[Nut-upsuser] Incorrect Values From usbhid-ups
Bill S
kenwood0622 at gmail.com
Mon Mar 24 03:12:14 UTC 2014
I recently purchased a CyberPower CP1500PFCLCD UPS as a replacement
UPS for a headless server running Slackware 14.1 with the 3.10.7
kernel. I then downloaded the NUT 2.7.1 tarball on the server and
following the directions installed the software. The installation
went well and the UPS will shutdown the server using the forced down
test and then it powers back up as it should. The installation of
the cgi software has been a real slog however and so far I only have
upsstats.cgi working which brings me to my problem. When I first
looked at the upsstats.cgi screen I found the UPS output voltage to be
very high and it did not match the input voltage. It should however
since the line power just passes through the UPS when it is not on
battery power. After further investigation I determined that problem
was not with upsstats.cgi but apparently with the usbhid-ups driver.
It appears the driver recognizes the CP1500 but it is not interpreting
the response from the CP1500 correctly when it interrogates the unit
for the current output voltage. I now suspect that I wasted quite a
bit of time on this project since it will take programming skills that
I certainly do not have to fix the driver. I am writing however in the
hopes that I am wrong, that the fix is simple, and that it only only
seems complex as a result of my not understanding the real problem.
Is there anything I can do to obtain the correct values?
The output of the driver is below. The incorrect voltage of 136 is
shown at 0.265256. It should match input voltage of 119 as shown at
0.265219 but it doesn't. The voltages displayed on the UPS LCD panel
information however are equal and match the input voltage provided by
the driver. There might be other incorrect values in the usbhid-ups
output but that is the one that has caught my attention so far.
Network UPS Tools - Generic HID driver 0.38 (2.7.1)
USB communication driver 0.32
0.000000 debug level is '2'
0.000404 upsdrv_initups...
0.259751 Checking device (0557/7000) (001/002)
0.259799 Failed to open device, skipping. (Permission denied)
0.259804 Checking device (0764/0501) (001/003)
0.260607 - VendorID: 0764
0.260622 - ProductID: 0501
0.260626 - Manufacturer: CP1500PFCLCD
0.260630 - Product: CRCA102*AF1
0.260634 - Serial Number: CPS
0.260638 - Bus: 001
0.260642 Trying to match device
0.260685 Device matches
0.260697 failed to claim USB device: Device or resource busy
0.260713 detached kernel driver from USB device...
0.261109 HID descriptor length 430
0.261807 Report Descriptor size = 430
0.261958 Using subdriver: CyberPower HID 0.3
0.262049 Path: UPS.PowerSummary.iProduct, Type: Feature,
ReportID: 0x01, Offset: 0, Size: 8, Value: 1
0.262137 Path: UPS.PowerSummary.iSerialNumber, Type: Feature,
ReportID: 0x02, Offset: 0, Size: 8, Value: 2
0.262220 Path: UPS.PowerSummary.iDeviceChemistry, Type:
Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 4
0.262305 Path: UPS.PowerSummary.iOEMInformation, Type: Feature,
ReportID: 0x04, Offset: 0, Size: 8, Value: 3
0.262412 Path: UPS.PowerSummary.Rechargeable, Type: Feature,
ReportID: 0x05, Offset: 0, Size: 8, Value: 1
0.262519 Path: UPS.PowerSummary.CapacityMode, Type: Feature,
ReportID: 0x06, Offset: 0, Size: 8, Value: 2
0.262607 Path: UPS.PowerSummary.DesignCapacity, Type: Feature,
ReportID: 0x07, Offset: 0, Size: 8, Value: 100
0.262618 Path: UPS.PowerSummary.CapacityGranularity1, Type:
Feature, ReportID: 0x07, Offset: 8, Size: 8, Value: 5
0.262627 Path: UPS.PowerSummary.CapacityGranularity2, Type:
Feature, ReportID: 0x07, Offset: 16, Size: 8, Value: 10
0.262637 Path: UPS.PowerSummary.WarningCapacityLimit, Type:
Feature, ReportID: 0x07, Offset: 24, Size: 8, Value: 20
0.262646 Path: UPS.PowerSummary.RemainingCapacityLimit, Type:
Feature, ReportID: 0x07, Offset: 32, Size: 8, Value: 10
0.262655 Path: UPS.PowerSummary.FullChargeCapacity, Type:
Feature, ReportID: 0x07, Offset: 40, Size: 8, Value: 100
0.262740 Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x08, Offset: 0, Size: 8, Value: 100
0.262749 Path: UPS.PowerSummary.RemainingCapacity, Type:
Feature, ReportID: 0x08, Offset: 0, Size: 8, Value: 100
0.262759 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input,
ReportID: 0x08, Offset: 8, Size: 16, Value: 3030
0.262767 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x08, Offset: 8, Size: 16, Value: 3030
0.262776 Path: UPS.PowerSummary.RemainingTimeLimit, Type:
Input, ReportID: 0x08, Offset: 24, Size: 16, Value: 300
0.262784 Path: UPS.PowerSummary.RemainingTimeLimit, Type:
Feature, ReportID: 0x08, Offset: 24, Size: 16, Value: 300
0.262865 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature,
ReportID: 0x09, Offset: 0, Size: 8, Value: 24
0.262966 Path: UPS.PowerSummary.Voltage, Type: Feature,
ReportID: 0x0a, Offset: 0, Size: 8, Value: 24
0.263050 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Input, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
0.263059 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Input, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
0.263067 Path: UPS.PowerSummary.PresentStatus.Discharging,
Type: Input, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
0.263075 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Input, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
0.263082 Path: UPS.PowerSummary.PresentStatus.FullyCharged,
Type: Input, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
0.263090 Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input,
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
0.263098 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
0.263105 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
0.263113 Path: UPS.PowerSummary.PresentStatus.Discharging,
Type: Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
0.263121 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
0.263129 Path: UPS.PowerSummary.PresentStatus.FullyCharged,
Type: Feature, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
0.263137 Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type:
Feature, ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
0.263218 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.263227 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Input, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.263307 Path: UPS.PowerSummary.iManufacturer, Type: Feature,
ReportID: 0x0d, Offset: 0, Size: 8, Value: 3
0.263390 Path: UPS.Input.ConfigVoltage, Type: Feature,
ReportID: 0x0e, Offset: 0, Size: 8, Value: 120
0.263488 Path: UPS.Input.Voltage, Type: Feature, ReportID:
0x0f, Offset: 0, Size: 16, Value: 119
0.263575 Path: UPS.Input.LowVoltageTransfer, Type: Feature,
ReportID: 0x10, Offset: 0, Size: 16, Value: 88
0.263585 Path: UPS.Input.LowVoltageTransfer, Type: Input,
ReportID: 0x10, Offset: 0, Size: 16, Value: 88
0.263593 Path: UPS.Input.HighVoltageTransfer, Type: Feature,
ReportID: 0x10, Offset: 16, Size: 16, Value: 139
0.263601 Path: UPS.Input.HighVoltageTransfer, Type: Input,
ReportID: 0x10, Offset: 16, Size: 16, Value: 139
0.263718 Path: UPS.Output.Voltage, Type: Feature, ReportID:
0x12, Offset: 0, Size: 16, Value: 136
0.263824 Path: UPS.Output.PercentLoad, Type: Feature, ReportID:
0x13, Offset: 0, Size: 8, Value: 16
0.263906 Path: UPS.Output.Test, Type: Feature, ReportID: 0x14,
Offset: 0, Size: 8, Value: 6
0.263914 Path: UPS.Output.Test, Type: Input, ReportID: 0x14,
Offset: 0, Size: 8, Value: 6
0.263996 Path: UPS.Output.DelayBeforeShutdown, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
0.264105 Path: UPS.Output.DelayBeforeStartup, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
0.264214 Path: UPS.Output.Boost, Type: Feature, ReportID: 0x17,
Offset: 0, Size: 1, Value: 0
0.264223 Path: UPS.Output.Overload, Type: Feature, ReportID:
0x17, Offset: 1, Size: 1, Value: 0
0.264306 Path: UPS.Output.ConfigActivePower, Type: Feature,
ReportID: 0x18, Offset: 0, Size: 16, Value: 900
0.264388 Path: UPS.Output.ff010043, Type: Feature, ReportID:
0x1a, Offset: 0, Size: 8, Value: 1
0.264396 Path: UPS.Output.ff010043, Type: Input, ReportID:
0x1a, Offset: 0, Size: 8, Value: 1
0.264417 Report descriptor retrieved (Reportlen = 430)
0.264421 Found HID device
0.264426 Detected a UPS: CP1500PFCLCD/CRCA102*AF1
0.264455 Path: UPS.PowerSummary.iDeviceChemistry, Type:
Feature, ReportID: 0x03, Offset: 0, Size: 8, Value: 4
0.264735 Path: UPS.PowerSummary.iOEMInformation, Type: Feature,
ReportID: 0x04, Offset: 0, Size: 8, Value: 3
0.264960 Path: UPS.PowerSummary.WarningCapacityLimit, Type:
Feature, ReportID: 0x07, Offset: 24, Size: 8, Value: 20
0.264973 Path: UPS.PowerSummary.RemainingCapacityLimit, Type:
Feature, ReportID: 0x07, Offset: 32, Size: 8, Value: 10
0.264988 Path: UPS.PowerSummary.RemainingCapacity, Type:
Feature, ReportID: 0x08, Offset: 0, Size: 8, Value: 100
0.265001 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x08, Offset: 8, Size: 16, Value: 3030
0.265013 Path: UPS.PowerSummary.RemainingTimeLimit, Type:
Feature, ReportID: 0x08, Offset: 24, Size: 16, Value: 300
0.265025 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature,
ReportID: 0x09, Offset: 0, Size: 8, Value: 24
0.265035 Path: UPS.PowerSummary.Voltage, Type: Feature,
ReportID: 0x0a, Offset: 0, Size: 8, Value: 24
0.265049 Path: UPS.Output.PercentLoad, Type: Feature, ReportID:
0x13, Offset: 0, Size: 8, Value: 16
0.265059 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.265071 Path: UPS.Output.Test, Type: Feature, ReportID: 0x14,
Offset: 0, Size: 8, Value: 6
0.265082 Path: UPS.Output.ConfigActivePower, Type: Feature,
ReportID: 0x18, Offset: 0, Size: 16, Value: 900
0.265104 Path: UPS.Output.DelayBeforeStartup, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
0.265116 Path: UPS.Output.DelayBeforeShutdown, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
0.265130 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
0.265141 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
0.265151 Path: UPS.PowerSummary.PresentStatus.Discharging,
Type: Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
0.265160 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
0.265170 Path: UPS.PowerSummary.PresentStatus.FullyCharged,
Type: Feature, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
0.265179 Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type:
Feature, ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
0.265189 Path: UPS.Output.Boost, Type: Feature, ReportID: 0x17,
Offset: 0, Size: 1, Value: 0
0.265199 Path: UPS.Output.Overload, Type: Feature, ReportID:
0x17, Offset: 1, Size: 1, Value: 0
0.265208 Path: UPS.Input.ConfigVoltage, Type: Feature,
ReportID: 0x0e, Offset: 0, Size: 8, Value: 120
0.265219 Path: UPS.Input.Voltage, Type: Feature, ReportID:
0x0f, Offset: 0, Size: 16, Value: 119
0.265231 Path: UPS.Input.LowVoltageTransfer, Type: Feature,
ReportID: 0x10, Offset: 0, Size: 16, Value: 88
0.265243 Path: UPS.Input.HighVoltageTransfer, Type: Feature,
ReportID: 0x10, Offset: 16, Size: 16, Value: 139
0.265256 Path: UPS.Output.Voltage, Type: Feature, ReportID:
0x12, Offset: 0, Size: 16, Value: 136
0.265270 Path: UPS.Output.Test, Type: Feature, ReportID: 0x14,
Offset: 0, Size: 8, Value: 6
0.265280 Path: UPS.Output.Test, Type: Feature, ReportID: 0x14,
Offset: 0, Size: 8, Value: 6
0.265290 Path: UPS.Output.Test, Type: Feature, ReportID: 0x14,
Offset: 0, Size: 8, Value: 6
0.265300 Path: UPS.Output.DelayBeforeShutdown, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
0.265310 Path: UPS.Output.DelayBeforeStartup, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
0.265321 Path: UPS.Output.DelayBeforeShutdown, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
0.265334 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.265344 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.265353 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.265363 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.265373 Path: UPS.PowerSummary.AudibleAlarmControl, Type:
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 2
0.265391 upsdrv_initinfo...
0.265399 upsdrv_updateinfo...
0.515466 libusb_get_interrupt: Connection timed out
0.515484 Got 0 HID objects...
0.515490 Quick update...
0.515500 Path: UPS.Output.DelayBeforeStartup, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
0.515509 Path: UPS.Output.DelayBeforeShutdown, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
0.515517 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
0.515524 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
0.515530 Path: UPS.PowerSummary.PresentStatus.Discharging,
Type: Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
0.515536 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
0.515620 dstate_init: sock /var/state/ups/usbhid-ups-CyberPower
open on fd 8
0.515633 upsdrv_updateinfo...
0.765694 libusb_get_interrupt: Connection timed out
0.765712 Got 0 HID objects...
0.765718 Quick update...
0.765727 Path: UPS.Output.DelayBeforeStartup, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
0.765736 Path: UPS.Output.DelayBeforeShutdown, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
0.765744 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
0.765750 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
0.765757 Path: UPS.PowerSummary.PresentStatus.Discharging,
Type: Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
0.765763 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
2.516475 upsdrv_updateinfo...
2.517702 Got 6 HID objects...
2.517722 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Input, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
2.517733 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Input, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
2.517742 Path: UPS.PowerSummary.PresentStatus.Discharging,
Type: Input, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
2.517751 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Input, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
2.517760 Path: UPS.PowerSummary.PresentStatus.FullyCharged,
Type: Input, ReportID: 0x0b, Offset: 4, Size: 1, Value: 1
2.517769 Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input,
ReportID: 0x0b, Offset: 5, Size: 1, Value: 0
2.517777 Quick update...
2.517896 Path: UPS.Output.DelayBeforeStartup, Type: Feature,
ReportID: 0x16, Offset: 0, Size: 16, Value: -60
2.518007 Path: UPS.Output.DelayBeforeShutdown, Type: Feature,
ReportID: 0x15, Offset: 0, Size: 16, Value: -60
2.518016 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x0b, Offset: 0, Size: 1, Value: 1
2.518023 Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x0b, Offset: 1, Size: 1, Value: 0
2.518029 Path: UPS.PowerSummary.PresentStatus.Discharging,
Type: Feature, ReportID: 0x0b, Offset: 2, Size: 1, Value: 0
2.518035 Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x0b, Offset: 3, Size: 1, Value: 0
4.518470 upsdrv_updateinfo...
4.518515 libusb_get_interrupt: Input/output error
4.518521 Got 0 HID objects...
4.518526 Quick update...
4.518538 libusb_get_report: Input/output error
4.518549 Can't retrieve Report 16: Input/output error
6.520478 upsdrv_updateinfo...
6.520513 Got to reconnect!
More information about the Nut-upsuser
mailing list