[Nut-upsuser] Recommended UPS to buy for use with NUT?
Rob MacGregor
rob.macgregor at gmail.com
Sun Jun 4 21:07:35 UTC 2006
On 6/4/06, Arjen de Korte <nut+users at de-korte.org> wrote:
>
> At least here in the Netherlands, quite a few (cheap) UPSes are sold
> nowadays that sport high VA ratings, but really lack the battery
> capacity needed to power even a modest load for more than a few minutes.
> Clay should avoid these at all cost.
MGE rather usefully do a runtime calculator where you put in the power
draw and required runtime and it suggests options from their range.
Worked like a charm when I used it, however there's a gotcha. An ups
with a 28 minute runtime may signal LB at 19 minutes, resulting in a
shutdown sometime sooner than you expect :)
If you need a 20 minute actual runtime you'll probably need a 30
minute theoretical runtime.
--
Please keep list traffic on the list.
Rob MacGregor
Whoever fights monsters should see to it that in the process he
doesn't become a monster. Friedrich Nietzsche