[Nut-upsuser] Digitech support
Jim Klimov
jimklimov+nut at gmail.com
Wed Dec 17 10:03:48 GMT 2025
> Can't open /run/nut/nutdrv_qx-ups1: No such file or directory
That's the driver checking if another instance of it is running. Newer
releases should log it less frighteningly.
> ... but nut-driver complained so...
The `nut-driver at upsname` is a systemd instance wrapping an execution of a
NUT driver program as a daemon. It is the driver program that actually
complains, and its debug logs we want to see to figure out what puzzle
pieces did not fit together.
For an in-vivo debug bump (so the detailed logs end up in systemd journal)
you can also temporarily set `debug_min` in the `ups.conf`, see
https://github.com/networkupstools/nut/wiki/Changing-NUT-daemon-debug-verbosity
for
more details (they varied from one NUT release to another).
Jim
On Wed, Dec 17, 2025 at 9:45 AM Stephen Davies <sdavies at sdc.com.au> wrote:
> Thanks for the feedback.
>
> The NUT vwersion is 2.8.2.1.
>
> I am in the process of building a new Rocky Linux 10 server after my old
> Centos 7 server died.
>
> The old box used upsSmart to access the UPS but that relies on an X
> server and does not work on ocky 10.
>
> One of the errors from your suggested test is:
>
> Can't open /run/nut/nutdrv_qx-ups1: No such file or directory
>
> I had "langid_fix=0x0409" in ups.conf but nut-driver complained so I
> removed it.
>
> Cheers,
> Stephen
>
> On 17/12/25 18:47, Jim Klimov wrote:
> > Cheers,
> >
> > What NUT version is involved? Per `nut-driver at ups1` I suppose it is
> > some v2.8.x, and reports like https://github.com/networkupstools/nut/
> > pull/638 <https://github.com/networkupstools/nut/pull/638> and https://
> > github.com/networkupstools/nut/issues/674 <https://github.com/
> > networkupstools/nut/issues/674> suggest the needed support was merged
> > before v2.8.0, so that should suffice.
> >
> > It may well be that the manufacturer moved on and stamped the same
> > label onto a completely unrelated device (or firmware), these things
> > sadly tend to happen as products evolve.
> >
> > One of those discussions starts with a "|Device not supported|"
> > initially, but then it gets found "after opening and then closing the
> > OEM software" (UPSmart), and apparently by the end of the ticket they
> > got it working right away. The new hunnox subdriver introduced in PR 638
> > changed the initialization to work with that, per https://github.com/
> > networkupstools/nut/pull/638#issuecomment-443558510 <https://github.com/
> > networkupstools/nut/pull/638#issuecomment-443558510> - notably there's a
> > sleep involved before the device returns valid info; maybe your device
> > or its firmware needs a longer one or something?
> >
> > Compared to settings in those tickets and HCL, your setup misses a
> > `langid_fix=0x0409` line, not sure if that makes the difference. This
> > seems to be a hardcoded default in hunnox_protocol() initializer at
> > https://github.com/networkupstools/nut/pull/638/changes#diff-
> > cb890ac7b82cb7a4f861284bcf39cc4f168312b61cb9455eb2755e345c0aa627R692-
> > R696 <https://github.com/networkupstools/nut/pull/638/changes#diff-
> >
> cb890ac7b82cb7a4f861284bcf39cc4f168312b61cb9455eb2755e345c0aa627R692-R696>
> >
> > Can you start the driver with higher verbosity to collect what/how it
> > probes of the device, and how that fails (with what errors), e.g.
> >
> > |nutdrv_qx -a ups1 -d 1 -DDDDDD|
> >
> > If there would be a long wall of text, maybe follow up with that as a
> > new GitHub issue?
> >
> > Hope this helps,
> > Jim Klimov
> >
> >
> >
> > On Wed, Dec 17, 2025 at 8:23 AM Stephen Davies via Nut-upsuser <nut-
> > upsuser at alioth-lists.debian.net <mailto:nut-upsuser at alioth-
> > lists.debian.net>> wrote:
> >
> > According to the support list, the Digitech 650VA UPS is supported
> but
> > when I try to connect to my unit, I get:
> > nut-driver at ups1[357464]: Device not supported!
> >
> > My ips.conf has:
> > [ups1]
> > driver = nutdrv_qx
> > port = auto
> > vendorid=0001
> > productid=0000
> > protocol=hunnox
> > novendor
> > noscanlangid
> >
> >
> >
> > _______________________________________________
> > Nut-upsuser mailing list
> > Nut-upsuser at alioth-lists.debian.net <mailto:Nut-upsuser at alioth-
> > lists.debian.net>
> > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
> > <
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser>
> >
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20251217/cf8451e7/attachment-0001.htm>
More information about the Nut-upsuser
mailing list