[Nut-upsuser] Belkin 800VA Universal AVR doesn't warn about battery
Arjen de Korte
nut+users at de-korte.org
Sun Jul 12 12:28:25 UTC 2009
Citeren Gasper Kozak <gasper.kozak op gmail.com>:
> I've installed the mentioned packages and LB event still doesn't get
> generated/reported.
That is bad. In that case we need the output of
/path/to/usbhid-ups -DD -a upsname
Note that I want exactly *two* debug flags here. Not more, not less.
You'll want to stop all parts of NUT, fire up the above command and
leave that running for about thirty seconds. Then kill the driver with
ctrl-C and post the results here, so we can have a look what is going
on.
> Just to make sure, if values displayed with upsc are set to these values
> battery.charge: 75
> battery.charge.low: 30
> battery.charge.warning: 30
>
> Then the driver should report LB when battery.charge is below
> battery.charge.low (30)?
No, that's the job of the UPS.
> What does battery.charge.warning have to do here?
It's the HID path 'UPS.PowerSummary.WarningCapacityLimit' as read by
NUT. If you're interested in finding out what it means, I suggest the
USB HID Power Device Class specifications. These are available online
(Google is your friend).
Best regards, Arjen
--
Please keep list traffic on the list
More information about the Nut-upsuser
mailing list