[Nut-upsuser] Belkin 800VA Universal AVR doesn't warn about battery
Arjen de Korte
nut+users at de-korte.org
Mon Jul 13 12:28:43 UTC 2009
Citeren Gasper Kozak <gasper.kozak op gmail.com>:
> Here it is, 30 seconds of output:
> http://pastebin.com/f2c5aa338
This is looking good. The HID path
(UPS.BELKINStatus.BELKINBatteryStatus) that we're using is available.
Bit 2 of the value reported (when converted to an int) will be set if
the battery is low and bit 6 will be set if the battery is empty. You
may want to run the driver in debug mode and log the lines with the
above path to see what is going on. Make sure to run the UPS with some
load until it switches off by itself (so don't use it to power any
systems at that time).
Best regards, Arjen
--
Please keep list traffic on the list
More information about the Nut-upsuser
mailing list