Hi Gene,
On 5/16/23 21:08, gene heskett wrote:
> Take an extra vitamin b1 and start hacking ;o)
yeah ;-)
>
> Seriously, if its that important, do as I did when my last wife was
> dying of COPD.
:( sorry to hear
> Leave your ups setup as is but for under $10k (USD),
> have an automatic home sized standby generator installed to run the
> important stuff,
no room for that and also our set-up is kind of large, the two UPS
systems I'm talking about are 800kVA each and without doing the actual
maths, I'd guess we would need at least a 100kW generator.
That would come with all sort of other problems (getting a room,
deciding whether to run all the time for quick mains sync, i.e.
generator wheel is powered by mains when not needed, fuel exchange every
few months as gas add-ons tend to flocculate(?) when stored too long, ...).
So, I doubt that will materialize any time soon ;-)