[Nut-upsuser] AVR750U Low Power not Triggering Shutdown
Manuel Wolfshant
wolfy at nobugconsulting.ro
Sun Jun 28 04:11:02 BST 2020
On 6/28/20 5:54 AM, Scott Colby wrote:
>
> I'm not convinced this is the problem; I think that pfSense has
> an alternative way of running the NUT components:
> # ps aux | grep ups
> root 45456 0.0 0.1 6796 884 - Is 02:22 0:00.01 /usr/local/sbin/upsmon
> uucp 45751 0.0 0.1 6796 772 - S 02:22 0:00.10 /usr/local/sbin/upsmon
> uucp 46796 0.0 0.1 6888 888 - Ss 02:22 0:00.45 /usr/local/libexec/nut/usbhid-ups -a AVR750U
> root 56752 0.0 0.1 6788 832 - Ss 02:22 0:00.13 /usr/local/sbin/upsd -u root
> root 39437 0.0 0.2 6828 2464 0 S+ 02:46 0:00.01 grep ups
>
> Is there anything else that should be running?
AFAIK, no, those 3 daemons should do the job. But just for the fun of
it, I would test changing that variable anyway. There is nothing to
lose, after all.
>
> Would you expect `upsmon -c fsd` to not work as I described above
> (system halting but UPS not power cycling) if MODE was set to none
> but upsmon, the driver, and upsd were running?
If it is running ( i.e. started ) -c fsd should trigger an immediate
shutdown. quote from man upsmon:
*-c* /command/
Send the command /command/ to the existing upsmon process. Valid
commands are:
*fsd*
shutdown all master UPSes (use with caution)
>>> # cat ups.conf
>>> [AVR750U]
>>> driver=usbhid-ups
>>> port=auto
>>> productid=3024
>>>
>>> # cat upsmon.conf
>>> MONITOR AVR750U 1 local-monitor <password> master
>>> [...]
>>> driver.version.internal: 0.41
>>> input.frequency: 5990.0
>> This value is definitely incorrectly reported. Based on the voltages
>> below I assume you are in USA and the displayed value could be an
>> incorrectly scaled 59.9 Hz
>>
>>
> You are correct about my location and expected voltage. Is there
> somewhere that I can change the scaling factor used by NUT?
>
>
not that I know of. and
https://networkupstools.org/docs/man/usbhid-ups.html does not show any
either. fortunately the errors are purely cosmetic
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200628/092f8f1c/attachment.html>
More information about the Nut-upsuser
mailing list