[Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
Todd Benivegna
todd at benivegna.com
Fri Aug 7 00:48:55 BST 2020
Ok guys,
So we just had a storm roll through and of course we lost power for just a split second. This time I was actually home for it. Sure enough, the servers shutdown and wouldn’t boot all the way up until I restarted my Synology. I grep’d the syslog and here’s the results:
> proton at proton:~$ sudo grep upsmon /var/log/syslog
> Aug 6 19:19:09 proton upsmon[1552]: UPS ups at 192.168.1.70 on battery
> Aug 6 19:19:14 proton upsmon[1552]: UPS ups at 192.168.1.70 on line power
> Aug 6 19:19:44 proton upsmon[1552]: UPS ups at 192.168.1.70: forced shutdown in progress
> Aug 6 19:19:44 proton upsmon[1552]: Executing automatic power-fail shutdown
> Aug 6 19:19:45 proton upsmon[1552]: Auto logout and shutdown proceeding
> Aug 6 19:19:50 proton upsmon.conf: UPS status is
> Aug 6 19:19:59 proton upsmon[1545]: fopen /run/nut/upsmon.pid: No such file or directory
> Aug 6 19:19:59 proton upsmon[1545]: UPS: ups at 192.168.1.70 (slave) (power value 1)
> Aug 6 19:19:59 proton upsmon[1545]: Using power down flag file /etc/killpower
> Aug 6 19:19:59 proton systemd[1]: nut-monitor.service: Can't open PID file /run/nut/upsmon.pid (yet?) after start: Operation not permitted
> Aug 6 19:19:59 proton upsmon[1557]: Startup successful
> Aug 6 19:19:59 proton upsmon[1558]: UPS [ups at 192.168.1.70]: connect failed: Connection failure: Network is unreachable
> Aug 6 19:19:59 proton upsmon[1558]: Communications with UPS ups at 192.168.1.70 lost
> Aug 6 19:20:04 proton upsmon[1558]: UPS [ups at 192.168.1.70]: connect failed: Connection failure: Network is unreachable
> Aug 6 19:20:04 proton upsmon[1558]: UPS ups at 192.168.1.70 is unavailable
> Aug 6 19:28:03 proton upsmon[1558]: Communications with UPS ups at 192.168.1.70 established
> proton at proton:~$ sudo upsc UPS at 192.168.1.70
> Init SSL without certificate database
> battery.charge: 100
> battery.charge.low: 10
> battery.charge.warning: 50
> battery.date: 2001/09/25
> battery.mfr.date: 2016/12/11
> battery.runtime: 2076
> battery.runtime.low: 120
> battery.type: PbAc
> battery.voltage: 13.6
> battery.voltage.nominal: 12.0
> device.mfr: American Power Conversion
> device.model: Back-UPS NS 650M1
> device.serial: 4B1650P02109
> device.type: ups
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 5
> driver.parameter.port: auto
> driver.version: DSM6-2-25364-191230
> driver.version.data: APC HID 0.95
> driver.version.internal: 0.38
> input.sensitivity: medium
> input.transfer.high: 139
> input.transfer.low: 92
> input.transfer.reason: input voltage out of range
> input.voltage: 121.0
> input.voltage.nominal: 120
> ups.beeper.status: enabled
> ups.delay.shutdown: 20
> ups.firmware: 929.a5 .D USB FW
> ups.load: 15
> ups.mfr: American Power Conversion
> ups.mfr.date: 2016/12/11
> ups.model: Back-UPS NS 650M1
> ups.productid: 0002
> ups.realpower.nominal: 360
> ups.serial: 4B1650P02109
> ups.status: OL
> ups.test.result: No test initiated
> ups.timer.reboot: 0
> ups.timer.shutdown: -1
> ups.vendorid: 051d
Looks like what we did earlier didn’t work as it just says “UPS Status is” with nothing after it. Also after grep’d the syslog I got the current status of the UPS.
What do you think? I really just don’t understand what the heck is going on. Like I said before, whenever I test manually it works! This is crazy.
Thanks for all your help,
Todd
--
Todd Benivegna // todd at benivegna.com
On Aug 5, 2020, 7:29 AM -0400, Todd Benivegna <todd at benivegna.com>, wrote:
> > grep nut /etc/passwd
>
> nut:x:129:134::/var/lib/nut:/usr/sbin/nologin
>
> > In your manual test do you restore utility power after 3-5 seconds?
> Yes, I have tried that. I have also tried less than one second. I’ve tried for 1-2 minutes, for 3-5 minutes, I’ve tried just about every length of time and all appears Ok when I manually test.
>
> --
> Todd Benivegna // todd at benivegna.com
> On Aug 5, 2020, 3:26 AM -0400, Roger Price <roger at rogerprice.org>, wrote:
> > On Tue, 4 Aug 2020, Todd Benivegna wrote:
> >
> > > Sorry. I've lost the thread here, what is the "it" you refer to?
> > >
> > > I’m not an linux expert so you’ll have to bear with me, but I guess the it I
> > > was referring to whatever NUT is using since what we’re editing is a config
> > > file, not a script; it doesn’t have a shebang at the top.
> >
> > The command sequence specified by the SHUTDOWNCMD declaration is called from
> > upsmon (a program written in C).
> >
> > > If you run the command
> > > grep nut /etc/password
> > >
> > > I got: grep: /etc/password: No such file or directory
> >
> > Sorry, my mistake it should be
> >
> > grep nut /etc/passwd
> >
> > > That may seem to be the case, however, whenever I test by manually pulling the
> > > power, the servers stay up and all appears normal. It has happened three
> > > times now where I am away and the power goes out for 3-5 seconds and the
> > > servers shutdown and will stay down, even if I try to power back on, until I
> > > restart the Synology NAS.
> >
> > In your manual test do you restore utility power after 3-5 seconds?
> >
> > Roger
> > _______________________________________________
> > Nut-upsuser mailing list
> > Nut-upsuser at alioth-lists.debian.net
> > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200806/1025ae10/attachment-0001.html>
More information about the Nut-upsuser
mailing list