Citeren Gasper Kozak <gasper.kozak op gmail.com>:

> Here it is, 30 seconds of output:
> http://pastebin.com/f2c5aa338

This is looking good. The HID path  
(UPS.BELKINStatus.BELKINBatteryStatus) that we're using is available.  
Bit 2 of the value reported (when converted to an int) will be set if  
the battery is low and bit 6 will be set if the battery is empty. You  
may want to run the driver in debug mode and log the lines with the  
above path to see what is going on. Make sure to run the UPS with some  
load until it switches off by itself (so don't use it to power any  
systems at that time).

Best regards, Arjen
-- 