[Nut-upsuser] Selftest intervall, APC Smart-UPS 750 RM
Markus Wildi
wildi.markus at bluewin.ch
Thu Sep 3 13:21:46 UTC 2009
Hello Arnaud
I checked out and compiled r1952.
Find below the answers,
bye wildi
On Thursday 03 September 2009 14:00:39 you wrote:
> 2009/9/2 Markus Wildi <wildi.markus at bluewin.ch>
>
> > Hello Arnaud
>
> Hi Markus,
>
> thanks for having cc'ed the list ;-)
It was my fault, this time it appears on the list.
> > I compiled the source of nut-2.4.1 and you'll
> > find the output of usbhid-ups -D -a apcsmart
> > below.
> >
> > The UPS did regularly report a self-test while
> > running under apcupsd. It reports in addition
> > e.g. the last reason for a on battery event.
>
> if apcupsd can do it, NUT can do it too ;-)
Yes, indeed :-))
> the last self test report should already be available through
> ups.test.result (linked to the HID path UPS.Battery.Test, with the current
> value "No test initiated").
Here the result (see the whole output below):
0.379454 Path: UPS.Battery.Test, Type: Input, ReportID: 0x16, Offset:
0, Size: 8, Value: 6.000000
0.379961 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x16, Offset:
0, Size: 8, Value: 6.000000
> I've just commited a patch that adds:
> - input.transfer.reason
> - input.sensitivity (which is settable)
I see only the variable input.sensitivity (see below). With upsrw I see
[battery.charge.low]
[battery.runtime.low]
[input.sensitivity]
[ups.delay.shutdown]
> can you test the development version (Subversion trunk, r1952) to validate
> this.
> Some helpful info are available here:
> http://buildbot.ghz.cc/~buildbot/docs/r1950-97/website/download.html
>
> please send back an upsc output too.
obsvermes:/etc/init.d # /usr/local/ups/bin/upsc apcsmart at localhost
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2006/06/30
battery.runtime: 2160
battery.runtime.low: 120
battery.temperature: 21.1
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 750 RM
device.serial: AS0627130223
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/hiddev0
driver.version: 2.4.1-1952M
driver.version.data: APC HID 0.93
driver.version.internal: 0.34
input.sensitivity: high
input.voltage: 234.7
output.voltage: 234.7
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 20
ups.firmware: 619.3.I
ups.firmware.aux: 8.1
ups.load: 31.2
ups.mfr: American Power Conversion
ups.mfr.date: 2006/06/30
ups.model: Smart-UPS 750 RM
ups.productid: 0002
ups.serial: AS0627130223
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.vendorid: 051d
>
> if you still see differences with apcupsd, please tell me back. It's quite
> possible that I've missed something more about how APC units work.
>
> (...)
>
>
> thanks for these data.
>
> cheers,
> Arnaud
Network UPS Tools - Generic HID driver 0.34 (2.4.1-1952M)
USB communication driver 0.31
0.000000 debug level is '1'
0.003207 upsdrv_initups...
0.090069 Using subdriver: APC HID 0.93
0.092504 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID:
0x01, Offset: 0, Size: 8, Value: 1.000000
0.094466 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID:
0x02, Offset: 0, Size: 8, Value: 2.000000
0.096460 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID:
0x03, Offset: 0, Size: 8, Value: 3.000000
0.098455 Path: UPS.PowerSummary.iOEMInformation, Type: Feature,
ReportID: 0x04, Offset: 0, Size: 8, Value: 3.000000
0.100452 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x05, Offset: 0, Size: 8, Value: 4.000000
0.102456 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID:
0x06, Offset: 0, Size: 8, Value: 1.000000
0.102938 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID:
0x06, Offset: 8, Size: 8, Value: 2.000000
0.104462 Path: UPS.PowerSummary.DesignCapacity, Type: Feature,
ReportID: 0x0e, Offset: 0, Size: 8, Value: 100.000000
0.104932 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature,
ReportID: 0x0e, Offset: 8, Size: 8, Value: 100.000000
0.106470 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x0c, Offset: 0, Size: 8, Value: 100.000000
0.106969 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x0c, Offset: 0, Size: 8, Value: 100.000000
0.108455 Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature,
ReportID: 0x10, Offset: 0, Size: 8, Value: 1.000000
0.108924 Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature,
ReportID: 0x10, Offset: 8, Size: 8, Value: 1.000000
0.110456 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature,
ReportID: 0x0f, Offset: 0, Size: 8, Value: 50.000000
0.116625 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature,
ReportID: 0x11, Offset: 0, Size: 8, Value: 10.000000
0.222510 Path: UPS.PowerSummary.ManufacturerDate, Type: Feature,
ReportID: 0x09, Offset: 0, Size: 16, Value: 13534.000000
0.224477 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID:
0x0d, Offset: 0, Size: 16, Value: 2160.000000
0.225418 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x0d, Offset: 0, Size: 16, Value: 2160.000000
0.227465 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature,
ReportID: 0x12, Offset: 0, Size: 16, Value: -1.000000
0.229453 Path: UPS.PowerSummary.DelayBeforeReboot, Type: Feature,
ReportID: 0x13, Offset: 0, Size: 24, Value: -1.000000
0.231463 Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input,
ReportID: 0x08, Offset: 0, Size: 24, Value: 120.000000
0.231957 Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature,
ReportID: 0x08, Offset: 0, Size: 24, Value: 120.000000
0.233456 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID:
0x0a, Offset: 0, Size: 16, Value: 24.000000
0.326507 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x0b,
Offset: 0, Size: 16, Value: 27.400000
0.362493 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Input,
ReportID: 0x14, Offset: 0, Size: 8, Value: 1.000000
0.363524 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x14, Offset: 0, Size: 8, Value: 1.000000
0.365470 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x07, Offset: 0, Size: 1, Value: 0.000000
0.366476 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature,
ReportID: 0x07, Offset: 0, Size: 1, Value: 0.000000
0.366960 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input,
ReportID: 0x07, Offset: 1, Size: 1, Value: 0.000000
0.367418 Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x07, Offset: 1, Size: 1, Value: 0.000000
0.367869 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x07, Offset: 2, Size: 1, Value: 1.000000
0.368332 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x07, Offset: 2, Size: 1, Value: 1.000000
0.368771 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type:
Input, ReportID: 0x07, Offset: 3, Size: 1, Value: 1.000000
0.369265 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type:
Feature, ReportID: 0x07, Offset: 3, Size: 1, Value: 1.000000
0.369715 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x07, Offset: 4, Size: 1, Value: 0.000000
0.370185 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature,
ReportID: 0x07, Offset: 4, Size: 1, Value: 0.000000
0.370681 Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type:
Input, ReportID: 0x07, Offset: 5, Size: 1, Value: 0.000000
0.371212 Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, Type:
Feature, ReportID: 0x07, Offset: 5, Size: 1, Value: 0.000000
0.371665 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x07, Offset: 6, Size: 1, Value: 0.000000
0.372124 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Feature, ReportID: 0x07, Offset: 6, Size: 1, Value: 0.000000
0.372577 Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input,
ReportID: 0x07, Offset: 7, Size: 1, Value: 0.000000
0.373045 Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature,
ReportID: 0x07, Offset: 7, Size: 1, Value: 0.000000
0.373496 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type:
Input, ReportID: 0x07, Offset: 8, Size: 1, Value: 0.000000
0.373981 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, Type:
Feature, ReportID: 0x07, Offset: 8, Size: 1, Value: 0.000000
0.374478 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x07, Offset: 9, Size: 1, Value: 0.000000
0.374968 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x07, Offset: 9, Size: 1, Value: 0.000000
0.375410 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input,
ReportID: 0x07, Offset: 10, Size: 1, Value: 0.000000
0.375892 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Feature,
ReportID: 0x07, Offset: 10, Size: 1, Value: 0.000000
0.376338 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated,
Type: Input, ReportID: 0x07, Offset: 11, Size: 1, Value: 0.000000
0.376840 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated,
Type: Feature, ReportID: 0x07, Offset: 11, Size: 1, Value: 0.000000
0.377294 Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Input,
ReportID: 0x07, Offset: 12, Size: 1, Value: 0.000000
0.377760 Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Feature,
ReportID: 0x07, Offset: 12, Size: 1, Value: 0.000000
0.379454 Path: UPS.Battery.Test, Type: Input, ReportID: 0x16, Offset:
0, Size: 8, Value: 6.000000
0.379961 Path: UPS.Battery.Test, Type: Feature, ReportID: 0x16, Offset:
0, Size: 8, Value: 6.000000
0.381444 Path: UPS.Battery.APCBattCapBeforeStartup, Type: Input,
ReportID: 0x17, Offset: 0, Size: 8, Value: 0.000000
0.381950 Path: UPS.Battery.APCBattCapBeforeStartup, Type: Feature,
ReportID: 0x17, Offset: 0, Size: 8, Value: 0.000000
0.383449 Path: UPS.Battery.ff86001a, Type: Input, ReportID: 0x1b,
Offset: 0, Size: 8, Value: 3.000000
0.384197 Path: UPS.Battery.ff86001a, Type: Feature, ReportID: 0x1b,
Offset: 0, Size: 8, Value: 3.000000
0.385452 Path: UPS.Battery.ff86001b, Type: Input, ReportID: 0x1c,
Offset: 0, Size: 8, Value: 0.000000
0.385905 Path: UPS.Battery.ff86001b, Type: Feature, ReportID: 0x1c,
Offset: 0, Size: 8, Value: 0.000000
0.492502 Path: UPS.Battery.ManufacturerDate, Type: Input, ReportID:
0x15, Offset: 0, Size: 16, Value: 13534.000000
0.493575 Path: UPS.Battery.ManufacturerDate, Type: Feature, ReportID:
0x15, Offset: 0, Size: 16, Value: 13534.000000
0.495468 Path: UPS.Battery.RemainingCapacity, Type: Feature, ReportID:
0x18, Offset: 0, Size: 16, Value: 100.000000
0.497450 Path: UPS.Battery.RemainingTimeLimit, Type: Input, ReportID:
0x1a, Offset: 0, Size: 16, Value: 120.000000
0.497921 Path: UPS.Battery.RemainingTimeLimit, Type: Feature, ReportID:
0x1a, Offset: 0, Size: 16, Value: 120.000000
0.499454 Path: UPS.Battery.RunTimeToEmpty, Type: Feature, ReportID:
0x19, Offset: 0, Size: 16, Value: 2160.000000
0.582506 Path: UPS.Battery.Temperature, Type: Feature, ReportID: 0x1e,
Offset: 0, Size: 16, Value: 294.200000
0.584470 Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID:
0x1f, Offset: 0, Size: 16, Value: 24.000000
0.672488 Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x1d,
Offset: 0, Size: 16, Value: 27.400000
0.766514 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x20,
Offset: 0, Size: 16, Value: 234.700000
0.882497 Path: UPS.Input.APCLineFailCause, Type: Input, ReportID: 0x21,
Offset: 0, Size: 8, Value: 5.000000
0.882610 Path: UPS.Input.APCLineFailCause, Type: Feature, ReportID:
0x21, Offset: 0, Size: 8, Value: 5.000000
0.886274 Path: UPS.Input.APCSensitivity, Type: Input, ReportID: 0x22,
Offset: 0, Size: 8, Value: 2.000000
0.886421 Path: UPS.Input.APCSensitivity, Type: Feature, ReportID: 0x22,
Offset: 0, Size: 8, Value: 2.000000
0.972498 Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 0x2c,
Offset: 0, Size: 16, Value: 31.200000
1.062618 Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x2a,
Offset: 0, Size: 16, Value: 50.000000
1.152475 Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x2b,
Offset: 0, Size: 16, Value: 234.700000
1.154478 Path: UPS.Output.ConfigVoltage, Type: Input, ReportID: 0x2d,
Offset: 0, Size: 16, Value: 230.000000
1.154584 Path: UPS.Output.ConfigVoltage, Type: Feature, ReportID: 0x2d,
Offset: 0, Size: 16, Value: 230.000000
1.156449 Path: UPS.Output.HighVoltageTransfer, Type: Input, ReportID:
0x23, Offset: 0, Size: 16, Value: 253.000000
1.156558 Path: UPS.Output.HighVoltageTransfer, Type: Feature, ReportID:
0x23, Offset: 0, Size: 16, Value: 253.000000
1.158630 Path: UPS.Output.LowVoltageTransfer, Type: Input, ReportID:
0x24, Offset: 0, Size: 16, Value: 208.000000
1.158741 Path: UPS.Output.LowVoltageTransfer, Type: Feature, ReportID:
0x24, Offset: 0, Size: 16, Value: 208.000000
1.160450 Path: UPS.Output.APCDelayBeforeStartup, Type: Input, ReportID:
0x25, Offset: 0, Size: 16, Value: 60.000000
1.160557 Path: UPS.Output.APCDelayBeforeStartup, Type: Feature,
ReportID: 0x25, Offset: 0, Size: 16, Value: 60.000000
1.162481 Path: UPS.Output.APCShutdownAfterDelay, Type: Input, ReportID:
0x26, Offset: 0, Size: 16, Value: 90.000000
1.162588 Path: UPS.Output.APCShutdownAfterDelay, Type: Feature,
ReportID: 0x26, Offset: 0, Size: 16, Value: 90.000000
1.164448 Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID:
0x27, Offset: 0, Size: 16, Value: -1.000000
1.166473 Path: UPS.Output.DelayBeforeStartup, Type: Feature, ReportID:
0x28, Offset: 0, Size: 16, Value: -1.000000
1.168441 Path: UPS.Output.DelayBeforeReboot, Type: Feature, ReportID:
0x29, Offset: 0, Size: 24, Value: -1.000000
1.170457 Path: UPS.iProduct, Type: Feature, ReportID: 0x2e, Offset: 0,
Size: 8, Value: 5.000000
1.172423 Path: UPS.iSerialNumber, Type: Feature, ReportID: 0x2f,
Offset: 0, Size: 8, Value: 2.000000
1.174451 Path: UPS.iManufacturer, Type: Feature, ReportID: 0x30,
Offset: 0, Size: 8, Value: 3.000000
1.176419 Path: UPS.iName, Type: Feature, ReportID: 0x31, Offset: 0,
Size: 8, Value: 6.000000
1.178448 Path: UPS.APC_UPS_FirmwareRevision, Type: Feature, ReportID:
0x34, Offset: 0, Size: 8, Value: 7.000000
1.180445 Path: UPS.APC_USB_FirmwareRevision, Type: Feature, ReportID:
0x37, Offset: 0, Size: 8, Value: 8.000000
1.182454 Path: UPS.APCPanelTest, Type: Feature, ReportID: 0x32, Offset:
0, Size: 8, Value: 1.000000
1.296479 Path: UPS.ManufacturerDate, Type: Feature, ReportID: 0x35,
Offset: 0, Size: 16, Value: 13534.000000
1.332472 Path: UPS.ff860027, Type: Feature, ReportID: 0x3e, Offset: 0,
Size: 32, Value: 0.000000
1.334480 Path: UPS.ff860028, Type: Feature, ReportID: 0x3f, Offset: 0,
Size: 32, Value: 0.000000
1.336430 Path: UPS.AudibleAlarmControl, Type: Input, ReportID: 0x36,
Offset: 0, Size: 8, Value: 1.000000
1.336526 Path: UPS.AudibleAlarmControl, Type: Feature, ReportID: 0x36,
Offset: 0, Size: 8, Value: 1.000000
1.338472 Path: UPS.PresentStatus.Charging, Type: Input, ReportID: 0x33,
Offset: 0, Size: 1, Value: 0.000000
1.338577 Path: UPS.PresentStatus.Charging, Type: Feature, ReportID:
0x33, Offset: 0, Size: 1, Value: 0.000000
1.338666 Path: UPS.PresentStatus.Discharging, Type: Input, ReportID:
0x33, Offset: 1, Size: 1, Value: 0.000000
1.338755 Path: UPS.PresentStatus.Discharging, Type: Feature, ReportID:
0x33, Offset: 1, Size: 1, Value: 0.000000
1.338844 Path: UPS.PresentStatus.ACPresent, Type: Input, ReportID:
0x33, Offset: 2, Size: 1, Value: 1.000000
1.338932 Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID:
0x33, Offset: 2, Size: 1, Value: 1.000000
1.339022 Path: UPS.PresentStatus.BatteryPresent, Type: Input, ReportID:
0x33, Offset: 3, Size: 1, Value: 1.000000
1.339111 Path: UPS.PresentStatus.BatteryPresent, Type: Feature,
ReportID: 0x33, Offset: 3, Size: 1, Value: 1.000000
1.339200 Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type:
Input, ReportID: 0x33, Offset: 4, Size: 1, Value: 0.000000
1.339290 Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x33, Offset: 4, Size: 1, Value: 0.000000
1.339396 Path: UPS.PresentStatus.ShutdownRequested, Type: Input,
ReportID: 0x33, Offset: 5, Size: 1, Value: 0.000000
1.339484 Path: UPS.PresentStatus.ShutdownRequested, Type: Feature,
ReportID: 0x33, Offset: 5, Size: 1, Value: 0.000000
1.339572 Path: UPS.PresentStatus.ShutdownImminent, Type: Input,
ReportID: 0x33, Offset: 6, Size: 1, Value: 0.000000
1.339660 Path: UPS.PresentStatus.ShutdownImminent, Type: Feature,
ReportID: 0x33, Offset: 6, Size: 1, Value: 0.000000
1.339750 Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type:
Input, ReportID: 0x33, Offset: 7, Size: 1, Value: 0.000000
1.339839 Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type:
Feature, ReportID: 0x33, Offset: 7, Size: 1, Value: 0.000000
1.339928 Path: UPS.PresentStatus.CommunicationLost, Type: Input,
ReportID: 0x33, Offset: 8, Size: 1, Value: 0.000000
1.340016 Path: UPS.PresentStatus.CommunicationLost, Type: Feature,
ReportID: 0x33, Offset: 8, Size: 1, Value: 0.000000
1.340106 Path: UPS.PresentStatus.NeedReplacement, Type: Input,
ReportID: 0x33, Offset: 9, Size: 1, Value: 0.000000
1.340195 Path: UPS.PresentStatus.NeedReplacement, Type: Feature,
ReportID: 0x33, Offset: 9, Size: 1, Value: 0.000000
1.340283 Path: UPS.PresentStatus.Overload, Type: Input, ReportID: 0x33,
Offset: 10, Size: 1, Value: 0.000000
1.340369 Path: UPS.PresentStatus.Overload, Type: Feature, ReportID:
0x33, Offset: 10, Size: 1, Value: 0.000000
1.340460 Path: UPS.PresentStatus.VoltageNotRegulated, Type: Input,
ReportID: 0x33, Offset: 11, Size: 1, Value: 0.000000
1.340549 Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature,
ReportID: 0x33, Offset: 11, Size: 1, Value: 0.000000
1.340641 Path: UPS.PresentStatus.ff860080, Type: Input, ReportID: 0x33,
Offset: 12, Size: 1, Value: 0.000000
1.340730 Path: UPS.PresentStatus.ff860080, Type: Feature, ReportID:
0x33, Offset: 12, Size: 1, Value: 0.000000
1.340917 Detected a UPS: American Power Conversion/Smart-UPS 750 RM
FW:619.3.I USB FW:8.1
1.348720 upsdrv_initinfo...
1.351981 upsdrv_updateinfo...
1.414506 Got 1 HID objects...
1.442458 Quick update...
1.443118 upsdrv_updateinfo...
1.478508 Got 1 HID objects...
1.482576 Quick update...
3.442723 upsdrv_updateinfo...
3.462751 Got 1 HID objects...
3.522401 Quick update...
^C 4.175906 Signal 2: exiting
4.175983 upsdrv_cleanup...
More information about the Nut-upsuser
mailing list