[Nut-upsuser] ULTRA 2000 ULT33046 configuration
JW Simpson
john at swajime.com
Mon Nov 23 19:03:39 UTC 2009
On Fri, 2009-11-20 at 20:49 +0100, Arjen de Korte wrote:
> Citeren JW Simpson <john at swajime.com>:
>
> > # # lsusb -vd 0d9f:0002|sed -ne '/^\w/p;/\bi/p'
> > # Bus 002 Device 002: ID 0d9f:0002 Powercom Co., Ltd
> > # Device Descriptor:
> > # idVendor 0x0d9f Powercom Co., Ltd
> > # idProduct 0x0002
> > # iManufacturer 1 POWERCOM CO., LTD.
> > # iProduct 2 USB to Serial
> > # iSerial 0
> > # iConfiguration 4 Sample HID
> > # iInterface 0
> > # Device Status: 0x0000
> >
> > # compatibility:
> > http://www.networkupstools.org/compat/stable.html
>
> This device should be supported by the 'powercom' driver (see 'man 8
> powercom' for options that may need to be provided in 'ups.conf'),
> provided cypress_m8 in your kernel is recent enough to recognize the
> build in USB to serial converter. If it is, you should point the
> 'port' to the /dev/ttyUSBx port that is created when the device is
> plugged in.
>
> Best regards, Arjen
Thank you Arjen,
I tried each set of settings listed in the powercom manpage, as you
suggested, until one claimed success.
Success ! (I think ?)
Unless that weird noise the UPS made was bad news ...
The settings for type=IMP resulted in a success status.
I stopped there, and did not try KIN, BNT, or BNT-other.
Should I try those too?
That took so long now, I've forgotten what I'm supposed to do next :-( .
root at system76-pc:/etc/nut# cat ups.conf
# Start with
#
# # upsdrvctl -u nut -D start MEGATEC
MODE=netserver
user=nut
# Ultra ULT33046 2000 VA 1200 W Backup UPS with AVR (B000GC98H8)
# From stickers:
# Label: ULTRA
# Model: RCD-UPS2000D
# Serial Number: 40206430906
# # lsusb -vd 0d9f:0002|sed -ne '/^\w/p;/\bi/p'
# Bus 002 Device 002: ID 0d9f:0002 Powercom Co., Ltd
# Device Descriptor:
# idVendor 0x0d9f Powercom Co., Ltd
# idProduct 0x0002
# iManufacturer 1 POWERCOM CO., LTD.
# iProduct 2 USB to Serial
# iSerial 0
# iConfiguration 4 Sample HID
# iInterface 0
# Device Status: 0x0000
[POWERCOM_TRUST]
driver=powercom
port=/dev/ttyUSB0
linevoltage=120
manufacturer=PowerCom
modelname=RCD-UPS2000D
serialnumber=40206430906
type=Trust
numOfBytesFromUPS=11
methodOfFlowControl=dtr0rts1
shutdownArguments={{0,10},n}
voltage={1.9216,-0.0977,0.9545,0.0000}
frequency={0.00020997,0.00020928}
batteryPercentage={5.0000,0.3268,-825.00,4.5639,-835.82}
loadPercentage={6.1343,-0.3808,4.3110,0.1811}
validationSequence={{5,0},{7,0},{8,0}}
# output for TRUST
#
# root at system76-pc:/etc/nut# upsdrvctl -u nut -DDDDD start
POWERCOM_TRUST
# Network UPS Tools - UPS driver controller 2.4.1
# Starting UPS: POWERCOM_TRUST
# exec: /lib/nut/powercom -a POWERCOM_TRUST -u nut
# Network UPS Tools - PowerCom protocol UPS driver 0.12 (2.4.1)
# writing error
# Nov 23 12:18:49 system76-pc powercom[11965]: Startup successful
# Nov 23 12:18:49 system76-pc powercom[11965]: writing error
# Nov 23 12:18:51 system76-pc powercom[11965]: data receiving error
(validation check)
# Nov 23 12:19:23 system76-pc last message repeated 16 times
[POWERCOM_KP625AP]
driver=powercom
port=/dev/ttyUSB0
linevoltage=120
manufacturer=PowerCom
modelname=RCD-UPS2000D
serialnumber=40206430906
type=KP625AP
numOfBytesFromUPS=16
methodOfFlowControl=dtr0rts1
shutdownArguments={{0,10},n}
voltage={1.9216,-0.0977,0.9545,0.0000}
frequency={0.00020997,0.00020928}
batteryPercentage={5.0000,0.3268,-825.00,4.5639,-835.82}
loadPercentage={6.1343,-0.3808,4.3110,0.1811}
validationSequence={{5,0x80},{7,0},{8,0}}
# output for KP625AP
#
# root at system76-pc:/etc/nut# upsdrvctl -u nut -DDDDD start
POWERCOM_KP625AP
# Network UPS Tools - UPS driver controller 2.4.1
# Starting UPS: POWERCOM_KP625AP
# exec: /lib/nut/powercom -a POWERCOM_KP625AP -u nut
# Network UPS Tools - PowerCom protocol UPS driver 0.12 (2.4.1)
# writing error
# Nov 23 12:47:55 system76-pc powercom[14159]: Startup successful
# Nov 23 12:47:55 system76-pc powercom[14159]: writing error
# Nov 23 12:47:58 system76-pc powercom[14159]: data receiving error
(validation check)
# Nov 23 12:48:30 system76-pc last message repeated 16 times
[POWERCOM_Egys]
driver=powercom
port=/dev/ttyUSB0
linevoltage=120
manufacturer=PowerCom
modelname=RCD-UPS2000D
serialnumber=40206430906
type=Egys
numOfBytesFromUPS=16
methodOfFlowControl=no_flow_control
shutdownArguments={{0,10},n}
voltage={1.9216,-0.0977,0.9545,0.0000}
frequency={0.00020997,0.00020928}
batteryPercentage={5.0000,0.3268,-825.00,2.2105,-355.37}
loadPercentage={6.1343,-0.3808,1.3333,0.6667}
validationSequence={{5,0x80},{7,0},{8,0}}
# output for Egys
#
# root at system76-pc:/etc/nut# upsdrvctl -u nut -DDDDD start POWERCOM_Egys
# Network UPS Tools - UPS driver controller 2.4.1
# Starting UPS: POWERCOM_Egys
# exec: /lib/nut/powercom -a POWERCOM_Egys -u nut
# Network UPS Tools - PowerCom protocol UPS driver 0.12 (2.4.1)
# data receiving error (validation check)
# Nov 23 12:52:02 system76-pc powercom[14559]: Startup successful
# Nov 23 12:52:05 system76-pc powercom[14559]: data receiving error (0
instead of 16 bytes)
# Nov 23 12:52:05 system76-pc powercom[14559]: data receiving error
(validation check)
[POWERCOM_IMP]
driver=powercom
port=/dev/ttyUSB0
linevoltage=120
manufacturer=PowerCom
modelname=RCD-UPS2000D
serialnumber=40206430906
type=IMP
numOfBytesFromUPS=16
methodOfFlowControl=no_flow_control
shutdownArguments={{1,30},y}
# voltage=
# frequency=
# batteryPercentage=
# loadPercentage=
validationSequence={{5,0xFF},{7,0},{8,0}}
# output for IMP
#
# root at system76-pc:/etc/nut# upsdrvctl -u nut -DDDDD start POWERCOM_IMP
# Network UPS Tools - UPS driver controller 2.4.1
# Starting UPS: POWERCOM_IMP
# exec: /lib/nut/powercom -a POWERCOM_IMP -u nut
# Network UPS Tools - PowerCom protocol UPS driver 0.12 (2.4.1)
# Nov 23 12:55:02 system76-pc powercom[14570]: Startup successful
[POWERCOM_KIN]
driver=powercom
port=/dev/ttyUSB0
linevoltage=120
manufacturer=PowerCom
modelname=RCD-UPS2000D
serialnumber=40206430906
type=KIN
numOfBytesFromUPS=16
methodOfFlowControl=no_flow_control
shutdownArguments={{1,30},y}
# voltage=
# frequency=
# batteryPercentage=
# loadPercentage=
validationSequence={{11,0x4b},{8,0},{8,0}}
[POWERCOM_BNT]
driver=powercom
port=/dev/ttyUSB0
linevoltage=120
manufacturer=PowerCom
modelname=RCD-UPS2000D
serialnumber=40206430906
type=BNT
numOfBytesFromUPS=16
methodOfFlowControl=no_flow_control
shutdownArguments={{1,30},y}
# voltage=
# frequency=
# batteryPercentage=
# loadPercentage=
validationSequence={{11,0x42},{8,0},{8,0}}
[POWERCOM_BNT-other]
driver=powercom
port=/dev/ttyUSB0
linevoltage=120
manufacturer=PowerCom
modelname=RCD-UPS2000D
serialnumber=40206430906
type=BNT-other
numOfBytesFromUPS=16
methodOfFlowControl=no_flow_control
shutdownArguments={{1,30},y}
voltage={1.9216,-0.0977,0.82857,0.0000}
# frequency=
batteryPercentage={5.0000,0.3268,-825.00,0.46511,0}
loadPercentage={1.4474,0.0,0.8594,0.0}
validationSequence={{8,0},{8,0},{8,0}}
--