[Nut-upsuser] FSD sequence: Waiting for bigger and slower clients before cutting power
Magnus Holmgren
magnus.holmgren at milientsoftware.com
Fri Oct 27 15:25:58 BST 2023
Hi, and thanks for this great piece of free software! I've been meaning to
sort this out for some time, but we don't get power outages that often,
fortunately...
So, correct me if I'm wrong, but from the documentation at https://
networkupstools.org/docs/user-manual.chunked/
Configuration_notes.html#UPS_shutdown, and also reading upsmon.c, when a UPS
goes OB LB (assuming we have a single UPS connected to a primary and supplying
power to the primary and some number of secondaries), the primary notifies the
secondaries, the secondaries wait for FINALDELAY and then execute SHUTDOWNCMD
immediately followed by exiting, thereby disconnecting from the primary, and
the primary, after seeing all secondaries disconnect, proceed with its
shutdown (only waiting for FINALDELAY), which ends with telling the UPS to cut
the power (without delay too, right?).
Again, correct me if I'm wrong, Is it only I who find this a bit flawed? I
would like for the secondaries to stay connected until they shut down. We have
a server with a bunch of virtual machines on, and they can take a couple of
minutes to shut down. Otherwise the primary can easily cut the power
prematurely. Avoiding this, it seems, could pretty easily be accomplished by
having upsmon wait, perhaps in a separate loop, for the INT/TERM/QUIT signal
(it would still be necessary to configure the service manager such that upsmon
is terminated as late as possible). The primary could start shutting down its
services in the meantime, but upsmon would hold the poweroff until the
secondaries have disconnected (or HOSTSYNC expires).
Surely this would be better than cranking up FINALDELAY on the primary and
always waiting for a fixed period of time, as suggested in https://alioth-lists.debian.net/pipermail/nut-upsuser/2012-April/007550.html? I guess I could
try writing a SHUTDOWNCMD script that doesn't exit until most other services
have also done so, taking care not to create a deadlock situation.
Another option would be to use upssched to shut down the "big rig" earlier. It
just seems unsatisfying to me that upssched is entirely time-based. It would
be nice if it were easier to trigger off battery.charge or battery.runtime
going below arbitrary values instead of just the on battery and low battery
statuses.
How do others solve this?
--