[Nut-upsuser] AVRX750/500 issues
objecttothis
objecttothis at gmail.com
Wed Jul 22 18:52:41 BST 2020
Thanks for chiming in @David Zomaya. Tripp Lite replaced my AVRX550U once thinking that the powering back on was a defective unit, but the replacement does the same thing. The SN on the first one is 2935AVHOM87BB00152. NUT has my model listed as protocol 2010, so that needs to be corrected to 2012, but I'm not sure if anyone is doing active development on it right now.
I also have a Tripp Lite OMNIVSX1000D with SN 2904AVLOM87E400114. That model is not on NUT compatibility list and I have an open ticket (#00681437) to get the relevant protocol information so that I can then submit it to NUT and see about getting support added to it, but the ticket has been open since May 28 and no protocol information from Tripp Lite. Any chance you could kick the tires to see what the delay is?
-----Original Message-----
From: David Zomaya <David_Zomaya at tripplite.com>
Sent: Wednesday, July 22, 2020 6:29 PM
To: nut-upsuser at alioth-lists.debian.net; objecttothis at gmail.com
Subject: Re: [EXTERNAL] [Nut-upsuser] AVRX750/500 issues
For what it's worth, productID should = protocol number.
I think objecttothis had 2012 but Scott had 3024. A lot of our smaller standby and line-interactive units recently changed to 302x protocols, hence this post to the development list:
https://alioth-lists.debian.net/pipermail/nut-upsdev/2020-June/007473.html
In any case, the support team or I can confirm if you send us serial numbers.
Thank you,
David Zomaya
Tripp Lite
From: Nut-upsuser <nut-upsuser-bounces+david_zomaya=tripplite.com at alioth-lists.debian.net> on behalf of objecttothis <objecttothis at gmail.com>
Sent: Wednesday, July 22, 2020 8:57 AM
To: nut-upsuser at alioth-lists.debian.net
Subject: [EXTERNAL] [Nut-upsuser] AVRX750/500 issues
This is an EXTERNAL email. Please take a moment and think before clicking any links or opening any attachments from this email. If suspicious, please forward to ishelpdesk at tripplite.com for review.
______________________________________________________________________
I wouldn't be surprised if they both use the same driver. I think they are essentially the same model, but with one having a slightly larger battery. My issue is primarily with the UPS turning back on after having shut off like it should. @Scott Colby if you take a look at the config files I posted in the github issue I created, perhaps that will give you some hints on your issue. Maybe there are differences in the config that would give you a clue as to why your Pi isn't shutting off. Does it work properly if you have it shut down from a timer instead of low battery? Are you wanting your UPS to turn back on after a delay, or just turn back on when power is restored to the mains?
-----Original Message-----
From: Nut-upsuser <nut-upsuser-bounces+objecttothis=gmail.com at alioth-lists.debian.net> On Behalf Of nut-upsuser-request at alioth-lists.debian.net
Sent: Wednesday, July 22, 2020 3:00 PM
To: nut-upsuser at alioth-lists.debian.net
Subject: Nut-upsuser Digest, Vol 181, Issue 5
Send Nut-upsuser mailing list submissions to
nut-upsuser at alioth-lists.debian.net
To subscribe or unsubscribe via the World Wide Web, visit
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_cgi-2Dbin_mailman_listinfo_nut-2Dupsuser&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=vC2kcmM-UcihmSZxRAeTUX22fYSlpXNHw9rpFUxfGiQ&s=Rpy7pnwa-6z9Wx0ikcpNLFh4nTj6tRsEueSvrXsU0Q4&e=
or, via email, send a message with subject or body 'help' to
nut-upsuser-request at alioth-lists.debian.net
You can reach the person managing the list at
nut-upsuser-owner at alioth-lists.debian.net
When replying, please edit your Subject line so it is more specific than "Re: Contents of Nut-upsuser digest..."
Today's Topics:
1. Re: AVR750U Low Power not Triggering Shutdown (Scott Colby)
----------------------------------------------------------------------
Message: 1
Date: Wed, 22 Jul 2020 00:07:03 -0400
From: "Scott Colby" <scott at scolby.com>
To: nut-upsuser at alioth-lists.debian.net
Cc: objecttothis at gmail.com
Subject: Re: [Nut-upsuser] AVR750U Low Power not Triggering Shutdown
Message-ID: <4f09187f-5718-4202-9550-3a61037deef9 at www.fastmail.com>
Content-Type: text/plain
Hello again,
I had to take a hiatus from troubleshooting this issue, but I'm back now with new information. As before, I am working with a TrippLite AVR750U purchased earlier this year. However, I've switched from the FreeBSD-based router to a Debian-based Raspberry Pi for reasons that are probably not worth explaining at the moment :^)
I've included my current configuration files at the bottom of this message.
I've run a few experiments to try to determine what's going on here.
I'll include the shell command and any output delimited by ###'s, followed by my observation of the behavior of the Raspberry Pi and the UPS.
First Experiment
################
$ sudo upsmon -c fsd
Network UPS Tools upsmon 2.7.4
Broadcast message from nut at raspi (somewhere) (Tue Jul 21 23:27:01
Executing automatic power-fail shutdown
Broadcast message from nut at raspi (somewhere) (Tue Jul 21 23:27:01
Auto logout and shutdown proceeding
$ Connection to pi closed by remote host.
Connection to pi closed.
################
I ran this command under two sets of conditions:
- UPS plugged in to the mains
- UPS unplugged from the mains, then plugging it back in approximately
60 seconds after it turned off
In both cases, the Pi shut down cleanly after approximately 5 seconds (FINALDELAY?), and the UPS turned off after approximately 25 seconds (FINALDELAY + the default offdelay?) However, the UPS never came back up.
Second Experiment
#################
$ sudo upsdrvctl shutdown
Network UPS Tools - UPS driver controller 2.7.4 Network UPS Tools - Generic HID driver 0.41 (2.7.4) USB communication driver 0.33 Using subdriver: TrippLite HID 0.82 Initiating UPS shutdown #################
Nothing happened as far as I can tell. I waited 2 minutes before moving on.
Third Experiment
################
$ sudo /lib/nut/usbhid-ups -a AVR750U -k Network UPS Tools - Generic HID driver 0.41 (2.7.4) USB communication driver 0.33 Using subdriver: TrippLite HID 0.82 Initiating UPS shutdown $ Connection to pi closed.
################
The UPS turned off after approximately 20 seconds, but there was no clean shut down of the Pi. I think this is expected.
Fourth Experiment
#################
$ sudo upscmd -u admin -p passw0rd AVR750U shutdown.return OK #################
I also ran this experiment under two conditions:
- UPS plugged into the mains
- UPS unplugged then reconnected approximately 30 seconds after
shutdown
In the first case, nothing happened. In the second case, the UPS shut off after 20 seconds. However, it did not turn back on after I reconnected it to power.
Fifth Experiment
################
To answer Roger's questions, I did the following:
- ran `upslog -f '{"time": "%TIME @Y- at m-@dT at H:@M:@S%", "charge": %VAR battery.charge%, "status": "%VAR ups.status%", "runtime": %VAR battery.runtime%}' -i 10 -l upslog.jsonl -s AVR750U` and tailed its output
- unplugged from the mains and observed a wall message and status
change from upslog
- reconnected to the mains and observed a wall message and status
change
- unplugged again and observed another wall message and status
change
- waited for the battery to run down
- here's an extract from that log:
{"time": "2020-07-22T02:20:22", "charge": 3, "status": "OB DISCHRG", "runtime": 138}
{"time": "2020-07-22T02:20:32", "charge": 3, "status": "OB DISCHRG", "runtime": 128}
{"time": "2020-07-22T02:20:42", "charge": 3, "status": "OB DISCHRG", "runtime": 123}
{"time": "2020-07-22T02:20:52", "charge": 2, "status": "OB DISCHRG", "runtime": 108}
{"time": "2020-07-22T02:21:02", "charge": 2, "status": "OB DISCHRG", "runtime": 98}
{"time": "2020-07-22T02:21:12", "charge": 2, "status": "OB DISCHRG", "runtime": 93}
{"time": "2020-07-22T02:21:22", "charge": 2, "status": "OB DISCHRG", "runtime": 77}
{"time": "2020-07-22T02:21:32", "charge": 1, "status": "OB DISCHRG", "runtime": 67}
{"time": "2020-07-22T02:21:42", "charge": 1, "status": "OB DISCHRG", "runtime": 62}
{"time": "2020-07-22T02:21:52", "charge": 1, "status": "OB DISCHRG", "runtime": 52}
{"time": "2020-07-22T02:22:02", "charge": 0, "status": "OB DISCHRG", "runtime": 41}
{"time": "2020-07-22T02:22:12", "charge": 0, "status": "OB DISCHRG", "runtime": 31}
{"time": "2020-07-22T02:22:22", "charge": 0, "status": "OB DISCHRG", "runtime": 21}
{"time": "2020-07-22T02:22:32", "charge": 0, "status": "OB DISCHRG", "runtime": 11}
{"time": "2020-07-22T02:22:42", "charge": 0, "status": "OB DISCHRG", "runtime": 1}
{"time": "2020-07-22T02:22:52", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T02:23:02", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T02:23:12", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T02:23:22", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T02:23:32", "charge": 0, "status": "OB DISCHRG", "runtime": 0} ...
{"time": "2020-07-22T03:19:52", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T03:20:02", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T03:20:12", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T03:20:22", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T03:20:32", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T03:20:42", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
{"time": "2020-07-22T03:20:52", "charge": 0, "status": "OB DISCHRG", "runtime": 0}
- !!!!! it ran for almost an hour on charge 0 runtime 0 and never
raised the LB flag
################
So, here are my questions:
- Have I made a configuration error?
- Why is the behavior of `upsdrvctl shutdown` different from that
of `usbhid-ups -k`?
- Why doesn't the UPS ever turn back on on its own?
- What's going on with the LB flag never coming on and the runtime
being badly wrong?
I'm wondering if this is related to what objecttothis is experiencing with the AVRX500U. I'll CC them on this message. Further, I will reach out to TrippLite support to ask what version of the USB HID protocol my AVR750U is using.
Thanks,
Scott
My Configuration
################
# /etc/udev/rules.d/62-nut-usbups-custom.rules
# based on the 62-nut-usbups.rules that came with the package ACTION!="add|change", GOTO="nut-usbups_rules_end"
SUBSYSTEM=="usb_device", GOTO="nut-usbups_rules_real"
SUBSYSTEM=="usb", GOTO="nut-usbups_rules_real"
SUBSYSTEM!="usb", GOTO="nut-usbups_rules_end"
LABEL="nut-usbups_rules_real"
# TrippLite
# e.g. TrippLite AVR750U - usbhid-ups
ATTR{idVendor}=="09ae", ATTR{idProduct}=="3024", MODE="664", GROUP="nut"
LABEL="nut-usbups_rules_end"
# nut.conf
MODE=standalone
# ups.conf
[AVR750U]
driver = usbhid-ups
productid = 3042
port = auto
# upsd.conf
# empty
# upsd.users
[admin]
password = passw0rd
instcmds = ALL
[upsmon]
password = passw0rd
upsmon master
# upsmon.conf
MONITOR AVR750U 1 upsmon passw0rd master MINSUPPLIES 1 SHUTDOWNCMD "/sbin/shutdown -h +0"
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower
RBWARNTIME 43200
NOCOMMWARNTIME 300
FINALDELAY 5
------------------------------
Subject: Digest Footer
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser at alioth-lists.debian.net
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_cgi-2Dbin_mailman_listinfo_nut-2Dupsuser&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=vC2kcmM-UcihmSZxRAeTUX22fYSlpXNHw9rpFUxfGiQ&s=Rpy7pnwa-6z9Wx0ikcpNLFh4nTj6tRsEueSvrXsU0Q4&e=
------------------------------
End of Nut-upsuser Digest, Vol 181, Issue 5
*******************************************
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser at alioth-lists.debian.net
https://urldefense.proofpoint.com/v2/url?u=https-3A__alioth-2Dlists.debian.net_cgi-2Dbin_mailman_listinfo_nut-2Dupsuser&d=DwIGaQ&c=f9s1WCuF-N6cmD_YaZ7gBg&r=lhr3k4au5dVQgHY_iS-v_t9g8PHVkn8Px_wyaupZGfQ&m=vC2kcmM-UcihmSZxRAeTUX22fYSlpXNHw9rpFUxfGiQ&s=Rpy7pnwa-6z9Wx0ikcpNLFh4nTj6tRsEueSvrXsU0Q4&e=
________________________________
This message is for the addressee's use only. It may contain confidential information. If you receive this message in error, please delete it and notify the sender. Tripp Lite disclaims all warranties and liabilities, and assumes no responsibility for viruses which may infect an email sent to you from Tripp Lite and which damage your electronic systems or information. It is your responsibility to maintain virus detection systems to prevent damage to your electronic systems and information.
More information about the Nut-upsuser
mailing list