSummary.PresentStatus.EmergencyStop, Type: Feature, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
   7.878874	Path: UPS.PowerSummary.PresentStatus.EmergencyStop, Type: Input, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
   7.878882	Path: UPS.PowerSummary.PresentStatus.FanFailure, Type: Feature, ReportID: 0x03, Offset: 16, Size: 8, Value: 0
   7.878890	Path: UPS.PowerSummary.PresentStatus.FanFailure, Type: Input, ReportID: 0x03, Offset: 16, Size: 8, Value: 0
   7.878898	Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, ReportID: 0x01, Offset: 32, Size: 8, Value: 1
   7.878907	Path: UPS.PowerSummary.PresentStatus.Good, Type: Input, ReportID: 0x01, Offset: 32, Size: 8, Value: 1
   7.913701	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 0
   7.913721	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x02, Offset: 0, Size: 8, Value: 0
   7.913736	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x02, Offset: 8, Size: 8, Value: 0
   7.913745	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x02, Offset: 8, Size: 8, Value: 0
   7.913754	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x02, Offset: 16, Size: 8, Value: 0
   7.913763	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, ReportID: 0x02, Offset: 16, Size: 8, Value: 0
   7.913772	Path: UPS.PowerSummary.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x03, Offset: 24, Size: 8, Value: 0
   7.913781	Path: UPS.PowerSummary.PresentStatus.OverTemperature, Type: Input, ReportID: 0x03, Offset: 24, Size: 8, Value: 0
   7.913791	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x02, Offset: 24, Size: 8, Value: 0
   7.913799	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x02, Offset: 24, Size: 8, Value: 0
   7.913808	Path: UPS.PowerSummary.PresentStatus.Switchable, Type: Feature, ReportID: 0x03, Offset: 32, Size: 8, Value: 1
   7.913817	Path: UPS.PowerSummary.PresentStatus.Switchable, Type: Input, ReportID: 0x03, Offset: 32, Size: 8, Value: 1
   7.950826	Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
   7.950843	Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
   7.982201	Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x08, Offset: 0, Size: 8, Value: 20
   8.017950	Path: UPS.PowerSummary.RemainingCapacityLimitSetting, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 20
   8.054081	Path: UPS.PowerSummary.RestartLevel, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 0
   8.054105	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x06, Offset: 8, Size: 32, Value: 932
   8.054115	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x06, Offset: 8, Size: 32, Value: 932
   8.089980	Path: UPS.PowerSummary.Schedule, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 0
   8.129582	Path: UPS.PowerSummary.Timer, Type: Feature, ReportID: 0x18, Offset: 0, Size: 32, Value: 1.3442e+08
   8.129599	Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x07, Offset: 8, Size: 16, Value: 53.8
   8.211575	get_model_name(Eaton 5PX, 2000)

   8.211596	comparing with: ellipse 300
   8.211600	comparing with: ellipse 500
   8.211604	comparing with: ellipse 650
   8.211607	comparing with: ellipse 800
   8.211610	comparing with: ellipse 1200
   8.211614	comparing with: ellipse premium 500
   8.211618	comparing with: ellipse premium 650
   8.211621	comparing with: ellipse premium 800
   8.211625	comparing with: ellipse premium 1200
   8.211629	comparing with: Ellipse 600
   8.211632	comparing with: Ellipse 750
   8.211635	comparing with: Ellipse 1000
   8.211639	comparing with: Ellipse 1500
   8.211642	comparing with: Ellipse MAX 600
   8.211646	comparing with: Ellipse MAX 850
   8.211649	comparing with: Ellipse MAX 1100
   8.211653	comparing with: Ellipse MAX 1500
   8.211656	comparing with: Protection Center 420
   8.211660	comparing with: Protection Center 500
   8.211663	comparing with: Protection Center 675
   8.211667	comparing with: Protection Station 500
   8.211671	comparing with: Protection Station 650
   8.211674	comparing with: Protection Station 800
   8.211678	comparing with: Ellipse ECO 650
   8.211681	comparing with: Ellipse ECO 800
   8.211685	comparing with: Ellipse ECO 1200
   8.211688	comparing with: Ellipse ECO 1600
   8.211692	comparing with: 3S 450
   8.211695	comparing with: 3S 550
   8.211699	comparing with: 3S 700
   8.211702	comparing with: 3S 750
   8.211705	comparing with: Pulsar Evolution 500
   8.211709	comparing with: Pulsar Evolution 800
   8.211712	comparing with: Pulsar Evolution 1100
   8.211716	comparing with: Pulsar Evolution 1500
   8.211719	comparing with: Pulsar Evolution 2200
   8.211723	comparing with: Pulsar Evolution 3000
   8.211726	comparing with: Pulsar Evolution 3000 XL
   8.211730	comparing with: Evolution 650
   8.211733	comparing with: Evolution 850
   8.211737	comparing with: Evolution 1150
   8.211740	comparing with: Evolution S 1250
   8.211744	comparing with: Evolution 1550
   8.211748	comparing with: Evolution S 1750
   8.211752	comparing with: Evolution 2000
   8.211756	comparing with: Evolution S 2500
   8.211760	comparing with: Evolution S 3000
   8.211764	comparing with: 5P 650
   8.211768	comparing with: 5P 850
   8.211772	comparing with: 5P 1150
   8.211776	comparing with: 5P 1550
   8.211781	comparing with: PULSAR M 2200
   8.211785	comparing with: PULSAR M 3000
   8.211788	comparing with: PULSAR M 3000 XL
   8.211791	comparing with: EX 2200
   8.211793	comparing with: EX 3000
   8.211795	comparing with: EX 3000 XL
   8.211797	comparing with: Pulsar MX 4000 RT
   8.211800	comparing with: Pulsar MX 5000 RT
   8.211802	comparing with: Nova 500 AVR
   8.211804	comparing with: Nova 600 AVR
   8.211806	comparing with: Nova 625 AVR
   8.211809	comparing with: Nova 1100 AVR
   8.211811	comparing with: Nova 1250 AVR
   8.211813	comparing with: Pulsar EXtreme 700C
   8.211816	comparing with: Pulsar EXtreme 1000C
   8.211818	comparing with: Pulsar EXtreme 1500C
   8.211820	comparing with: Pulsar EXtreme 1500C CLA
   8.211822	comparing with: Pulsar EXtreme 2200C
   8.211825	comparing with: Pulsar EXtreme 3200C
   8.211827	comparing with: Pulsar EX 700 RT
   8.211829	comparing with: Pulsar EX 1000 RT
   8.211831	comparing with: Pulsar EX 1500 RT
   8.211834	comparing with: Pulsar EX 2200 RT
   8.211836	comparing with: Pulsar EX 3200 RT
   8.211838	comparing with: EX 5 RT 3:1
   8.211840	comparing with: EX 7 RT 3:1
   8.211843	comparing with: EX 11 RT 3:1
   8.211845	comparing with: EX 5 RT
   8.211847	comparing with: EX 7 RT
   8.211849	comparing with: EX 11 RT
   8.211851	comparing with: Galaxy 3000 10 kVA
   8.211854	comparing with: Galaxy 3000 15 kVA
   8.211856	comparing with: Galaxy 3000 20 kVA
   8.211858	comparing with: Galaxy 3000 30 kVA
   8.211869	Report descriptor retrieved (Reportlen = 2580)
   8.211871	Found HID device
   8.211875	Detected a UPS: EATON/Eaton 5PX 2000
   8.211905	Path: UPS.PowerSummary.Country, Type: Feature, ReportID: 0x0b, Offset: 16, Size: 8, Value: 0
   8.211921	Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x06, Offset: 0, Size: 8, Value: 100
   8.211933	Path: UPS.PowerSummary.RemainingCapacityLimitSetting, Type: Feature, ReportID: 0x12, Offset: 0, Size: 8, Value: 20
   8.211964	Path: UPS.PowerSummary.RestartLevel, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 0
   8.237334	Path: UPS.BatterySystem.Battery.DesignCapacity, Type: Feature, ReportID: 0x23, Offset: 0, Size: 32, Value: 32400
   8.237376	Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x06, Offset: 8, Size: 32, Value: 932
   8.237439	Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 4
   8.319873	Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x07, Offset: 8, Size: 16, Value: 53.8
   8.319909	Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x0d, Offset: 8, Size: 16, Value: 48
   8.342090	Path: UPS.BatterySystem.Battery.DeepDischargeProtection, Type: Feature, ReportID: 0x22, Offset: 0, Size: 8, Value: 1
   8.342134	Path: UPS.PowerConverter.Input.[3].EnergySaving, Type: Feature, ReportID: 0x39, Offset: 0, Size: 8, Value: 0
   8.377999	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
   8.378017	ABM is enabled
   8.415229	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
   8.415242	ABM numeric status: 3
   8.415245	ABM string status: floating
   8.415271	Path: UPS.PowerConverter.Output.Efficiency, Type: Feature, ReportID: 0x42, Offset: 48, Size: 8, Value: 95
   8.415285	Path: UPS.PowerSummary.iVersion, Type: Feature, ReportID: 0x10, Offset: 48, Size: 8, Value: 5
   8.490865	Path: UPS.PowerSummary.PercentLoad, Type: Feature, ReportID: 0x07, Offset: 0, Size: 8, Value: 30
   8.521849	Path: UPS.Flow.[4].ConfigPercentLoad, Type: Feature, ReportID: 0x16, Offset: 0, Size: 8, Value: 105
   8.521903	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
   8.521915	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
   8.557999	Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1
   8.597604	Path: UPS.BatterySystem.Battery.TestPeriod, Type: Feature, ReportID: 0x25, Offset: 0, Size: 32, Value: 604800
   8.629866	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
   8.683107	Path: UPS.PowerConverter.Output.ApparentPower, Type: Feature, ReportID: 0x42, Offset: 16, Size: 16, Value: 611
   8.720992	Path: UPS.Flow.[4].ConfigApparentPower, Type: Feature, ReportID: 0x75, Offset: 0, Size: 16, Value: 2000
   8.721030	Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x42, Offset: 0, Size: 16, Value: 504
   8.757149	Path: UPS.Flow.[4].ConfigActivePower, Type: Feature, ReportID: 0x74, Offset: 0, Size: 16, Value: 1800
   8.791903	Path: UPS.PowerConverter.Input.[1].AutomaticRestart, Type: Feature, ReportID: 0x73, Offset: 0, Size: 8, Value: 1
   8.827857	Path: UPS.PowerConverter.Input.[3].StartOnBattery, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 1
   8.863855	Path: UPS.PowerConverter.Output.ForcedReboot, Type: Feature, ReportID: 0x43, Offset: 0, Size: 8, Value: 1
   8.863900	Path: UPS.PowerSummary.PresentStatus.Switchable, Type: Feature, ReportID: 0x03, Offset: 32, Size: 8, Value: 1
   8.899749	Path: UPS.PowerConverter.ConverterType, Type: Feature, ReportID: 0x4a, Offset: 0, Size: 8, Value: 1
   8.899795	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
   8.936108	Path: UPS.PowerConverter.Input.[3].PresentStatus.Used, Type: Feature, ReportID: 0x3b, Offset: 0, Size: 8, Value: 0
   8.977620	Path: UPS.PowerConverter.Input.[1].PresentStatus.Used, Type: Feature, ReportID: 0x32, Offset: 32, Size: 8, Value: 1
   8.977655	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
   8.977674	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
   8.977686	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
   8.977691	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
   8.977709	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
   8.977759	Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature, ReportID: 0x02, Offset: 16, Size: 8, Value: 0
   8.977777	Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x02, Offset: 8, Size: 8, Value: 0
   9.009108	Path: UPS.LCMSystem.LCMAlarm.[2].PresentStatus.TimerExpired, Type: Feature, ReportID: 0x5d, Offset: 8, Size: 8, Value: 1
   9.009141	Path: UPS.PowerConverter.Input.[1].PresentStatus.Buck, Type: Feature, ReportID: 0x32, Offset: 8, Size: 8, Value: 0
   9.009161	Path: UPS.PowerConverter.Input.[1].PresentStatus.Boost, Type: Feature, ReportID: 0x32, Offset: 0, Size: 8, Value: 0
   9.009181	Path: UPS.PowerConverter.Input.[1].PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x32, Offset: 40, Size: 8, Value: 0
   9.009202	Path: UPS.PowerConverter.Input.[1].PresentStatus.FrequencyOutOfRange, Type: Feature, ReportID: 0x32, Offset: 16, Size: 8, Value: 0
   9.009221	Path: UPS.PowerSummary.PresentStatus.Good, Type: Feature, ReportID: 0x01, Offset: 32, Size: 8, Value: 1
   9.009270	Path: UPS.PowerSummary.PresentStatus.FanFailure, Type: Feature, ReportID: 0x03, Offset: 16, Size: 8, Value: 0
   9.049881	Path: UPS.BatterySystem.Battery.PresentStatus.Present, Type: Feature, ReportID: 0x27, Offset: 0, Size: 8, Value: 1
   9.049911	Path: UPS.BatterySystem.Charger.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x27, Offset: 16, Size: 8, Value: 0
   9.049926	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooHigh, Type: Feature, ReportID: 0x27, Offset: 32, Size: 8, Value: 0
   9.049977	Path: UPS.BatterySystem.Charger.PresentStatus.VoltageTooLow, Type: Feature, ReportID: 0x27, Offset: 40, Size: 8, Value: 0
   9.050014	Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 0
   9.050033	Path: UPS.PowerSummary.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x03, Offset: 24, Size: 8, Value: 0
   9.050052	Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x02, Offset: 24, Size: 8, Value: 0
   9.050068	Path: UPS.PowerSummary.PresentStatus.EmergencyStop, Type: Feature, ReportID: 0x03, Offset: 8, Size: 8, Value: 0
   9.050098	Path: UPS.PowerSummary.PresentStatus.ConfigurationFailure, Type: Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 0
   9.079747	Path: UPS.PowerConverter.Output.PresentStatus.ShortCircuit, Type: Feature, ReportID: 0x49, Offset: 0, Size: 8, Value: 0
   9.121877	Path: UPS.PowerConverter.Input.[1].Voltage, Type: Feature, ReportID: 0x31, Offset: 32, Size: 16, Value: 235.4
   9.153124	Path: UPS.Flow.[1].ConfigVoltage, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 230
   9.153172	Path: UPS.PowerConverter.Input.[1].Current, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0
   9.153252	Path: UPS.PowerConverter.Input.[1].Frequency, Type: Feature, ReportID: 0x31, Offset: 16, Size: 16, Value: 49.9
   9.187874	Path: UPS.Flow.[1].ConfigFrequency, Type: Feature, ReportID: 0x14, Offset: 0, Size: 8, Value: 50
   9.224882	Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 160
   9.261021	Path: UPS.PowerConverter.Output.LowVoltageBoostTransfer, Type: Feature, ReportID: 0x4e, Offset: 0, Size: 16, Value: 184
   9.297144	Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x48, Offset: 0, Size: 16, Value: 294
   9.333159	Path: UPS.PowerConverter.Output.HighVoltageBuckTransfer, Type: Feature, ReportID: 0x4d, Offset: 0, Size: 16, Value: 265
   9.367778	Path: UPS.PowerConverter.Output.SensitivityMode, Type: Feature, ReportID: 0x4f, Offset: 0, Size: 8, Value: 0
   9.403783	Path: UPS.PowerConverter.Output.ExtendedVoltageMode, Type: Feature, ReportID: 0x4c, Offset: 0, Size: 8, Value: 0
   9.439757	Path: UPS.PowerConverter.Output.ExtendedFrequencyMode, Type: Feature, ReportID: 0x4b, Offset: 0, Size: 8, Value: 0
   9.439947	Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x42, Offset: 80, Size: 16, Value: 235
   9.476897	Path: UPS.Flow.[4].ConfigVoltage, Type: Feature, ReportID: 0x72, Offset: 0, Size: 16, Value: 230
   9.476939	Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x42, Offset: 32, Size: 16, Value: 2.6
   9.477006	Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x42, Offset: 56, Size: 16, Value: 49.9
   9.477019	Path: UPS.Flow.[4].ConfigFrequency, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 50
   9.477032	Path: UPS.PowerConverter.Output.PowerFactor, Type: Feature, ReportID: 0x42, Offset: 72, Size: 8, Value: 82
   9.518640	Path: UPS.OutletSystem.Outlet.[1].OutletID, Type: Feature, ReportID: 0x80, Offset: 8, Size: 8, Value: 0
   9.552640	Path: UPS.OutletSystem.Outlet.[1].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 0, Size: 8, Value: 0
   9.616020	Path: UPS.OutletSystem.Outlet.[1].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 16, Size: 16, Value: 287
   9.616067	Path: UPS.OutletSystem.Outlet.[1].ActivePower, Type: Feature, ReportID: 0x83, Offset: 0, Size: 16, Value: 285
   9.616089	Path: UPS.OutletSystem.Outlet.[1].Current, Type: Feature, ReportID: 0x83, Offset: 32, Size: 16, Value: 1
   9.616110	Path: UPS.OutletSystem.Outlet.[1].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 48, Size: 8, Value: 99
   9.616138	Path: UPS.OutletSystem.Outlet.[2].OutletID, Type: Feature, ReportID: 0x80, Offset: 24, Size: 8, Value: 1
   9.616173	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 16, Size: 8, Value: 1
   9.638885	Path: UPS.OutletSystem.Outlet.[2].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 0, Size: 8, Value: 1
   9.673788	Path: UPS.OutletSystem.Outlet.[2].RemainingCapacityLimit, Type: Feature, ReportID: 0x84, Offset: 0, Size: 8, Value: 0
   9.711163	Path: UPS.OutletSystem.Outlet.[2].ShutdownTimer, Type: Feature, ReportID: 0x87, Offset: 0, Size: 16, Value: 65535
   9.746891	Path: UPS.OutletSystem.Outlet.[2].StartupTimer, Type: Feature, ReportID: 0x8a, Offset: 0, Size: 16, Value: 3
   9.746935	Path: UPS.OutletSystem.Outlet.[2].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 72, Size: 16, Value: 282
   9.746958	Path: UPS.OutletSystem.Outlet.[2].ActivePower, Type: Feature, ReportID: 0x83, Offset: 56, Size: 16, Value: 151
   9.746980	Path: UPS.OutletSystem.Outlet.[2].Current, Type: Feature, ReportID: 0x83, Offset: 88, Size: 16, Value: 1.2
   9.747001	Path: UPS.OutletSystem.Outlet.[2].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 104, Size: 8, Value: 53
   9.747021	Path: UPS.OutletSystem.Outlet.[3].OutletID, Type: Feature, ReportID: 0x80, Offset: 40, Size: 8, Value: 2
   9.747055	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 32, Size: 8, Value: 1
   9.747073	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.Switchable, Type: Feature, ReportID: 0x81, Offset: 32, Size: 8, Value: 1
   9.747093	Path: UPS.OutletSystem.Outlet.[3].PresentStatus.SwitchOn/Off, Type: Feature, ReportID: 0x82, Offset: 8, Size: 8, Value: 1
   9.781677	Path: UPS.OutletSystem.Outlet.[3].RemainingCapacityLimit, Type: Feature, ReportID: 0x85, Offset: 0, Size: 8, Value: 0
   9.819019	Path: UPS.OutletSystem.Outlet.[3].ShutdownTimer, Type: Feature, ReportID: 0x88, Offset: 0, Size: 16, Value: 65535
   9.854902	Path: UPS.OutletSystem.Outlet.[3].StartupTimer, Type: Feature, ReportID: 0x8b, Offset: 0, Size: 16, Value: 6
   9.854950	Path: UPS.OutletSystem.Outlet.[3].ApparentPower, Type: Feature, ReportID: 0x83, Offset: 128, Size: 16, Value: 94
   9.854971	Path: UPS.OutletSystem.Outlet.[3].ActivePower, Type: Feature, ReportID: 0x83, Offset: 112, Size: 16, Value: 68
   9.854992	Path: UPS.OutletSystem.Outlet.[3].Current, Type: Feature, ReportID: 0x83, Offset: 144, Size: 16, Value: 0.4
   9.855013	Path: UPS.OutletSystem.Outlet.[3].PowerFactor, Type: Feature, ReportID: 0x83, Offset: 160, Size: 8, Value: 72
   9.890032	Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1
   9.890058	Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1
   9.890066	Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x24, Offset: 0, Size: 8, Value: 1
   9.929275	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
   9.965149	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
   9.965184	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
   9.965212	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
   9.965228	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
   9.965243	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
   9.965259	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
   9.965273	Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x13, Offset: 0, Size: 8, Value: 2
  10.001170	Path: UPS.OutletSystem.Outlet.[2].DelayBeforeShutdown, Type: Feature, ReportID: 0x8d, Offset: 0, Size: 32, Value: 0
  10.037284	Path: UPS.OutletSystem.Outlet.[2].DelayBeforeStartup, Type: Feature, ReportID: 0x90, Offset: 0, Size: 32, Value: 0
  10.073446	Path: UPS.OutletSystem.Outlet.[3].DelayBeforeShutdown, Type: Feature, ReportID: 0x8e, Offset: 0, Size: 32, Value: 0
  10.109287	Path: UPS.OutletSystem.Outlet.[3].DelayBeforeStartup, Type: Feature, ReportID: 0x91, Offset: 0, Size: 32, Value: 0
  10.109328	upsdrv_initinfo...
  10.109337	upsdrv_updateinfo...
  10.360175	libusb_get_interrupt: Connection timed out
  10.360200	Got 0 HID objects...
  10.360216	Quick update...
  10.393838	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  10.393848	ABM is enabled
  10.431063	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  10.431075	ABM numeric status: 3
  10.431078	ABM string status: floating
  10.431086	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  10.431092	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  10.470311	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  10.470324	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  10.470329	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  10.470334	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  10.470337	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  10.470342	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  10.470418	dstate_init: sock /var/run/nut/usbhid-ups-eaton-5px-1 open on fd 5
  10.470427	upsdrv_updateinfo...
  10.721106	libusb_get_interrupt: Connection timed out
  10.721126	Got 0 HID objects...
  10.721131	Quick update...
  10.721139	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  10.721143	ABM is enabled
  10.721147	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  10.721150	ABM numeric status: 3
  10.721153	ABM string status: floating
  10.721158	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  10.721164	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  10.721169	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  10.721173	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  10.721178	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  10.721182	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  10.721185	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  10.721189	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  12.470584	upsdrv_updateinfo...
  12.720842	libusb_get_interrupt: Connection timed out
  12.720861	Got 0 HID objects...
  12.720867	Quick update...
  12.751293	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  12.751307	ABM is enabled
  12.788896	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  12.788908	ABM numeric status: 3
  12.788912	ABM string status: floating
  12.826780	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  12.863031	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  12.900173	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  12.900185	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  12.900191	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  12.900199	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  12.900203	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  12.900207	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  14.472173	upsdrv_updateinfo...
  14.722859	libusb_get_interrupt: Connection timed out
  14.722884	Got 0 HID objects...
  14.722891	Quick update...
  14.749145	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  14.749157	ABM is enabled
  14.786472	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  14.786490	ABM numeric status: 3
  14.786523	ABM string status: floating
  14.824849	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  14.860478	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  14.898477	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  14.898544	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  14.898550	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  14.898555	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  14.898559	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  14.898563	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  16.473763	upsdrv_updateinfo...
  16.724399	libusb_get_interrupt: Connection timed out
  16.724443	Got 0 HID objects...
  16.724449	Quick update...
  16.747058	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  16.747071	ABM is enabled
  16.784236	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  16.784250	ABM numeric status: 3
  16.784253	ABM string status: floating
  16.822177	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  16.858555	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  16.895438	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  16.895459	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  16.895469	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  16.895479	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  16.895484	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  16.895492	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  18.474146	upsdrv_updateinfo...
  18.724923	libusb_get_interrupt: Connection timed out
  18.724952	Got 0 HID objects...
  18.724956	Quick update...
  18.762579	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  18.762596	ABM is enabled
  18.799640	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  18.799662	ABM numeric status: 3
  18.799667	ABM string status: floating
  18.838017	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  18.874026	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  18.911419	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  18.911470	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  18.911551	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  18.911562	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  18.911568	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  18.911575	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  20.475753	upsdrv_updateinfo...
  20.726863	libusb_get_interrupt: Connection timed out
  20.726900	Got 0 HID objects...
  20.726914	Quick update...
  20.760427	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  20.760447	ABM is enabled
  20.797526	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  20.797551	ABM numeric status: 3
  20.797555	ABM string status: floating
  20.836150	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  20.871759	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  20.909158	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  20.909198	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  20.909216	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  20.909240	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  20.909248	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  20.909256	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  22.477327	upsdrv_updateinfo...
  22.728159	libusb_get_interrupt: Connection timed out
  22.728181	Got 0 HID objects...
  22.728185	Quick update...
  22.758007	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  22.758018	ABM is enabled
  22.795300	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  22.795314	ABM numeric status: 3
  22.795318	ABM string status: floating
  22.833432	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  22.869423	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  22.906797	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  22.906815	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  22.906827	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  22.906835	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  22.906841	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  22.906846	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  24.478878	upsdrv_updateinfo...
  24.729082	libusb_get_interrupt: Connection timed out
  24.729108	Got 0 HID objects...
  24.729123	Quick update...
  24.755833	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  24.755842	ABM is enabled
  24.793278	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  24.793308	ABM numeric status: 3
  24.793314	ABM string status: floating
  24.831278	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  24.867513	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  24.904643	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  24.904658	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  24.904664	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  24.904669	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  24.904672	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  24.904683	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  26.479712	upsdrv_updateinfo...
  26.730527	libusb_get_interrupt: Connection timed out
  26.730547	Got 0 HID objects...
  26.730552	Quick update...
  26.753828	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  26.753836	ABM is enabled
  26.790729	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  26.790742	ABM numeric status: 3
  26.790746	ABM string status: floating
  26.829004	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  26.865102	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  26.902101	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  26.902129	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  26.902134	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  26.902140	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  26.902144	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  26.902150	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  28.480219	upsdrv_updateinfo...
  28.730685	libusb_get_interrupt: Connection timed out
  28.730705	Got 0 HID objects...
  28.730711	Quick update...
  28.769591	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  28.769605	ABM is enabled
  28.806410	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  28.806425	ABM numeric status: 3
  28.806430	ABM string status: floating
  28.844661	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  28.880694	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  28.918039	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  28.918057	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  28.918067	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  28.918101	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  28.918106	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  28.918113	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  30.481806	upsdrv_updateinfo...
  30.732316	libusb_get_interrupt: Connection timed out
  30.732335	Got 0 HID objects...
  30.732340	Quick update...
  30.767207	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  30.767220	ABM is enabled
  30.804256	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  30.804271	ABM numeric status: 3
  30.804276	ABM string status: floating
  30.842794	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  30.878642	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  30.915760	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  30.915789	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  30.915795	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  30.915800	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  30.915803	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  30.915807	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  32.482501	upsdrv_updateinfo...
  32.733127	libusb_get_interrupt: Connection timed out
  32.733148	Got 0 HID objects...
  32.733152	Quick update...
  32.764912	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  32.764926	ABM is enabled
  32.801953	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  32.801967	ABM numeric status: 3
  32.801970	ABM string status: floating
  32.840199	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  32.876214	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  32.913253	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  32.913272	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  32.913278	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  32.913283	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  32.913287	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  32.913291	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0
  34.484081	upsdrv_updateinfo...
  34.735026	libusb_get_interrupt: Connection timed out
  34.735045	Got 0 HID objects...
  34.735049	Quick update...
  34.762868	Path: UPS.BatterySystem.Charger.ABMEnable, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 1
  34.762881	ABM is enabled
  34.799901	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  34.799914	ABM numeric status: 3
  34.799919	ABM string status: floating
  34.838031	Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
  34.873920	Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, ReportID: 0x09, Offset: 0, Size: 32, Value: 0
  34.911033	Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
  34.911055	Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x01, Offset: 24, Size: 8, Value: 0
  34.911065	Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x01, Offset: 16, Size: 8, Value: 1
  34.911074	Path: UPS.BatterySystem.Charger.Mode, Type: Feature, ReportID: 0x26, Offset: 8, Size: 8, Value: 3
  34.911079	ABM CHRG/DISCHRG legacy string status (ups.status): chrg
  34.911086	Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x01, Offset: 8, Size: 8, Value: 0

Cheers,
 James.