on 24/01/2011 16:18 Arjen de Korte wrote:
> Citeren Kevin <bakdong at gmail.com>:
>
>> Different....
>>
>> # ./clients/upsc apc1500
>
> [...]
>
>> ups.delay.shutdown: 90
>> ups.delay.start: 250
>
> This is what I expected to happen. The value of ups.delay.shutdown is
> now read from the UPS...
Understood.
>
>> ./clients/upsrw -s ups.delay.shutdown=30 -u apcmon -p pass123 apc1500
>> OK
>>
>> # ./clients/upsc apc1500
>
> [...]
>
>> ups.delay.shutdown: 30
>> ups.delay.start: 250
>
> ..and apparently can be written as well.
Yes, but this value could also be changed before the patches. (See
previous posts)
>
> Sadly, it looks like this value is used for a different purpose than
> setting the minimum delay value before shutdown (like I expected).
> Unless you're willing to dig deeper into this, I think we have to
> conclude that this model doesn't allow setting the delay values lower
> than 90 seconds. Using an 'ondelay' value of 100, does the UPS cycle the
> output if mains is present? And does it wait until the mains return if
> it is not present?
Happy to dig as deep as you would like me to. (I would like to get the
CS 500 sorted out too though) I will check again with the unmodified
code, but I'm fairly sure that the output will cycle when power is
present. (even with on and offdelay values at the default 90 minimum)
> I would still like to see the full output of the below command. An
> earlier version you posted was incomplete (the report descriptor was
> missing, which is vital to be able to check our HID parser without
> access to a specific UPS model). Could you please post the output of
>
> /path/to/usbhid-ups -DD -a apc1500 > APC_Smart-UPS_1000.log 2>&1
>
> here? The redirection of stderr to stdin was probably missing in your
> previous post.
I'll do it now and attach it here.....
Regards,
Kevin.
-------------- next part --------------
A non-text attachment was scrubbed...
Name: APC_Smart-UPS_1000.zip
Type: application/x-compressed
Size: 6230 bytes
Desc: not available
URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20110124/94f13c37/attachment-0001.bin>