[Nut-upsuser] dual cyberpower 2200 on windows
    Richard Ward 
    richard at kafiandrich.com
       
    Fri Aug 12 03:46:17 BST 2022
    
    
  
Thanks Charles,
The devices are the same make and model, bought at the same time. both
return the following when running upsc, and I cant see any way to
distiguish the 2 apart. Any suggestions, other than to connect them to
different servers? :
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 1031
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 17.3
battery.voltage.nominal: 24
device.mfr: CPS
device.model: Value2200E
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 1
driver.parameter.port: auto
driver.parameter.productid: 0501
driver.parameter.vendorid: 0764
driver.version: Windows-v2.6.5-5-7-g72f380c
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.38
input.transfer.high: 0
input.transfer.low: 0
input.voltage: 239.0
input.voltage.nominal: 230
output.voltage: 241.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 29
ups.mfr: CPS
ups.model: Value2200E
ups.productid: 0501
ups.realpower.nominal: 1320
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764
On Fri, 12 Aug 2022 at 12:18, Charles Lepple <clepple at gmail.com> wrote:
> On Aug 11, 2022, at 10:06 AM, Richard Ward wrote:
> >
> >  I need to specify the usb port in the ups.conf file, but I cannot work
> out how to find the path for each ups to fill in the port = section. If I
> leave it as port = auto, then only 1 unit can be monitored at a time.
> >
> as the documentation describes, just leave port=auto and use the other
> USB-specific options to distinguish USB UPSes from one another:
> https://networkupstools.org/docs/man/usbhid-ups.html#_implementation
> (port is a relic from the days of serial UPSes)
>
> If the UPSes are truly identical (no unique serial number), then that's
> something you should take up with your UPS vendor.
>